Rounding off on the migration stuff, one more help please.

So far so good, Almost done with this migration stuff
Someone please help me on this one:
ERROR IS:
''Bit and LSBit triggered alarms that used a Trigger Tag with a Bit data type will only be able to trigger a single alarm after import.''
Who can help give me an ideal of the right correction to this log error?
  Reply With Quote
Old December 12th, 2017, 02:28 PM   #2
arlenjacobs
Lifetime Supporting Member
Canada

arlenjacobs is offline
 
Join Date: Sep 2014
Location: Kelowna
Posts: 631
If it's a single bit trigger, no problem. Change the tag to a Bool type in the tag database.
Then use analog trigger in the Alarm setup, value 1 in the messages tab.

If it's a LSBit, then you need to change the tag to an Integer type. Now you can create a bit array in the Alarm trigger using LSBit.
Open the FactoryTalk View ME Help and search for topic "About array tags"

In either case, you will want to look at that tag in PanelBuilder and see how it was configured. Watch out for a bit array that starts in the middle of the word (ex. it does not starts at 0). Those you may not be able to convert exactly the same.
  Reply With Quote
Old December 12th, 2017, 02:59 PM   #3
IdealDan
Member
Malaysia

IdealDan is offline
 
Join Date: May 2017
Location: MA
Posts: 314
Quote:
Originally Posted by arlenjacobs View Post
If it's a single bit trigger, no problem. Change the tag to a Bool type in the tag database.
Then use analog trigger in the Alarm setup, value 1 in the messages tab.

If it's a LSBit, then you need to change the tag to an Integer type. Now you can create a bit array in the Alarm trigger using LSBit.
Open the FactoryTalk View ME Help and search for topic "About array tags"

In either case, you will want to look at that tag in PanelBuilder and see how it was configured. Watch out for a bit array that starts in the middle of the word (ex. it does not starts at 0). Those you may not be able to convert exactly the same.
Thanks Dear. and remain blessed. I will try that right away!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
FactoryTalk Historian SE Migration problem (2.1 to 3.01 version) nibed LIVE PLC Questions And Answers 0 November 26th, 2014 05:12 AM
PV Standard to Pv+ 600 Migration Issues gmondrax LIVE PLC Questions And Answers 1 December 10th, 2012 10:18 AM
PLC5 SLC500 migration to Controllogix felmed LIVE PLC Questions And Answers 4 July 29th, 2010 03:05 PM
WinCC migration orense LIVE PLC Questions And Answers 3 November 27th, 2008 09:42 AM
CMT - Common Migration Tool Alan Horn LIVE PLC Questions And Answers 0 September 5th, 2003 08:36 AM


All times are GMT -5. The time now is 06:38 PM.


.