Controlling DC drive with Siemens PLC S7-1500
samvivi7
Apr 2016
NJ
50
Hey Guy,
I would like to control the (attached) DC motor drive with my S7-1500 PLC through an HMI.
when i say control i mean only the speed.
any help is appreciated.
Thank you,
Sam
This controller appears to be very basic and designed for control using a 10k potentiometer. You would need a motorized potentiometer like high end stereo equipment used once upon a time.
Personally I'd look at finding DC motor controllers that accept a 0-10V or 4-20mA reference signal
Depends what the control voltage is returning on S2, if its 0v to 10v then you can simply substitute this with a PLC analogue output.
Measure across S1 and S3 and see if it's 10v.
Janner10
thanks for the help. So i called the manufacturer and its 5V out and also they want me to use a Analog interface and isolation module.
since i cant spend any money on this (project) i will have to let things be.
thanks for all the help guys,
Sam
How many "Relay Outputs" can you dedicate to control the motor speed?
Build a Voltage Dividing Network, Example: put 5 resisters in series (lets say 2k each).
That would only cost a couple of dollars!
Now program the drive to have a min-max speed of let's 30hz - 70hz.
Now wire each PLC relay output in between each resistor, now just program your hmi with a button for 70hz, then one for 60hz then one for 50hz then one for 40hz then one for 30hz, with each turning on the associated relay output.
This would at least allow you to set various motor speeds, changing the resistor network would allow for different speed adjustments.
Just an Idea - this would cost no more than a couple of dollars!!
Janner10
Sam
Doesn't really matter what they want, it's not their project.
Just restrict your 0v to 10v output from the PLC to a max of 5v. If your budget is zero, you haven't got many options.
Hello guys, by examining one STEP 7 program that is used for controlling VFD micromaster drive I came accross one part which is particulary...
5,311
Hi All, I am facing one issue with the SEW MDX61B drive. Issue- I want to run a conveyor with this drive in two directions but it runs in...
315
Well mis-communication has lead me to a point where my micro is no longer the proper controller for the application its currently being utilized...
1,420
Hi all, I've been handed over a project for a simple conveyor control system, what I've been given is a Micro 820 PLC and 3 AB 525 Drives, I've...
2,453
Hello Experts I have a simovert VC drive which has a CBP2 card , I have installed the gsd of the CBP2 card and configured it with PPO3 . now i...
27
5,552