Old December 29th, 2017, 11:07 AM   #1
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,395
Updating EDS files

I am working on a small project that involves a 1769-L16ER-BB1B PLC controlling a Powerflex 700H-E variable frequency drive over Ethernet. My client already has an existing system in operation, and they have asked me to basically duplicate the functionality of the existing program for the new mill installation.

So, I have created an offline program in which I added the drive to my IO tree. All of the tags for the drive were created in the process. I noticed, however, when looking at the existing program, that it contains at least two Input tags for the drive that don't exist in my offline program. They are VFD1:I.OutputCurrent and VFD1:I.OutputVoltage. I need to access these variables for display on my HMI. I assume that they are missing because an out of date version of the EDS file for the drive was employed when I added the drive in offline mode.

I know that I can use RS Linx to upload the EDS file from the drive when I get on-site, but will doing so modify my existing IO configuration, or do I need to delete the drive from my program altogether and then add it back after uploading the EDS file from the drive?
__________________
  Reply With Quote
Old December 29th, 2017, 12:36 PM   #2
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,922
The issue is the configuration of the DataLinks, rather than the EDS file or drive Add-On Profile.

In your Studio 5000 project, go into the PowerFlex 700H object in the I/O tree and look at the Module Definition section. Click on that "Change" button.

You want to select the "Parameters via DataLinks" connection type.

You'll have to enable DataLink A, and then select the Output Current and Output Voltage from the pull-down lists on the Input Data side.

Studio 5000 will then create a new Data Type that has those named sub-elements in it, and switch your AC drive object to using that new Data Type.

For kicks, go into the Data Types folder and look at the two different drive-related data types. The original one created by default will just have the discrete command/status and the reference/feedback. The new one will have the .OutputCurrent and .OutputVoltage named elements.
  Reply With Quote
Old December 31st, 2017, 06:10 PM   #3
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,395
Quote:
Originally Posted by Ken Roach View Post
The issue is the configuration of the DataLinks, rather than the EDS file or drive Add-On Profile.

In your Studio 5000 project, go into the PowerFlex 700H object in the I/O tree and look at the Module Definition section. Click on that "Change" button.

You want to select the "Parameters via DataLinks" connection type.

You'll have to enable DataLink A, and then select the Output Current and Output Voltage from the pull-down lists on the Input Data side.

Studio 5000 will then create a new Data Type that has those named sub-elements in it, and switch your AC drive object to using that new Data Type.

For kicks, go into the Data Types folder and look at the two different drive-related data types. The original one created by default will just have the discrete command/status and the reference/feedback. The new one will have the .OutputCurrent and .OutputVoltage named elements.
I've been away for a while. Thanks for the prompt response!
__________________
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
1734-IB8S EDS file jgebhardt LIVE PLC Questions And Answers 23 August 10th, 2017 10:30 AM
EDS files in TwinCAT 3 busarider29 LIVE PLC Questions And Answers 2 April 8th, 2016 02:28 PM