plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old December 27th, 2017, 08:54 AM   #1
Rahul3005
India
Rahul3005 is offline
Rahul3005's Avatar
Post burning smell from plc panel
I am using a Micrologix 1400 with 5 IO cards and i have done all Input and Output Connections properly,But when i Powered up the Panel for the very first time,a burning like smell was coming from panel ?
what may be the issue ?
There was no smoke visible and plc and all cards are working properly ?
Old December 27th, 2017, 09:40 AM   #2
scott.lawrence
United States
scott.lawrence is online now
something is burning, or at least started to... double check all wiring connections to make sure they are tight
Old December 27th, 2017, 02:10 PM   #3
kalabdel
Canada
kalabdel is offline
My first thought is disconnect everything except the PLC power supply and make sure it powers up fine and that smell is or is not there. Then decide based on the result what to do next. If the smell was there and the PLC stayed good and it was just paranoia then power down and start connecting wires again. If the PLC craps out out or goes up in flame then you have decided if it was defective to start with or your wiring did it and finally if the PLC works fine and there was no smell then it has to be wiring.
But I would never just power it again the way it is no matter how confident I am of my wiring. I've been wrong way too often to do that.
Old December 27th, 2017, 03:38 PM   #4
padees
United States
padees is offline
padees's Avatar
This is off topic, but I experienced a burning, kinda an electric smell today. I immediately turned off the electric heater in my office thinking that might be the issue, Nope! Next few seconds my right arm got bit... Looked at my insulated flannel shirt and it was smoldering. Picked up a spark from someone flicking the end off a cigarette.
Old December 28th, 2017, 05:20 AM   #5
sjohnson
United States
sjohnson is offline
sjohnson's Avatar
Not sure if it is Related but worth checking. Every time I smell a fire on a new panel it is usually caused by someone wiring 120Vac to a 24VDC circuit or 24VDC to a 24VAC circuit. 9 out of 10 someone put 120VAC to a 24VDC card..
Old December 28th, 2017, 07:11 AM   #6
widelto
Colombia
widelto is offline
widelto's Avatar
Rahul:
This happened to me several years ago, I forgot to take out that paper cover that is located on top of plcīs cpu, plc has no ventilation after taking it out that smell disappeared.
__________________
My two cents.
Old December 29th, 2017, 12:36 PM   #7
Rahul3005
India
Rahul3005's Avatar
I messed up with wiring connection,gave +24V to Input COMM.
Old December 29th, 2017, 05:21 PM   #8
g.mccormick
United States
g.mccormick is offline
Flyback diodes in backwards will let out little smoke.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Beginner in Panel Builder for PLC budiman LIVE PLC Questions And Answers 8 November 29th, 2013 04:04 PM
ASCII PLC -and dimmer panel Benton LIVE PLC Questions And Answers 1 March 1st, 2013 08:14 PM
update Cmore panel thru CLick PLC ?? Buzzkill LIVE PLC Questions And Answers 2 April 9th, 2012 08:25 AM
Quick PAnel communications to GE Rx3i PLC MadPLC LIVE PLC Questions And Answers 11 September 16th, 2011 03:31 PM
connect AB panel to simense PLC - OPC logicinn LIVE PLC Questions And Answers 0 August 14th, 2007 12:26 PM
