1200 absolute address tags MW100--MW500 move to global DB
Hello everybody,
for Siemens 1200
I have a question need help,
Through HMI, I use absolute address tags MW100--MW500 to set their values.
but in program, I have to use lots of their value in global DB, but 1200 block move only can do in global DB, if have ways to move MW100--MW500 to Globle DB, like DB1?
Old December 11th, 2017, 03:33 PM   #2
balash
Croatia
balash is offline
maybe you could try with BLKMOV P# M100.0 byte 400
BLKMOV should be under move operations / legacy (v13+)
source: how can I move block byte or word, Dword... in S7-1200 program?
Old December 11th, 2017, 03:47 PM   #3
mk42
United States
mk42 is offline
BLKMOV is supported in 1500s, but not 1200s.
Quote:
Originally Posted by suboliu View Post
Hello everybody,
for Siemens 1200
Is this different than the other thread you posted?
The comment linked below has an answer to your question that works in one instruction. If you're using the most recent software, you can add a network of SCL to the rest of your code
(LAD, probably?), to keep things simple.
http://www.plctalk.net/qanda/showpos...1&postcount=11
Old December 11th, 2017, 07:57 PM   #4
suboliu
Canada
suboliu is offline
Thank you very much!
the same, Because I didn't describe clearly. see attach for my questions.
Old December 12th, 2017, 03:47 AM   #5
BryanG
United Kingdom
BryanG is offline
The POKE_BLK instruction that I gave in your other thread will move from M memory to DB memory so long as the DB is non-optimised. It will also go from Inputs to Outputs, M or DB, from M or DB to Outputs, and from DB to M. The setting to make a DB non-optimised is: right click the DB in the program tree, go to Properties / Attributes / and untick Optimised block access. You will then get an extra column in the DB, right click the DB and Compile it and the offset gives you the 'in' DB address, add the DB number for something like DB1.DBD48. To use the block I gave, create a new FC block and select the Language SCL enter the block as I gave. The call to the new FC will be something like below which goes from M memory (B#16#83) starting at byte 100 for a total of 10 bytes, to DB (B#16#84) 1 starting at byte 0.
The whole thing of Siemens wanting us using optimised blocks feels like a bit of a con to me, memory isn't so tight that I need to worry any more and speed really isn't an issue. All that insisting on using optimised does is limit you to Siemens HMIs and software to talk to the PLC. Strike a blow for freedom and un-optimise.
Old December 12th, 2017, 09:00 AM   #6
suboliu
Canada
suboliu is offline
appreciate
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
siemens 1200 Block Move suboliu LIVE PLC Questions And Answers 39 December 12th, 2017 08:07 PM
S7 300 with Profibus communication jayasiri LIVE PLC Questions And Answers 26 August 27th, 2015 05:00 AM
Move data to a DB in different Int address?? HelloAll LIVE PLC Questions And Answers 5 December 16th, 2009 08:34 AM
Confused "again" S7 indirect Thim LIVE PLC Questions And Answers 17 July 22nd, 2008 04:47 PM
Building an S7 Array Move Questions DesertDog LIVE PLC Questions And Answers 19 June 17th, 2004 09:51 AM