I've got a AB ControlLogix that I'm gonna be installing into a smaller chassis and upgrading its firmware. I've never done so before so I want to know the dangers and anything I should know about before time. Is this all fairly standard, nothing to worry about?
 
I've got a AB ControlLogix that I'm gonna be installing into a smaller chassis and upgrading its firmware. I've never done so before so I want to know the dangers and anything I should know about before time. Is this all fairly standard, nothing to worry about?

Is the ControlLogix new, or is there a program loaded in it? If there is already a program loaded in it, then make sure you upload the program first so you have a backup. Also, if you are moving it to a smaller rack, you may have to update the rack size in the program (RSLogix5000/Studio5000), if there is already a program loaded in it.
 
You don't want to lose comms when doing a firmware change (power loss, cable gets disconnected, etc)... it can brick the controller
 

Similar Topics

I have a 1756-L62 processor in use on a system. I want to replace it with a 1756-L73. I need to upgrade the firmware in the L73. Can I do this...
Replies
5
Views
7,880
Hey guys, We're updating our PLC5s to ControlLogix racks. We have two PLC5s that currently perform very similar functions, but for different parts...
Replies
9
Views
3,155
I have a large process running. 4 ControlLogix Processors, multiple remote I/O Racks, 3 or 4 devicenet bridges, all communicating through...
Replies
19
Views
5,218
Hi guys, We've a customer plant running about 10 sets of PLC 5 redundant, some of them has a few IO rack due to large quantity of IOs in the...
Replies
3
Views
5,815
Hi, I am upgrading a Wonderware SCADA form version 9.5 to version 23. I am able to migrate all the graphic, but when to activate the runtime this...
Replies
8
Views
336
Back
Top Bottom