plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old January 2nd, 2018, 01:01 PM   #1
bodoo23
Turkey
bodoo23 is offline
RPI & Periodic Event
I am new in programming. There are two things I am wondering about
1- if we set RPI of a module 20ms and if the scan time is for example 70ms what would happen ? PLC will get values from module in the beginning and process these values in logic but what happen after 20ms when plc get new values from module in the same time scan is going on ? Can it use these values or it will ignore second (2x20ms) values and will use third(3x20ms) values in the second scan(after 70ms)
2-The second question is similar actually. when the period of periodic task is 10ms and scan time is 25ms. are the inputs and outputs used in periodic task being updated in every 10ms or it is like other values and need to be wait for the scan to be completed ? if they are like the values used in continuous tasks and just to be updated before and after scans. What are the advantageous of using periodic tasks ?
I hope my questions were clear since I am not very good at english I might not clarify well. Thanks
Old January 2nd, 2018, 01:42 PM   #2
RonJohn
United States
RonJohn is offline
RonJohn's Avatar
Welcome to the forum bodoo23! Let me see if I understand correctly. You didn't specify which processor you are using, so I will discuss from the perspective of an A-B Logix based controller (other types may differ).
1. I'm not sure what you mean by scan time - it sounds like you're saying the program takes 70ms to complete a scan. In that case, the data will get updated every 20ms (based on RPI). There is no guarantee when the data will update unless you choose to buffer the input data. For example, I buffer my data at the beginning of each program scan and only use the buffer tags throughout my program. This ensures that the input data is not changing somewhere mid-scan.
2. The advantage of using a periodic task rather than a continuous task is that you know exactly how often the task will execute. Also, continuous task scan time will increase as the size of the program increases but a 10ms periodic task will execute every 10ms even as program size increases. Now if you have a 10ms task that takes 25ms to scan, this will create an error. Periodic task time must be greater than the actual task scan time.
For a good discussion of RPI, RTS and other such settings, check out THIS thread from the forum a few years ago
Old January 2nd, 2018, 01:52 PM   #3
bodoo23
Turkey
bodoo23 is offline
Hi RonJohn. Thanks for answers. As I have known by now PLC first read inputs then process logic and write the outputs and the input values cant be updated in process of logic(It will remain the same value for this cycle even if the value changes during this scan). So now I see my understanding was wrong. If it changes in the mid of scan, it is updated immediately even if it is a physical input ?
Thanks again.
Old January 2nd, 2018, 02:00 PM   #4
Ron Beaufort
United States
Ron Beaufort is offline
Ron Beaufort's Avatar
this thread might also be helpful to you ...
http://www.plctalk.net/qanda/showthr...7&postcount=61
it gives some simple "test" programs that you can experiment with - so that you can discover how these "update" features work on your own ...
welcome to the forum - and your English is perfectly understandable ...
__________________
2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
I once was lost, but now am found, was blind, but now I see.
Old January 2nd, 2018, 02:01 PM   #5
RonJohn
United States
RonJohn is offline
RonJohn's Avatar
Quote:
This depends on which controller you are using. **If you tell us what you're working with, we can give you a more clear answer.
As I stated initially, my example used an A-B Logix based controller. In these, the inputs update asynchronously to program scan. With an A-B SLC500 or PLC5, the IO updates synchronously at the end of each program scan. For the SLC or PLC5, input buffering was not necessary.
Old January 2nd, 2018, 02:05 PM   #6
bodoo23
Turkey
bodoo23 is offline
I am working with 1756-L62 plc.
Old January 2nd, 2018, 02:14 PM   #7
RonJohn
United States
RonJohn is offline
RonJohn's Avatar
OK, so a 1756-L62 will scan the IO asynchronous to (not necessarily in step with) the program scan since that is a ControlLogix processor. For many of us who started our careers with SLC500 or PLC5, this was an adjustment for us also.
I agree with Ron Beaufort that your English is good - much better than my Turkish! Let me encourage you to use the forum search for a lot of useful information and feel free to post questions as we are all learning.
Old January 2nd, 2018, 02:28 PM   #8
bodoo23
Turkey
bodoo23 is offline
Thank you both for answers & kindness. I am really eager to learn and now I feel like I am talking with my friends. It will make me feel free to ask questions. I will keep searching here.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Parametre assignment error Palnivelmoorthy87 LIVE PLC Questions And Answers 1 October 20th, 2014 07:51 AM
S7-314 cpu and SM332 I/o error akrogh24 LIVE PLC Questions And Answers 14 March 10th, 2014 08:25 PM
All the light on s7-400 panel flashing leon.LEE LIVE PLC Questions And Answers 2 January 8th, 2009 10:06 AM
FC AG_SEND and AG_RECEIVE cfbosch LIVE PLC Questions And Answers 10 December 3rd, 2008 03:00 AM
Periodic event & Event in RSView ckchew666 LIVE PLC Questions And Answers 1 October 8th, 2004 07:37 AM