Going from 500 to 5000

Hi to all,
I have a good understanding for RsLogix 500 and would like to know the best way to start learning RsLogix 5000. I would appreciate help to let me know the best way to start learning RsLogix 5000. Thank you for your help in advance.

I appreciate it very much.

Maintenance
__________________
There are three kinds of people; those that make things happen, those that watch things happen and those who don't know what's happening.
  Reply With Quote
Old December 19th, 2017, 08:33 PM   #2
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,380
Key points....

The ladder program looks much the same, some new instructions to learn, some instructions lost, but about 99% will be understandable.

Probably the biggest hurdle to overcome is how your data is stored.

Logix5000 doesn't have "data tables", where your data is stored in elements of data files, e.g. N7:23 Instead, it has a pukka "tag database" (actually it has more than one, you will learn later). Your data is stored in the database(s) with names you define, so the tag-name can be as descriptive as you want it to be (up to an 80 character limit). That can be a large part of your "documentation", making the ladder easier to read and understand.

All the old favourite data types are supported, plus a few new ones that weren't available in Logix500, but some have been renamed to comply with IEC standards....

BOOL (was bit) - a memory storage for a single bit, 0 or 1
SINT (never existed) - 8-bit memory storage for numbers -128 to +127
INT (probably most familiar) - 16-bit memory storage for numbers -32768 to +32767
DINT (new to you) - 32-bit memory storage for numbers -2,147,483,648 to +2,147,483,647
REAL (was called Float) - 32-bit memory storage for floating point numbers +/-10^+/-38

Get your head round those 5 "Atomic" data-types, everything else you will see are "collections" or "structures" of those atomic types. You can even create your own data structures, called UDTs (User-Definable Types) - very convenient.

I had a "good understanding" of Logix5 and Logix500 when I was abruptly introduced to Logix5000, and I found the transition quite painless.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old December 19th, 2017, 09:42 PM   #3
willxfmr
Lifetime Supporting Member
United States

willxfmr is offline
 
Join Date: Nov 2013
Location: Wisconsin
Posts: 304
Take some time to research the AOI instruction. That was the one thing that really tripped me up going from 500 to 5K. The help file for the instruction is a good place to start, then when you are having a hard time sleeping, give this a read. http://literature.rockwellautomation...m010_-en-p.pdf
The other thing that was hard for me to wrap my head around, but is crucial to understand is the UDT (User Defined Data Type). They are very popular with programmers and engineers, but can be a bit confusing when you first encounter one. All in all, the transition is not too hard, and you will find that in time 5K is actually much easier to work with at the maintenance level.

Have fun!
Bubba.
__________________
“Now will come the nay-sayers with all the reasons why you shouldn't do this. Some of them are teachers, and some of us are doers. Besides, you have got to let the smoke out of this equipment every now and then, or it starts to clog up the chimney.”
~Lancie1
  Reply With Quote
Old December 19th, 2017, 09:49 PM   #4
thingstodo
Member
Canada

thingstodo is offline
 
Join Date: Feb 2012
Location: Saskatoon
Posts: 218
Quote:
Originally Posted by Maintenance Man View Post
Hi to all,
I have a good understanding for RsLogix 500 and would like to know the best way to start learning RsLogix 5000. I would appreciate help to let me know the best way to start learning RsLogix 5000. Thank you for your help in advance.

I appreciate it very much.

Maintenance
Agree with @Daba on data types

The ladder logic will be familiar. Logix has SFC, Structured text, and function block as well. They are each suited to different types of programming, depending on how you think when you program. They are IEC languages and there are lots of books on how to program with them.

As @willxfmr mentioned, another big thing is Add-On Instructions.

You make a subroutine, sort of like in a micrologix or a SLC. But the subroutine is called an AOI and you can define a local data structure that holds all of the information that is useful, and you can pass in tags and get tags back out, like making your own function block.

When you re-use some good ladder logic in a SLC, you normally have to make sure that there are timers, and counters, and integers, at specific addresses, that are available to be used. Or you need to change your old code to use different addresses and it sometimes causes it to stop working.

With the AOI, you don't need 'global' variables to pass stuff in and out. And you don't have to worry about passing in the wrong number of parameters and fault you PLC. You don't need to change anything. You call the AOI, send in tags of the correct type for your code, and your code just WORKS!

Ahh ... if ONLY you could change the code in an AOI without going offline, downloading to the PLC ... that would be truly AWESOME ... but I am talking about your journey, not mine Sorry about that !

I think the UDT is sort of like the data part of the AOI without the code. But that's just my interpretation

Last edited by thingstodo; December 19th, 2017 at 09:51 PM. Reason: Correct spelling and typos!
  Reply With Quote
Old December 19th, 2017, 09:55 PM   #5
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,380
Quote:
Originally Posted by thingstodo View Post

Ahh ... if ONLY you could change the code in an AOI without going offline, downloading to the PLC ... that would be truly AWESOME
AOI's cannot be changed online for many reasons. Usually the AOI is well-defined, well-tested, and "certified" before it is employed. Rockwell don't let you change the execution of their instructions, so why should you be able to change an AOI online. Way too dangerous if you get it wrong (incorrect, George)
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old December 20th, 2017, 07:49 AM   #6
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 482
Quote:
Originally Posted by daba View Post
Way too dangerous if you get it wrong (incorrect, George)
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old December 20th, 2017, 07:51 AM   #7
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 482
I hate that they got rid of the SCP instruction, but once you have the AOI it's no different. Just wish when you had the AOI installed, it would convert the old SCPs into the new SCPs when running the auto conversion instead of making them into long nonsensical CPT statements instead.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old December 20th, 2017, 08:07 AM   #8
RonJohn
Lifetime Supporting Member
United States

RonJohn is offline
 
RonJohn's Avatar
 
Join Date: Jul 2013
Location: NE Ohio
Posts: 428
One other big change is that I/O in the Logix family updates asynchronously to the program scan. For this reason, it is advised to buffer your inputs (at least) in order to get the same response as you had with the SLC.
  Reply With Quote
Old December 20th, 2017, 08:29 AM   #9
thingstodo
Member
Canada

thingstodo is offline
 
Join Date: Feb 2012
Location: Saskatoon
Posts: 218
Quote:
Originally Posted by daba View Post
AOI's cannot be changed online for many reasons. Usually the AOI is well-defined, well-tested, and "certified" before it is employed. Rockwell don't let you change the execution of their instructions, so why should you be able to change an AOI online. Way too dangerous if you get it wrong (incorrect, George)
I guess we'll have to agree to disagree on this one.

Or maybe you are kidding and I don't know you well enough? If you were kidding - ignore the rest of this message!

I have 'typical' motor and valve subroutines spread across 10 ControlLogix. The structures are all the same. The code is all the same. When I find some fringe condition that breaks my logic, I move to my offline system, make the changes required, test it, then copy the code to the affected ControlLogix and log the change. A simple checklist keeps track of where it has been deployed and where I still need to deploy it. It usually takes a couple of days to get it onto all of the ControlLogix in between other tasks. The 'typical' simple motor subroutine controls 450 motors across those 10 ControlLogix

I guess I could copy the AOI to a new name, and change several (450) AOI calls to accomplish the same thing with AOI. AOIs import much nicer. But I run a continuous process. There is usually 1 day a year (sometimes 2) that I can shut down all of the ControlLogix at the same time and change the AOI without changing the name. And I need that 1 day to do other stuff, like patching network switches, maintaining standby power, etc. Editing AOI online is definitely on my wish list
  Reply With Quote
Old December 20th, 2017, 10:00 AM   #10
LoganB
Lifetime Supporting Member
United States

LoganB is offline
 
Join Date: Apr 2017
Location: Michigan
Posts: 482
From my understanding, the point of AOIs is to segregate areas of the logic that shouldn't ever NEED to be edited. They are used to black box and/or protect. If you are finding that you often have to edit AOIs, you should probably have that logic as a subroutine or scheduled task instead of an AOI imo.
__________________
Present: Controls Engineer
Future: Skynet Engineer
  Reply With Quote
Old December 20th, 2017, 10:38 AM   #11
thingstodo
Member
Canada

thingstodo is offline
 
Join Date: Feb 2012
Location: Saskatoon
Posts: 218
Quote:
Originally Posted by LoganB View Post
From my understanding, the point of AOIs is to segregate areas of the logic that shouldn't ever NEED to be edited. They are used to black box and/or protect. If you are finding that you often have to edit AOIs, you should probably have that logic as a subroutine or scheduled task instead of an AOI imo.
Hmm. The Rockwell sales guys always seem disappointed when I tell them that I have not 'converted' to AOIs.

I get the impression that they think subroutines are 'old-fashioned' and 'obsolete'.

It is easier to document how to add a new motor if you just create a new instance of an AOI. Using a subroutine requires changing tags in a subroutine call .. and using the wrong number of parameters (simply typos) cause the ControlLogix to fault

We started with version 1 of our motor logic in 2003. We are up to version 8 now, with several a,b,c minor revisions between. The valves are more varied. We started with about a dozen different types and are down to 5 different types now, 1 or 2 limits, spring return or double-acting, etc.

Not sure if that counts as often?

IS there EVER code that should NEVER change? In my world, nothing that is still used is EVER done
  Reply With Quote
Old December 20th, 2017, 12:18 PM   #12
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,385
Quote:
Originally Posted by daba
...Way too dangerous if you get it wrong (incorrect, George)
Hehe. Now that's just silly. "it" implies you are referring to the task of manipulating an AOI online and not the person per se. So your statement is perfectly fine here as it implies more a potentially wrong task. You could have alternatively said "...Way too dangerous if you were to incorrectly edit an AOI online..." or similar. But that's just me being fancy. Nope, you haven't even offended me here.

At least I've got you thinking about it now 😉

On the subject of Add-On Instructions - don't forget that you can perform a Partial Import Online (PIO) since v17. This allows you to replace an existing AOI with a new offline edited AOI which may simply contain the update you require. Caveats - you cannot use the same name and you cannot online delete the existing AOI. At least not the last time I tried - v28.

I'm sure these topics are of interest to the OP but I'm wondering if this is jumping ahead too quickly here? Perhaps not?

Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Old December 20th, 2017, 04:24 PM   #13
Maintenance Man
Member
United States

Maintenance Man is offline
 
Join Date: Feb 2007
Location: Oklahoma
Posts: 248
Thank you to all.

Thank you so very much for all the great information. I appreciate it very much.
__________________
There are three kinds of people; those that make things happen, those that watch things happen and those who don't know what's happening.
  Reply With Quote
Old December 21st, 2017, 07:54 AM   #14
T Gibbs
Member
United States

T Gibbs is offline
 
Join Date: Jun 2012
Location: Morristown, TN
Posts: 379
I was thrown into 5000 a couple of years ago. I had no idea where to even start writing a program in it, so I went to youtube. I learned about the data files, how to create tags, and how to buffer the inputs to make them synchronous. After that I started programming and learned the software as I went, either from the help files or youtube.
  Reply With Quote
Old December 21st, 2017, 10:46 AM   #15
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,385
A small observation...
Quote:
Originally Posted by T Gibbs
...I learned about the data files, how to create tags, and how to buffer the inputs to make them synchronous...
For "5000", I think you meant "Data Types" here?
(BOOL, INT, DINT, REAL, STRING, etc.)

"Data Files" would be the reserve of "500".
(B3, T4, C5, R6, N7, F8, etc.)

Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RS Logix 500 - When loading is FactoryTalk Service Platform the same as RS Logix 5000 Rob S. LIVE PLC Questions And Answers 3 March 15th, 2017 08:14 AM
is it possible to program direct logic plcs with rs logix 500, 5000 kevin098 LIVE PLC Questions And Answers 2 November 25th, 2013 12:54 PM