First Scan reset with Compact/Controllogix

My new friend Ron Beaufort got me thinking about the issues with using OTL's in regards to a power cycle. While you can use a first scan bit (s:fs) to clear entire output tables, what about non aliased/"internal" bits?

Is there an (easy) way to set all OTL's to 0 on first scan? (Currently experimenting on CompactLogix system)
  Reply With Quote
Old January 6th, 2018, 05:27 PM   #2
lpc921
Member
New Zealand

lpc921 is offline
 
Join Date: Nov 2012
Location: Auckland
Posts: 18
I just create an initialisation routine and in it manually create OTUs for each bit I need to clear on power-up. That's one of the reasons why OTE should be preferred over OTL/OTU.
  Reply With Quote
Old January 7th, 2018, 12:52 AM   #3
Jerry Ferrell
Member
United States

Jerry Ferrell is offline
 
Join Date: Jan 2018
Location: Minnesota
Posts: 2
OTL's vs OTE

I've been working a lot with Beckhoff and Modicon where you can use an initialization value on power up. But from now on with Allen Bradley I think I have to swear off OTL's completely because of not having the control of them at power up. (Without extra programming) With AB I think latch branches are the only way to go.
  Reply With Quote
Old January 7th, 2018, 01:30 AM   #4
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,981
Quote:
Originally Posted by Jerry Ferrell View Post
I've been working a lot with Beckhoff and Modicon where you can use an initialization value on power up. But from now on with Allen Bradley I think I have to swear off OTL's completely because of not having the control of them at power up. (Without extra programming) With AB I think latch branches are the only way to go.
You should use OTL for boolean things that need to be remembered through a power cycle. They also have a few other good applications.

They are often abused, and it is generally better to use a sealed in OTE for things you want the PLC to turn off on first scan.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old January 7th, 2018, 08:11 AM   #5
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,461
one size does not fit all ...

here's some light reading material from days gone by ...

http://www.plctalk.net/qanda/showthr...27&postcount=1

quick summary:

sometimes you want the machine to REMEMBER that there is a "part in place" or that there is a "log in position B" ...

Seal-In type rungs might work PERFECTLY for these types of situations AS LONG AS THE POWER STAYS ON in normal day-to-day operations ...

the big question becomes: "Will the machine be able to REMEMBER those conditions when the power is finally restored after a power failure?" ...

so ...

the machine works and it "meets the specifications" ... the programmer gets paid and goes on to another project ... time marches on ... and then one day the power fails while the machine is operating ... later the power comes back on again - and the machinery crashes ...

why? ...

obviously the damage was caused by the "POWER SURGE" associated with the power failure ...

or ...

but maybe NOT so obvious is that the programmer never considered whether a "seal-in" rung would act differently than a "latched/unlatched" arrangement ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.


Last edited by Ron Beaufort; January 7th, 2018 at 08:27 AM.
  Reply With Quote
Old January 7th, 2018, 08:20 AM   #6
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,461
and while we're on the subject - here's a thought for those of you who prefer STX (Structured Text Programming) ...

you might want to consider the difference between

:=

(which is a "retentive" assignment)

and

[:=]

(which is a "non-retentive" assignment)

many STX programmers never know there's a difference - until the Allen-Bradley has an unexpected "go to run" situation ... depending on the type of machinery being discussed, we could potentially have a "lawyer level" situation on our hands ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.


Last edited by Ron Beaufort; January 7th, 2018 at 08:30 AM.
  Reply With Quote
Old January 8th, 2018, 08:07 AM   #7
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,401
Another consideration if you want to use S:FS to reset latched bits....

Each Program has its own S:FS bit, that is acted upon on the first pass of that program.

If an early program inspects a latched bit from a program that is later in the program schedule, or from a program that is inhibited, that bit will not yet have been reset by the S:FS code.

This could lead to unexpected operation.

My pictures show two programs, Program1 and Program2....
Both Program1_BitBox and Program2_BitBox are controller-scoped tags...

I start, in Program mode, with both bits toggled ON, and Trap_Bit OFF.

When I change to RUN mode, you can see that Program1 sees Program2_BitBox as ON, and latches the Trap_Bit. It is not until Program2 is executed that Program2_BitBox is unlatched.

This could have dangerous consequences, depending on how the bits are inter-related between programs.

As Ron has pointed out, it's a case of "horses for courses"... If you definitely want a bit to be turned OFF when the processor enters Run-mode, then program it as "seal-in" latch logic. If you definitely want the bit to retain its state when the processor restarts, then use OTL/OTU combinations of the bit in your logic.
Attached Images
File Type: jpg 2018-01-08_130553.jpg (90.7 KB, 15 views)
File Type: jpg 2018-01-08_130613.jpg (89.3 KB, 13 views)
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old January 8th, 2018, 10:58 AM   #8
keshik
Lifetime Supporting Member
Canada

keshik is offline
 
Join Date: Jun 2011
Location: Portland, OR
Posts: 401
Quote:
Originally Posted by Ron Beaufort View Post
and while we're on the subject - here's a thought for those of you who prefer STX (Structured Text Programming) ...

you might want to consider the difference between

:=

(which is a "retentive" assignment)

and

[:=]

(which is a "non-retentive" assignment)

many STX programmers never know there's a difference - until the Allen-Bradley has an unexpected "go to run" situation ... depending on the type of machinery being discussed, we could potentially have a "lawyer level" situation on our hands ...
Ron - I assume that this is specific for the Allen-Bradley implementation, correct?

I remember with Wago and Schneider having to locate the tag in retentive memory for it to be retained (using any Codesys programming language).
  Reply With Quote
Old January 8th, 2018, 12:46 PM   #9
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 235
I've asked a similar question; a few people posted some good examples in my thread here: http://www.plctalk.net/qanda/showthr...=103493&page=1
  Reply With Quote
Old January 9th, 2018, 06:33 AM   #10
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,461
question from keshik:

Quote:
Ron - I assume that this is specific for the Allen-Bradley implementation, correct?
yes, and more specifically - with the RSLogix/Studio 5000 software ... for the (much) older Allen-Bradley PLC-5 systems using RSLogix 5 software, the "retentive" assignments in Structured Text programming were taken care of differently ... see Example H ...

http://www.plctalk.net/qanda/showthr...9&postcount=21

as we've already noticed, one size does NOT fit all - not even when considering different platforms from the SAME manufacturer of PLCs ...

and for those who might be interested, here's a thread from WAY BACK that compares Allen-Bradley's method with Automation Direct's method of handling retentive and non-retentive memory ... just for comparison ...

http://www.plctalk.net/qanda/showthr...86&postcount=1

note: this is the sort of thing that I find amusing when folks say: "If you can program ONE make of PLC - then you can program them ALL" ... that's sort of like saying: "If you can speak English, then you can also speak German, Spanish, or whatever" ... well, maybe - but not without a considerable amount of work and effort ...

party on ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.


Last edited by Ron Beaufort; January 9th, 2018 at 06:55 AM.
  Reply With Quote
Old January 9th, 2018, 07:56 AM   #11
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,401
It is also worth noting that even instructions can behave differently, from the same manufacturer, across different platforms.

Here's just one example....

The instruction that decodes a 4-bit Binary Coded input into a number is called FRD (From BCD).

In Logix500 (SLC etc.), it will only recognize the encoded numbers 0 to 9, anything else presented on the 4 inputs is flagged as an "overflow", and the overflow trap bit is set. This can cause problems with the processor faulting out, unless the overflow trap bit is reset before the end of the ladder scan. On a BCD thumbwheel switch, (depending on the manufacturer), it is possible to generate "illegal" BCD codes as the wiper moves between two indents.

In Logix5000 (ControlLogix, CompactLogix etc.), FRD decodes the whole of the possible 4-bit combinations, and then gives the decimal number equivalent to the 4-bit HEX (not BCD) code.

0 to 9 works as expected....

0000 = 0
...
1001 = 9

but going on from there, this is what happens...

1010 = 10
1011 = 11
1100 = 12
1101 = 13
1110 = 14
1111 = 15

In effect the FRD is actually an "FRH" (From HEX).

I have seen Logix5000 controllers major fault if the "BCD" 0-9 is used as the index into a 10-element array, because the non-BCD numbers (which can occur between the 0-9 indents), are decoded, and the index tries to address an array element that doesn't exist.

You have to pay special attention when up-converting Logix500 to Logix5000
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens S7-200 to S7-1200 Counter reset BryanG LIVE PLC Questions And Answers 11 April 14th, 2011 04:31 AM
SLC 5/05 Scan Time vs Input Pulse robertmee LIVE PLC Questions And Answers 11 May 20th, 2008 11:54 PM
New File in Downloads - M91 Event Scan TimothyMoulder LIVE PLC Questions And Answers 1 February 8th, 2006 01:05 PM
Compare register from one scan to another scan lostpatrol1 LIVE PLC Questions And Answers 7 April 22nd, 2003 01:29 PM
Sequential Logic to AB PLC Tze LIVE PLC Questions And Answers 7 January 4th, 2003 12:41 PM


All times are GMT -5. The time now is 04:38 PM.


.