Old December 12th, 2017, 04:07 AM   #1
Charbel
Member
Lebanon

Charbel is offline
 
Join Date: Jan 2012
Location: Beirut
Posts: 274
230VAC vs 24VDC

Dear,

what is the advantage of using 230VAC over 24VDC for discrete signals (digital input and outputs)

It is well understood that 24VDC is to be used for safety purposes

however, the client is asking for 230VAC to be used for DI/DO since it can handle better bad environmental conditions (It is used for field instruments far from the PLC in a large sewage treatment facility), please advise.

bad environmental conditions in this area (Kuwait) can be heavy sandstorm, high temperature (which I doubt it will affect)

thank you,

charbel
  Reply With Quote
Old December 12th, 2017, 04:48 AM   #2
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 781
I can't think of any reason? Many modern PLC systems don't even have 230V inputs anymore?

If your cables are properly screened, terminated and run seperately from other 230/400V services then you will have no issue.

Heat has no effect.
  Reply With Quote
Old December 12th, 2017, 04:59 AM   #3
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Heath, TX
Posts: 1,895
With very long runs, voltage drop can be significant. Let's say the run is so long that we have a voltage drop of 10 volts. At 24 volts, this is a serious problem.
At 230 VAC, it's negligible. I just checked AD Productivity 2000 PLC modules. You can get 120V and 120-240V I/O.
  Reply With Quote
Old December 12th, 2017, 05:02 AM   #4
Dirt
Member
Sweden

Dirt is offline
 
Join Date: Apr 2008
Location: Stockholm
Posts: 123
When I worked at a nuclear power plant, we had similar designs at two reactors. There was lots of reed relays for detecting position and volume flow (very specialized equipment)

One plant ran 24VDC (with a modernized control and safety system) and the one I worked at ran 110VDC center ground system. The 24VDC had a tendency to miss closed contacts due to oxidization.

The 110VDC center grounded system only needed one side, 55VDC basically to actually detect and had higher percentage of detection.

But this was a very old system and like nothing that'd be used in modern equipment. 24VDC is sufficient in most places, situations and SIL classes. As long as cable runs aren't too long, eg. voltage drop.
  Reply With Quote
Old December 12th, 2017, 05:09 AM   #5
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,046
I agree with the voltage drop over long runs

And just a WAG is it cheaper to run a 240 volt over 24? From the power consumption point but if you're pulling in a large coil would it be cheaper for 240? I don't know but maybe a reason

I would also think the 240 would be heavy-duty vs the 24, I work on a system that had a bunch of 240v outputs for larger motor starters
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old December 12th, 2017, 05:21 AM   #6
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 781
Keith I understand what you're saying but i don't think that applies here.

Purely hypothetical, but a micrologix 1400 digital input turn on voltage is 10V. Nominal draw per input is 5mA.

Using a 0.5mm2 instrument cable with a 36.8ohm/km resistance, I can still run 38km of cable before i have an issue....

Not that you would of course... I'm not rolling out that drum!!!



Ine
  Reply With Quote
Old December 12th, 2017, 05:52 AM   #7
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Heath, TX
Posts: 1,895
Yes, in a perfect world with no corrosion.
Some customers have silos that are 100 feet tall. Full sensors are motorized paddles with dry contacts. The silos will be wired by electricians. They use bare copper, TFFN.
  Reply With Quote
Old December 12th, 2017, 05:54 AM   #8
pal
Member
United Kingdom

pal is offline
 
Join Date: Apr 2011
Location: Tilbury
Posts: 165
Another point - with ac , you could have up to 10 ms signal delay from waveform . If timing is not critical then no problem .

Paul
  Reply With Quote
Old December 12th, 2017, 06:24 AM   #9
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 781
As it's a WWTP, nothing is likely to need 10ms resolution so safe on that account

Specifying (and checking!) Cable type is important, as is glanding, to ensure minimum corrosion.

I've been working in water and waste for a decade and i have yet to see any 230V input cards. A few 24AC ones but DC has been the norm.
  Reply With Quote
Old December 12th, 2017, 07:02 AM   #10
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 420
Just from a common sense point of view you wouldn't want 240 vac anywhere near field equipment.

The amount of poorly maintained plants I see with prox wires exposed because of chaffing springs to mind.

It still works so nobody bothers with it.
  Reply With Quote
Old December 12th, 2017, 07:39 AM   #11
Dirt
Member
Sweden

Dirt is offline
 
Join Date: Apr 2008
Location: Stockholm
Posts: 123
Quote:
Originally Posted by saffa View Post
as it's a wwtp, nothing is likely to need 10ms resolution so safe on that account

specifying (and checking!) cable type is important, as is glanding, to ensure minimum corrosion.

I've been working in water and waste for a decade and i have yet to see any 230v input cards. A few 24ac ones but dc has been the norm.
Quote:
Originally Posted by janner_10 View Post
just from a common sense point of view you wouldn't want 240 vac anywhere near field equipment.

The amount of poorly maintained plants i see with prox wires exposed because of chaffing springs to mind.

It still works so nobody bothers with it.
+1
  Reply With Quote
Old December 12th, 2017, 09:01 AM   #12
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,281
120 VAC IO is typically used in harsh industrial environments because the higher voltage can be detected through an oxidized, high resistance contact closure that would appear open to a 24 VDC input. I've encountered very few systems employing 230 VAC IO, and I've never built a new system using that control voltage. I suspect that 230 VAC IO has been used primarily to interface to existing 230 VAC hardwired control systems when upgrading to PLC controls.
__________________
  Reply With Quote
Old December 12th, 2017, 02:03 PM   #13
Alfons Gessl
Member
South Africa

Alfons Gessl is offline
 
Join Date: Apr 2014
Location: Jo-Burg
Posts: 11
24V DC is the standard for instrumentation in general for longer distances I use ET stations via ProfiBus or ProfiNet.
Only for return signals from Motor Isolator I use 230V AC, reason if the return signal wire gets in contact with power wires from the motor it will bow my entire 24V DC system. A 230V AC feedback can handle that. In the panel I reduce the 230V AC to 24V DC vie relay for the PLC input cards.
  Reply With Quote
Old December 12th, 2017, 09:12 PM   #14
mk42
Member
United States

mk42 is online now
 
Join Date: Jun 2013
Location: MI
Posts: 1,577
Quote:
Originally Posted by Bit_Bucket_07 View Post
120 VAC IO is typically used in harsh industrial environments because the higher voltage can be detected through an oxidized, high resistance contact closure that would appear open to a 24 VDC input. I've encountered very few systems employing 230 VAC IO, and I've never built a new system using that control voltage. I suspect that 230 VAC IO has been used primarily to interface to existing 230 VAC hardwired control systems when upgrading to PLC controls.
My guess is that it just the European standard AC, compared to our 110/120 over here. As an example, I don't think siemens has any 120 only modules. Any digital AC stuff is 110-240
  Reply With Quote
Old December 13th, 2017, 04:58 AM   #15
Aabeck
Member
United States

Aabeck is offline
 
Aabeck's Avatar
 
Join Date: Feb 2013
Location: Detroit
Posts: 832
How about running the long signals 220V for corrosion resistance and in the panel have a bank of 24V interposing relays going to the inputs & powered off the outputs?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
24VDC distribution to remote I/O panels from central control panel radfahrer LIVE PLC Questions And Answers 6 May 31st, 2015 08:22 PM
power 24VDC to power for 230VAC Charbel LIVE PLC Questions And Answers 4 January 9th, 2015 08:55 AM
Common 0V only on 2 x 24VDC power supplies qwsoftware LIVE PLC Questions And Answers 7 December 14th, 2009 07:45 PM