plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old December 28th, 2017, 04:28 AM   #1
rQx
Sweden
rQx is offline
Modbus adressing question
Hi!
We have a MicroLogix 1400 that is programmed to be readable to modbus tcp. This is working and I use for example adress 10001 to access coils and 40001 to access a register. I was learned that each table had 9999 values.
1-9999 output coil
10001-19999 input coil
30001-39999 input register
40001-49999 output register
Now we had a customer that wanted me to change our adressing so that it matched their standard modbus mapping. This is where my question arise.
They specified that they wanted to se:
PLC INPUTS at 1001 divided into 16 bits
PLC INPUTS at 1002 divided into 16 bits
PLC OUTPUTS at 0001 divided into 16 bits.
PLC OUTPUTS at 0002 divided into 16 bits.
This confuse me. In my world the adress should be 10001, 10002, 0001 and 0002? and that is a bit, not a word.
ALARM at 4001 divided into 16 bits ---- this make sense to me but not the address of 4001???
INTEGER at 4010 - also make sense but not the 4010 adress?
I'm no expert at all, what am I missing here?
I guess the adressing could be a typo, but the coils divided into 16 bits?
/Tim
Old December 28th, 2017, 08:20 AM   #2
damica1
United States
damica1 is offline
You may want to read this.
https://en.wikipedia.org/wiki/Modbus
__________________
David M. Camp
Marshall Electric / https://mei-tech.com/monitor-and-control
Please Download from our download section "Monitor and Control" .pdf.
Old December 28th, 2017, 08:40 AM   #3
rQx
Sweden
rQx is offline
Thanks for the response but that didn't clear things up. How do they want to access a coil at adress 1001 and 1002 and expect recieve 32 bits? 1001 and 1002 is only coils and bot registers. And also the address should in my mind be 10001 and 10002??
Old December 28th, 2017, 09:10 AM   #4
Pete.S.
United States
Pete.S. is offline
Wikipedia article is just a bunch of BS.
The real modbus tcp standard is here: http://modbus.org/specs.php
Your best bet is to ask your client what equipment they have on the other end. They are obviously confused.
Or they are trying to trick you into doing their job. It's the job of the modbus tvp client (their equipment) to be set up so that they are reading the correct addresses from the modbus tcp server (the PLC) and interpret them correctly.
PS. The thing that might confuse you (and everyone else) is that addresses that start with 3 & 4 indicates that it's a register. But the register address in modbus tcp is a word. So address 30001 is actually not a request for address 30001 but rather a request for the first address of the input register type 3.
Traditionally modbus uses 1-9999 for addresses but since it's a word the represents the address you could use larger addresses as well. There are more confusion to add because the first address is actually 0 but it is named 1.
Connecting two devices over modbus tcp is usually something that requires some time to figure out what settings is needed in either end. Some vendors are confused about the purpose of the slave address with modbus tcp (it has no purpose for standard modbus devices) so that is a thing that might end up causing problems.
Expect problems and some tweaking when the manufacturer even couldn't be bothered to be a member of the modbus organization. Rockwell isn't a member btw.
Old December 28th, 2017, 09:59 AM   #5
Aardwizz
United Kingdom
Aardwizz is offline
Aardwizz's Avatar
First off, we don't know what your client means either. You need to ask them for clarification.
But to make sure you are speaking the same language, a brief tutorial is in order. Caveat: I only work with Modsoft/Proworx/Concept/Unity every few years, just enough to go through the pain, but not enough to be a pro. Take everything I say with lots of salt.
First off, Modicon addressing is either 5 or 6 characters, 00001 or 000001. The leading character ('0','1','3', or '4') are roughly the equivalent of "O:", "I:, or "N7" -- a file identifier; the remainder of the number is parsed to match whether the system is configured for 5 or 6 characters. 30001 is the same as 300001. Many of the addresses in your post are only 4 characters, making it hard to know exactly what you're tying to say. Use at least 5 characters in all your correspondence from here on out, and include the leading 0 if talking about the 00000 - 09999 bit registers.
Quote:
They specified that they wanted to see:
As you correctly point out, 10001 is a bit address, and cannot be divided into 16 bits. Because "1001" is not a valid address, they could be that they are referring to 1001xx, and so what they are asking for is:
Map: I:0/0 to I:0/15 to 100101 to 100115
Map: I:1/0 to I:0/15 to 100201 to 100215
Map: O:2/0 to O:2/15 to 000101 to 000115
Map: O:3/0 to O:3/15 to 000201 to 000215
rather than I:0 & I:1 getting mapped to 100001 to 100032, etc.
But this is just a guess. ASK!
You are also correct that the 4000x is an unusual choice for registers. Typically in Modicon programming, the 0000x registers are used for internal coils, and you pick addresses outside the I/O range. Similarly, the 3000x addresses are used for internal integer & floating point math, HMI data and whatnot. IIRC, it is difficult to reference bits in 3000x and 4000x addresses. Unlike, say N7:0/1, 30001/1 is not valid for an -| |- instruction. (Salt, lots of salt).
(If) so, it would be weird to pack "alarms" in a 4000x register.
So perhaps they aren't talking about 1001xx and 4010xx, but about 001001 and 004010. In which case they really mean:
001xxxx = mapped inputs
002xxxx = mapped outputs
004xxxx = alarms
But it's impossible to be sure, with so little information.
Good luck
Old December 28th, 2017, 10:13 AM   #6
rQx
Sweden
rQx is offline
Thanks alot, I'm going to ask ofcourse but as I'm no expert I wanted to have some conversation about it before I questioned anything. This thread has now given me some more inputs so I can ask more relevant questions to my customer.
Thanks!
Old December 28th, 2017, 12:47 PM   #7
Saffa
New Zealand
Saffa is offline
Quote:
Not really, done all the time in remote SCADA systems where you need transmission efficiency over low bandwidth links, i.e. one read and one write per remote device.
Unity can reference bits in words using either the word.x nomenclature, or the WORD_TO_BIT function block.
Agree that the OPs client is asking for weird stuff though with their addressing
Old December 28th, 2017, 04:00 PM   #8
Pete.S.
United States
Pete.S. is offline
Packing the bits into words makes no difference for the modbus protocol because the bits are always packed into bytes anyway. All binary protocols do that.
A byte is the smallest amount of data that can be transferred over modbus rtu (serial) or modbus tcp (ethernet). So if you want to read the status of for example 256 flags (I/O or whatever) you will get 8 bytes of data back. So there no reason to pack bits into words for the sake of efficiency.
Old December 28th, 2017, 08:31 PM   #9
danw
United States
danw is offline
danw's Avatar
1. In Modbus addressing, a leading digit representing the address memory table is widely used as a help in identifying the type of data:
discrete input uses a leading or inferred numeral (0)
coil uses a leading numeral (1)
input register uses a leading number (3)
holding register uses a leading numeral (4)
I put the leading numeral in parentheses, because the leading numeral is NOT part of the Modbus message, it is an aid for human beings to interpret what type of data the address holds.
I do a lot of Scada and (4)0412 or (4)00412 address tells me the data is in a holding register because of the leading (4), which Function Code 03 addresses.
2.
a. 5 digit addressing
Your customer is likely 12 years behind the times because the 1979 era Modbus used address (0)0001-(0)9999 or (1)0001-(1)9999 addressing. This is known as 5 digit addressing.
b. 6 digit addressing
The more recent Modbus Application Protocols, V1.1a (June 4, 2004) and (V1.1b December 28, 2006) state in para 4.4 MODBUS
Addressing model:
"The MODBUS application protocol defines precisely PDU addressing rules.
In a MODBUS PDU each data is addressed from 0 to 65535."
(Each protocol further states (para 6.3) that the addressing range for the 03 read/write holding registers
is 0x0000 to 0xFFFF, [which is understood to be at the 40000 to 4FFFF (hex) or 40000 (decimal) to 465535 (decimal)])
This is known as 6 digit addressing and would translate to (0)00001-(0)65353 for FC01 or (1)00001-(1)65535 for FC02
c. The purpose of Modbus Function Code (FC) 01 is to read a bit-packed byte of data representing 8 sequentially numbered coils.
See these explanations from various sources. Caveat Emptor - correctly computing the initial offset and number of sequential coils is tedious and should not be done when consuming adult beverages.
Old December 29th, 2017, 12:50 AM   #10
Saffa
New Zealand
Saffa is offline
When you have a 2400 baud radio channel, doing a single read instead of a read for 0x and then another read for 4x makes a big difference. Radio key up time, protocol overhead etc all add up. Doing one read instead of two means i can get more sites on a single radio channel.
I have made plenty of money fixing systems implemented by people who have no understanding of how the transmission systems they have chosen actually work. People trying to do 4 reads from a site every second over a radio link via a repeater... it doesn't work... i wonder why!
Old December 29th, 2017, 04:17 AM   #11
rQx
Sweden
rQx is offline
Thanks alot for all replies. I'm feeling more confident that my understanding is correct and I can question the customer
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
PLC 5 and Modbus RTU Steve Cav LIVE PLC Questions And Answers 3 September 18th, 2012 03:21 PM
Modbus data question. dsking LIVE PLC Questions And Answers 4 May 21st, 2012 04:11 PM
Modbus Master not polling the Modbus Slave through an EtherNet/IP Connection mihiri LIVE PLC Questions And Answers 3 July 15th, 2010 03:41 AM
S7 315-2DP / 341 Modbus Master with Multiple Slaves richyr32gtr LIVE PLC Questions And Answers 1 October 14th, 2009 12:05 AM
CompactLogix RS-485 Modbus master question kittydog42 LIVE PLC Questions And Answers 2 March 26th, 2007 09:25 PM