plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old December 12th, 2017, 12:40 PM   #1
RBergmann
United States
RBergmann is offline
RBergmann's Avatar
MicroLogix 1400 MB TCP & RTU
Does anyone know if the MicroLogix 1400, Series B, can handle both Modbus RTU & Modbus TCP at the same time? I am working on a project that has existing RTU communications. I need to provide a chart recorder with two digital signals for alarm messages. However the customer purchased the chart recorder without digital inputs so I thought, since the 1400 can handle Modbus comms, maybe I could send the bit signal via TCP.
Does anyone have experience with this?
__________________
...rab
Old December 12th, 2017, 01:14 PM   #2
gclshortt
Canada
gclshortt is offline
gclshortt's Avatar
Yes this should work. Here are a couple of references for both Modbus RTU (RS485) and Modbus TCP (Ethernet).
http://www.plctalk.net/qanda/showthread.php?t=86796
http://www.plctalk.net/qanda/showthread.php?t=73953
http://www.plctalk.net/qanda/showthread.php?t=76852
Regards,
__________________
Garry
https://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
Old December 12th, 2017, 01:21 PM   #3
RBergmann
United States
RBergmann's Avatar
Regards,
None of these links tells me if the two protocols can be used in the same code, at the same time, in a MicroLogix 1400.
__________________
...rab
Old December 12th, 2017, 02:28 PM   #4
gclshortt
Canada
gclshortt's Avatar
https://www.mesta-automation.com/mod...crologix-1400/
The above thread shows an example of setting up both the serial and Ethernet ports with Modbus RTU and TCP respectfully.
This may help you out.
Regards,
__________________
Garry
Old December 12th, 2017, 07:22 PM   #5
Ken Roach
United States
Ken Roach is online now
Ken Roach's Avatar
The MicroLogix 1400 Series B can simultaneously support Modbus/TCP on the Ethernet port and Modbus RTU on a serial port.
The EtherNet/IP protocol also happily co-exists on the same Ethernet port with the Modbus/TCP client or server.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
micrologix 1400 plc communication with java suing ethernet Tcp ip mehulpopat12 LIVE PLC Questions And Answers 5 September 8th, 2014 02:43 AM
Modbus TCP communications with Micrologix 1400 H2Otbaker LIVE PLC Questions And Answers 6 April 13th, 2014 01:41 AM
Micrologix 1400 B Modbus TCP questions Hemlock LIVE PLC Questions And Answers 7 March 18th, 2014 11:15 AM
Comunications between Micrologix 1400 and Sew Movidrive-B d4n1_g LIVE PLC Questions And Answers 0 October 31st, 2013 05:19 PM
Micrologix 1400 + Panelview 550 + DH485 alexbeatle LIVE PLC Questions And Answers 2 September 13th, 2011 11:30 AM