Emergency Stop Pushbutton Design

Does anyone know the criteria/standards that walk you through the process of determining if Emergency Stop buttons need to be hardwired, or if they can just be defined on the PLC HMI?

I have a customer that needs to be perform certain E-Stop actions for their particular process application (specialty chemical industry), but they don't currently know if the buttons need to be hardwired (or if they can just be 'soft' buttons on an HMI).

Any input that you can provide would be greatly appreciated. Thanks in advance!
  Reply With Quote
Old December 15th, 2017, 10:02 AM   #2
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,407
If it's a software stop pushbutton, then, by definition, it is not an Emergency Stop.
__________________
  Reply With Quote
Old December 15th, 2017, 10:14 AM   #3
damica1
Member
United States

damica1 is offline
 
Join Date: Aug 2015
Location: Illinois
Posts: 534
Here's a .pdf from Rockwell!! I think everyone would benefit from this read?

http://literature.rockwellautomation...p008_-en-p.pdf
__________________
David M. Camp

Marshall Electric / https://mei-tech.com/monitor-and-control

Please Download from our download section "Monitor and Control" .pdf.
  Reply With Quote
Old December 15th, 2017, 10:17 AM   #4
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,908
Siemens has an instruction for the HMI interacting with the safety program (2 step process with confirmation), so hypothetically safety on the HMI isn't impossible.

That said, a button on the HMI is not a replacement for an E-Stop button, but if you're using a safety PLC it could potentially be incorporated as an additional measure.

In the US, NFPA 79 is the main safety code. Worldwide, you can take a look at a standard like IEC 61511.
  Reply With Quote
Old December 15th, 2017, 11:52 AM   #5
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,210
See nfpa 79 - Electrical standard for industrial machinery.

HMI (touchscreen) terminals can and do go bad - I have replaced several for that reason.

regards,
james
  Reply With Quote
Old December 15th, 2017, 12:11 PM   #6
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 224
Do both, have one hardwired and one controlled by software. E-stops are always hardwired cause the delay from software can cause safety issues.
  Reply With Quote
Old December 15th, 2017, 12:35 PM   #7
dogleg43
Member
United States

dogleg43 is offline
 
Join Date: Dec 2005
Location: Indiana
Posts: 299
Quote:
Originally Posted by alive15 View Post
Do both, have one hardwired and one controlled by software. E-stops are always hardwired cause the delay from software can cause safety issues.
I believe a lot of what is being stated in this thread needs to have an asterisk by it.

It would be incorrect to say that E-stops cannot be in software because safety PLC's do exist and I believe it would be OK to have E-stop software inside of them.

As far as having an E-stop PB on an HMI screen then PROBABLY the HMI would need to be a safety-rated device. I'm not sure they exist.
  Reply With Quote
Old December 15th, 2017, 12:41 PM   #8
kalabdel
Member
Canada

kalabdel is offline
 
Join Date: Feb 2015
Location: Ontario
Posts: 343
Quote:
Originally Posted by harryggianakis View Post
Does anyone know the criteria/standards that walk you through the process of determining if Emergency Stop buttons need to be hardwired, or if they can just be defined on the PLC HMI?

I have a customer that needs to be perform certain E-Stop actions for their particular process application (speciality chemical industry), but they don't currently know if the buttons need to be hardwired (or if they can just be 'soft' buttons on an HMI).

Any input that you can provide would be greatly appreciated. Thanks in advance!
I would first consider the application and the consequences of not being able to stop the equipment then I check electrical codes and last but not least personal and company liability.
  Reply With Quote
Old December 15th, 2017, 01:48 PM   #9
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,407
Quote:
Originally Posted by harryggianakis View Post
Does anyone know the criteria/standards that walk you through the process of determining if Emergency Stop buttons need to be hardwired, or if they can just be defined on the PLC HMI?

I have a customer that needs to be perform certain E-Stop actions for their particular process application (specialty chemical industry), but they don't currently know if the buttons need to be hardwired (or if they can just be 'soft' buttons on an HMI).

Any input that you can provide would be greatly appreciated. Thanks in advance!
You don't really clarify, but if your goal is simply to execute an immediate stop of various pieces of equipment to prevent a process train wreck, rather than to address safety concerns, then it would be fine to do that with an HMI pushbutton, but I wouldn't label it an "E-Stop".
__________________
  Reply With Quote
Old December 15th, 2017, 02:10 PM   #10
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,908
Quote:
Originally Posted by dogleg43 View Post
As far as having an E-stop PB on an HMI screen then PROBABLY the HMI would need to be a safety-rated device. I'm not sure they exist.
I have heard of HMIs with Estop pushbuttons built in. I've even heard of a SCADA system that billed itself as SIL2, although I have no idea what the application was. I haven't seen any machine HMIs rated to have a button on the screen act as an Estop.

HOWEVER, it seems reasonable to be able to have the safety system respond to a standard input IN ADDITION to the regular safety inputs/estops. Depending on your risk assessment, etc etc.
  Reply With Quote
Old December 15th, 2017, 03:09 PM   #11
harryggianakis
Member
United States

harryggianakis is offline
 
Join Date: Oct 2016
Location: Philadelphia, Pa
Posts: 20
Emergency Stop Pushbutton Design

Bit_Bucket_07

In answer to your question, yes we need to execute an immediate stop of various pieces of equipment because these actions will prevent safety related events from occurring

So, based on this, does that mean the E-Stop button must be hardwired, or (as kalabdel and mk42 indicated) does the decision really depend on the outcome of the risk assessment (which looks at the consequences, severity and risk associated with the relevant process related events that could occur)???

Looking forward to hearing everyone's thoughts again
  Reply With Quote
Old December 15th, 2017, 03:20 PM   #12
duckman
Member
United States

duckman is offline
 
Join Date: Sep 2013
Location: home
Posts: 243
IMHO, if you call it a E-Stop it needs to be hardwired, or call it a STOP and do what you want, but it comes back to the risk assessment.
To many people call a stop an E-stop, without understanding the issue they cause themselves by adding the E at the start.
  Reply With Quote
Old December 15th, 2017, 03:41 PM   #13
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,908
Quote:
Originally Posted by harryggianakis View Post
(as kalabdel and mk42 indicated) does the decision really depend on the outcome of the risk assessment (which looks at the consequences, severity and risk associated with the relevant process related events that could occur)???
The first thing you need to identify is what safety standard(s) you're trying to follow. From there you can start your risk assessment.

To be clear: I'm not aware of any situation in which a button on an HMI could replace (or even be called) an E-Stop button. However, it may be permissible for a button on an HMI to have a similar result (ie safely shut down a system).

E-stop is kind of a protected term, and a button usually needs to meet various requirements to qualify (I think someone linked a rockwell document somewhere in the thread that had some good details there). In addition, you really really shouldn't have any buttons that could conceivably confused as an Estop. If you have a red/yellow mushroom pushbutton as your start button, you're gonna have a bad time.
  Reply With Quote
Old December 15th, 2017, 03:55 PM   #14
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 224
Quote:
Originally Posted by dogleg43 View Post
I believe a lot of what is being stated in this thread needs to have an asterisk by it.

It would be incorrect to say that E-stops cannot be in software because safety PLC's do exist and I believe it would be OK to have E-stop software inside of them.

As far as having an E-stop PB on an HMI screen then PROBABLY the HMI would need to be a safety-rated device. I'm not sure they exist.
He is not using a safety PLC, so definitely needs a hardwired e-stop to prevent his safety-related issues from occurring. Since I've never used a safety PLC, I cannot say how well they work.
  Reply With Quote
Old December 15th, 2017, 04:33 PM   #15
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,384
You do not, ever, design an "Emergency Stop" pushbutton, unless you want to spend many thousands of pounds having it certified as an "Emergency Stop" device.

If "Emergency Stop" is what you want, you buy it in, from manufacturers that have gone through the expensive process of certification.

Of course you can, as others have suggested, design a "Stop" button, but you must never use a "Stop" button as an "Emergency Stop".

Be very, very, clear about the differences between the two, and the implications of using the wrong, inferior, or less safe, device or implementation in your applications.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Bottle line Joseca LIVE PLC Questions And Answers 43 September 8th, 2015 04:45 AM
E stop and PLC with HOLD or Pause leitmotif LIVE PLC Questions And Answers 5 February 20th, 2010 10:51 AM
MCR circuits required to be hardwired? cisco_kid LIVE PLC Questions And Answers 11 December 20th, 2007 09:09 AM
OT: Diodes in control circuits? plchacker LIVE PLC Questions And Answers 66 November 26th, 2007 05:52 PM
Manual/Auto jthornton LIVE PLC Questions And Answers 9 October 5th, 2006 12:40 PM


All times are GMT -5. The time now is 02:57 PM.


.