Old January 7th, 2018, 03:48 PM   #1
Slwagner73
Supporting Member
United States
Slwagner73 is offline
Dumb Newbee Question
So, just to start, I am not an engineer, but a sort-of self taught programmer.
And I am familiar with RSLogix-500, but I am just learning Studio-5000.
Here goes my question:
I would like to use a Panelview 800 HMI with a CompactLogix 1769-L27ERM PLC and a 1734-AENTR Remote I-O.
I used CCW to program the HMI, and I was sure to use the correct name for the PLC, and added the "192.168.0.2,1,0" per the manual.
I can see the HMI in RSLinks, and I can see the Remote I-O there also, but in the program, I get the stupid caution symbol for each of these devices.
And neither of them will do anything.
I get numerous errors every time I boot the HMI, and following the directions from the Rockwell site gets me nowhere.
Are these just not compatible?
Thanks for your time:
Scott
Old January 7th, 2018, 04:03 PM   #2
AustralIan
United Kingdom
AustralIan is offline
What are the errors?
- What are the errors on the HMI?
- What are the errors when you click on the stupid caution symbol?
Do you have firmware version 4.012 or later of the HMI? if not upgrade.
There are some other useful pointers and links on this technote #774421, access level everyone (you will need to sign up for an account though).
https://rockwellautomation.custhelp....il/a_id/774421
Sometimes the knowledgebase can be easier and more frank than the user manuals.
Old January 7th, 2018, 04:19 PM   #3
Slwagner73
Supporting Member
United States
AustralIan:
Thanks for the reply.
On the HMI, I have version 4.013.
And the error messages I get are for every tag. "2ata Access Error for Alias "Okay to Run the Pump, Controller PLC1, Address is PLC1:MainProgram.Okay_To_Run_Bit, Communication Flag is 0. And it is the same for all of the Tags.
As for the Studio5000 error:
For the Remote I-O, it is (Code 16#0204)Connection Request Error Connection Request Timed Out.
For the HMI error, (Code 16#0315) Connection Request Error: Invalid segment type.
I'm lost...
Old January 7th, 2018, 04:29 PM   #4
Slwagner73
Supporting Member
United States
And after following the link you provided, it would seem that making this work together is way above my head.
I have no idea what Modbus TCP to Ethernet/IP gateway is.
So, I guess I'll go back to the more expensive PanelView.
But thanks for your time.
Old January 7th, 2018, 04:41 PM   #5
Cellularscada
United States
Cellularscada is offline
Panelview 800 will only work with the compactlogix L1 controller...
Old January 7th, 2018, 04:44 PM   #6
Slwagner73
Supporting Member
United States
Well, that just sucks. Thanks a lot Allen-Bradley....
Old January 7th, 2018, 04:57 PM   #7
Cellularscada
United States
I just done more research into that....I may be wrong... I did read where the latest firmware for panelview 800 does support th L2,L3 controller....I will read more..
Old January 7th, 2018, 05:03 PM   #8
Cellularscada
United States
Im sorry...I'm wrong.... went to AB web site... it does it support L1, L2, and L3 with latest firmware
Old January 7th, 2018, 05:41 PM   #9
AustralIan
United Kingdom
I suspect you do not need the HMI in the I/O tree, as the HMI asks the PLC for info not the other way around.
Connection request timeout means that it isn't getting anything at all back from the I/O, not even a "nope, you asked for the wrong module".
You mention you can see the HMI and Remote I/O in RSLinx, can you also see the PLC?
Double check you have entered the PLC's IP address that you can see from RSLinx in the panelview project.
Double check that you have entered the right IP address, the right adapter and right firmware version in the AENTR.
There is something simple we have missed here, the PV800 to CPLX with AENTR is a fairly standard and well tested setup.
Did anything from answer ID 66192 help?:
https://rockwellautomation.custhelp....d/66192/page/1
Old January 7th, 2018, 06:26 PM   #10
Geospark
Ireland
Geospark is offline
Geospark's Avatar
Hi and Welcome to the Forum!
I'm just dealing with the communications between the PanelView 800 and the L2 controller here, as the distributed I/O is a separate issue...
Perhaps this previous thread might assist you in setting up or double-checking some of the basic requirements...
Communication problem between panelview 800 to compactlogix l2 controller
Any questions you may have on that thread's contents would be best addressed here.
Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
Old January 21st, 2018, 08:55 AM   #11
Slwagner73
Supporting Member
United States
Well, I am still lost. I have checked, rechecked, erased and started over, and still nothing.
I have checked the IP address, made sure I can see everything in RSLink, made sure the controller was addressed in CCW correctly, and still I get the address is zero error.
Is there anywhere I could send copies of the programs to see if maybe someone could see just what I have FUBARed?
Old January 21st, 2018, 09:48 AM   #12
thingstodo
Canada
thingstodo is offline
Quote:
Originally Posted by Slwagner73 View Post
AustralIan:
I'm lost...
I'm a bit out of date on the Compactlogix in general, and Panelview stuff as well. Back in the day, you had to use Controller scoped tags (PLC1:Okay_To_Run_Bit), which all of the programs on the PLC, and anything else on communications could see. I don't remember being able to access tags in PLC1:MainProgram .... but that was years ago and things may have changed.
We are running ControlLogix now. Our panelviews are on ethernet and were current firmware when we put them in ... when we commissioned them but someone else programmed them ... and they read and write our tags in Controller Scope because that's always worked for me.
Old January 21st, 2018, 09:52 AM   #13
Maxkling
United States
Maxkling is offline
Put everything you got in a folder and zip it. The post as attachment.
Can you go over how everything is plugged into each other? Are you using a switch?
Old January 21st, 2018, 10:48 AM   #14
Slwagner73
Supporting Member
United States
Well, even zipped, it says the file is too big to up load. Maybe I don't know how to correctly zip a file?
Scott
Old January 22nd, 2018, 10:09 PM   #15
bill4807
United States
bill4807 is offline
I just went through this. (Data access error)
I was using an L24er with a PV800.
Always had communications errors with a majority of my tags. They were configured properly. Called rockwell, no solution.
I ended up putting a relay from a PLC output to power ON the HMI. Because I noticed that whenever I restart the HMI on its own without powering down the PLC I got no messages..
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Dumb Question Tarheel LIVE PLC Questions And Answers 13 June 27th, 2007 07:44 PM
Integrator Business Question mjrx LIVE PLC Questions And Answers 3 April 12th, 2007 06:37 AM
How to Ask Questions The Smart Way Ken Roach LIVE PLC Questions And Answers 14 March 26th, 2007 09:12 AM
Really Dumb question CroCop LIVE PLC Questions And Answers 3 November 19th, 2006 05:37 PM
1756-ENBT Yellow Question Mark Coachman LIVE PLC Questions And Answers 4 October 9th, 2006 05:47 PM