Safety resets in a Guard Logix

I'm working on a project where the engineer at the plant is telling me you can use standard inputs for resets, for example resetting an E-stop block.

I've only used the PointIO safety a handful of times and with every application, all inputs related to safety were brought into the IB8S modules, including the resets. I attempted to use a controller tag from a non-safety input for the reset tag, but as I figured, the program does not allow it.

I don't disagree that a reset should be allowed to be controlled from a non-safety IO point, but from my experience, only safety IO is allowed in those routines.
  Reply With Quote
Old December 26th, 2017, 03:00 PM   #2
mobsoft
Member
United States

mobsoft is offline
 
Join Date: Jun 2013
Location: Bowling Green, KY USA
Posts: 32
Under the Logic menu you can map standard to safety tags.

Be sure to use the falling signal for your resets.
  Reply With Quote
Old December 26th, 2017, 03:02 PM   #3
lpc921
Member
New Zealand

lpc921 is offline
 
Join Date: Nov 2012
Location: Auckland
Posts: 15
I never used GuardLogix but it is surprising that the program doesn't allow standard tags in safety routines. I wonder if you are aware of the "Safety Tag Mapping" function?

Manual reset function does not need to be from a safety input if risk assessment agrees. However there are a few additional requirements for the reset function depending on which standards you are trying to comply with.
  Reply With Quote
Old December 26th, 2017, 03:09 PM   #4
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,885
I've seen standard bits used for resets in Siemens safety programs often.

If my little AB experience serves, I don't think standard tags can be read in safety at all. I think there's a way to set up mapping though.

If you have safe inputs to spare, having the reset there might be easiest, which is probably why you've always seen that before.
  Reply With Quote
Old December 27th, 2017, 05:12 AM   #5
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 744
Thanks, huge help guys!

(slightly embarrassed that I didn't know that existed)
  Reply With Quote
Old December 28th, 2017, 07:12 AM   #6
Keystone
Member
United States

Keystone is offline
 
Join Date: Aug 2008
Location: Indiana
Posts: 95
mobsoft is right on with the mapping.

To clarify with your reset button make sure it is using a One-Shot falling (OSF). This way the reset can not be maintained - only when the button is released. Prevents screw drivers that accidentally get stuck in the button to reset the machine.
__________________
Pressure - It can turn a lump of coal into a flawless diamond - or an average person into a perfect basketcase.
  Reply With Quote
Old December 28th, 2017, 10:23 AM   #7
Mispeld
Member
United States

Mispeld is offline
 
Mispeld's Avatar
 
Join Date: Feb 2017
Location: VA
Posts: 329
Quote:
Originally Posted by Keystone View Post
To clarify with your reset button make sure it is using a One-Shot falling (OSF). This way the reset can not be maintained - only when the button is released. Prevents screw drivers that accidentally get stuck in the button to reset the machine.
I get the distinction on using an edge signal for safety reset versus maintained. But is there a safety/functional difference if it is the rising edge versus the falling edge of a safety controller input?
  Reply With Quote
Old December 28th, 2017, 11:40 AM   #8
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,885
Quote:
Originally Posted by Mispeld View Post
I get the distinction on using an edge signal for safety reset versus maintained. But is there a safety/functional difference if it is the rising edge versus the falling edge of a safety controller input?
I was wondering that as well.

However, I have (in Siemens systems) seen rising edge used for resetting HW faults (like a short circuit in the card) then falling edge used for software resets (estop or light curtain).
  Reply With Quote
Old December 28th, 2017, 11:44 AM   #9
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,226
Quote:
Originally Posted by Keystone View Post
mobsoft is right on with the mapping.

To clarify with your reset button make sure it is using a One-Shot falling (OSF). This way the reset can not be maintained - only when the button is released. Prevents screw drivers that accidentally get stuck in the button to reset the machine.
I declare "stuck" push buttons as faults. It may actually point an electrician to a real problem.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old December 28th, 2017, 01:22 PM   #10
Keystone
Member
United States

Keystone is offline
 
Join Date: Aug 2008
Location: Indiana
Posts: 95
I have not read the full spec, I am sure there are more knowledge people who's posts I would be interested in. I was give the following.:

ISO 13849-1 stipulates instruction reset functions must occur on falling edge signals.
__________________
Pressure - It can turn a lump of coal into a flawless diamond - or an average person into a perfect basketcase.
  Reply With Quote
Old December 28th, 2017, 01:25 PM   #11
Keystone
Member
United States

Keystone is offline
 
Join Date: Aug 2008
Location: Indiana
Posts: 95
BTW - I am not declaring myself an expert in the safety PLC area. I have done a few systems with them and I like the functionality. Just passing on some thinks I was taught.
__________________
Pressure - It can turn a lump of coal into a flawless diamond - or an average person into a perfect basketcase.
  Reply With Quote
Old December 28th, 2017, 02:21 PM   #12
jacoffey85
Member
United States

jacoffey85 is offline
 
Join Date: Nov 2016
Location: NC
Posts: 68
Quote:
Originally Posted by mk42 View Post
I've seen standard bits used for resets in Siemens safety programs often.
Fun thing I learned a little while back with Tia Portal V13, don't use HMI reset buttons inside of the safety program directly. Make sure to map it to another bit inside of a standard function first, then use that bit inside of the safety logic.

Not having the HMI input synchronized with the scan cycle would sometimes give us a major PLC fault for the safety telegram error.
  Reply With Quote
Old January 2nd, 2018, 02:23 PM   #13
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 37
Not sure on guard logix but if using a 440C-CR30 programmable relay you can use a standard input from an expansion module for resets. However, in the software if a reset is held high for to long it will fault the relay. The same logic might be built into the guardlogix, i dont know.
  Reply With Quote
Old January 2nd, 2018, 02:23 PM   #14
phuz
Member
United States

phuz is offline
 
Join Date: Jun 2008
Location: Mohnton, PA
Posts: 744
Quote:
Originally Posted by _Dock_ View Post
Not sure on guard logix but if using a 440C-CR30 programmable relay you can use a standard input from an expansion module for resets. However, in the software if a reset is held high for to long it will fault the relay. The same logic might be built into the guardlogix, i dont know.
Yes, I've done this quite a few times on a 440C. Those are nice cheap little safety units!
  Reply With Quote
Old January 2nd, 2018, 02:42 PM   #15
_Dock_
Member
United States

_Dock_ is offline
 
Join Date: Sep 2015
Location: KY
Posts: 37
Quote:
Originally Posted by phuz View Post
Yes, I've done this quite a few times on a 440C. Those are nice cheap little safety units!
We use them alot as well, was just reviewing the banner version. They are slightly cheaper and one of the versions is expandable so we may be switching.

If you have any slight chance of needing to zone or expand after manufacturing then it is a no brainer.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
safety relay guard master e manikandan LIVE PLC Questions And Answers 3 September 19th, 2014 11:16 AM
Compact Logix Remote Racks The Plc Kid LIVE PLC Questions And Answers 10 September 29th, 2009 05:11 PM
Producer Consumer Messging between Control Logix & Compact Logix plcnovel LIVE PLC Questions And Answers 15 July 24th, 2006 10:04 AM
Relay guard master safety Alan B LIVE PLC Questions And Answers 5 December 5th, 2004 11:11 AM
E-Stop Circuit Wiring jshiepe LIVE PLC Questions And Answers 35 July 26th, 2004 09:46 AM


All times are GMT -5. The time now is 01:39 AM.


.