Hi all,
I've come across an issue when trying to integrating an MovifitFC drive onto a L62 processor using V13.
The system is one of the oldest we have in the factory other systems we have are running Logix V30 on the L72 using the Movifit without an issue.
In the past we have intergrated an MoviPro ADC unit onto the v13 processor without any issues.
As the V13 doesn't support EDS files I've used the Ethernet module to create my own connection to the drive but even using the structure specified by SEW cannot get the drive to communicate. It keeps giving me a comms timeout message.
Has anyone got any ideas on what the issue my be or successfully done this elsewhere?
I don't really fancy upgrading this PLC to a new revision to due other equipment installed on the line
Thanks in advance
Old December 11th, 2017, 04:16 AM   #2
jstolaruk
United States
jstolaruk is offline
(Duplicate message)
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
Old December 11th, 2017, 04:18 AM   #3
jstolaruk
United States
L62 can run v20, that would probably help with the eds issue.
__________________
Old December 11th, 2017, 08:23 AM   #4
0151paul
United Kingdom
0151paul is offline
Thanks for taking the time to reply.
We run v20 (& v30) on a number of other areas within the factory and have movifit running via EDS there. This is where I have cross referenced the input/output array sizes against the documented information from SEW I don't really want to upgrade the PLC in the first instance but will if I have to
Old December 11th, 2017, 03:34 PM   #5
ASF
Australia
ASF is offline
Can you post a screenshot of the error message you're getting?
Old December 12th, 2017, 04:29 AM   #6
0151paul
United Kingdom
0151paul is offline
Here's message & settings I'm using
Old December 12th, 2017, 03:31 PM   #7
ASF
Australia
ASF is offline
It's nothing more than a stab in the dark - but does your particular device have the option for Profinet and Ethernet/IP? A couple of years ago, I had an SEW device that I could not for the life of me get to talk. Turns out I'd forgotten to change a DIP switch that changed the port protocol from Profinet to Ethernet/IP. I finally worked it out after running a wireshark trace on the link, which showed the PLC sending out a connection request on the Ethernet/IP port, and the device rejecting it as the port wasn't open. A wireshark trace would likely be your next move also, if you can't find anything to "enable" Ethernet/IP.
Old December 14th, 2017, 03:15 PM   #8
0151paul
United Kingdom
0151paul is offline
Update.....
After setting up a test rig with a L62 v20 processor the issue was actually the ENBT card I was using to comunicate via to the movifit. When using an EN2T card there are no issues either via eds file or creation of a generic module. I checked the firmware revision levels against the card we used previously to communicate with the movipro on a different installation and they match. I have asked the question of SEW why there communication protocols are different between units, I'm waiting for a reply. As we have standard revision levels onsite for the ENBT I have not tried updating to the latest revision to see if I could establish communications that way.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Control Logix 1756 jamalshahid LIVE PLC Questions And Answers 9 May 8th, 2012 10:24 AM
Compact Logix Remote Racks The Plc Kid LIVE PLC Questions And Answers 10 September 29th, 2009 05:11 PM
Producer Consumer Messging between Control Logix & Compact Logix plcnovel LIVE PLC Questions And Answers 15 July 24th, 2006 10:04 AM