Hi,
I'm currently putting together a schedule to bring all our compact and controllogix processors up to a standard firmware level, and then attack the PV+'s.
I currently have some new equipment that I standardised on V30 for Studio and V9.0 for FTVME, so that will be the level I will go for. I probably have around 30-40 processors or more to update the firmware on, and in some instances swap out the L32E's for L33-ER's. The current firmware varies from V19, V20.13, V20.03, a couple V21's V24 and V28.
I am seeking out advice or recommendations (even horror stories) on how this is best performed. I have been looking at the "comparability checker" on the RA site as each processor has multiple drives, HMI's, some motion, remote I/O etc and i want to make sure I don't get caught out with incompatibility issues. Many years ago I upgraded an L32E from V16 to V19 when V19 had been out a good 6 months, only to find the PV would lock up and do the strangest things. so this is something I want to avoid having happen.
Any input gratefully received.
Rob
__________________
"So far as is reasonably practicable
"Not everything that can be counted counts and not everything that counts can be counted"
Albert Einstein
Old January 2nd, 2018, 12:09 AM   #2
janner_10
Supporting Member
United Kingdom
janner_10 is offline
If it were me and your not getting any problems, if it isn't broken, then don't try and fix it.
Yes it's lovely to have everything on the same firmware and only carry the one laptop or install the one VM, but you have to measure the risk v reward.
I speak from experience, that just leaving something alone that was working fine, would of avoided a lot of pain and downtime!
Old January 2nd, 2018, 07:39 AM   #3
bornwild
Member
Saudi Arabia
bornwild is offline
i agree with janeer. Leave it as it is. Do not upgragde if you dont have any issues.
Old January 2nd, 2018, 10:37 AM   #4
AustralIan
Member
United Kingdom
AustralIan is online now
If you want to avoid problems, set everything up in the workshop and run a quick acceptance test before putting on the shop floor. Make it permanentish so you have a test bay ready to go in the future.
Things to look out for:
L33 is much faster to execute than a L32, so potentially timing issues.
V30 does something different with ethernet/IP from V19, so you may have to upgrade the panel at the same time. If you want to do a phased approach of processor first then hmi later, definitely test both scenarios in your test bench.
Enjoy that feeling of having the 4th S of the 5S methodology (Standardise) until next year when you buy equipment that comes with V31.
Is now a good time to point out that Windows 7 is out of extended support in 2 years time?
Reply
Jump to Live PLC Question and Answer Forum
Bookmarks
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Similar Topics
Thread Thread Starter Forum Replies Last Post
Firmware Questions slickfix LIVE PLC Questions And Answers 1 October 11th, 2016 04:39 PM
CompactLogix Firmware Update and DeviceNet PLCstarter1884 LIVE PLC Questions And Answers 2 February 15th, 2016 11:24 AM
1769-L32E Compactlogix Firmware slickfix2 LIVE PLC Questions And Answers 3 August 13th, 2015 05:16 PM
panelview550 firmware upgrade problem wolf3000 LIVE PLC Questions And Answers 1 January 26th, 2011 02:16 PM
Upgrading the firmware version on my PanelView 900 (2711-T9C1) a_lo1204 LIVE PLC Questions And Answers 4 July 25th, 2008 11:57 PM