Can't receive any data through modbus client

Hi everyone,

I am trying to read a Modbus register in an Intelipro Unit with a S7-1200 over Modbus TCP using MB_Client. But i'm not able to receive any data through modbus client function. I am getting 16#7006 status on my modbus block stating that info is being received but the done bit is never getting activated.

I have been on with both Siemens and Comap and both companies claim I have everything set up correctly either end.

I have attached screenshots of my setup. if anyone can spot something. Any help would be greatly appreciated.
Attached Files
File Type: docx Modbus comms with Intelipro.docx (358.9 KB, 11 views)
File Type: docx Modbus DB setup.docx (218.1 KB, 6 views)
File Type: docx Modbus recieved Data.docx (230.6 KB, 4 views)
  Reply With Quote
Old January 17th, 2018, 08:11 AM   #2
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,202
Remote port should be 502 and Local Port can be left as zero, unless you are doing something tricky with port mapping on a router.

If that doesn't fix it you need to be doing some diagnostics on the LAN to see if data is coming out of the PLC. Disconnect the Intelipro and set you laptop to use its IP address, then run Hyperterminal or similar connected to Port 502 so that you see the data coming out of the PLC.
  Reply With Quote
Old January 17th, 2018, 11:35 AM   #3
tragically1969
Member
United Kingdom

tragically1969 is offline
 
Join Date: Jun 2007
Location: uk
Posts: 1,252
Quote:
Originally Posted by AClarke678 View Post
Hi everyone,

I am trying to read a Modbus register in an Intelipro Unit with a S7-1200 over Modbus TCP using MB_Client. But i'm not able to receive any data through modbus client function. I am getting 16#7006 status on my modbus block stating that info is being received but the done bit is never getting activated.

I have been on with both Siemens and Comap and both companies claim I have everything set up correctly either end.

I have attached screenshots of my setup. if anyone can spot something. Any help would be greatly appreciated.
Personally I would prove using ModPoll or similar from a PC that the Intellipro was indeed serving data serving data before i got anywhere near a PLC
  Reply With Quote
Old January 18th, 2018, 04:32 AM   #4
AClarke678
Member
United Kingdom

AClarke678 is offline
 
Join Date: Nov 2017
Location: Belfast
Posts: 2
I have connected the Intelipro with ModScan and can read all values within the holding registers within the Intelipro.

The port is the Intelipro is port 23 which is why i have it set to that and I have also set local port to 0 and still no data.

When I disconnect the Intelipro from the PLC (unplug the cable) the status sits at 16#7002 (Immediate Call) and moves up to 16#7006 (Information being received) when I plug the Intelipro back in, so it is seeing a connection but just doesn't display values of the registers.

I have also connected my PLC with a modbus simulator within my PC and it doesn't display any of the values I have forced through the simulator.
  Reply With Quote
Old January 18th, 2018, 08:27 AM   #5
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,202
Which version of MB_CLIENT are you using. I had problems with V4.0, V4.1 seemed to fix things.


Quote:
I have also connected my PLC with a modbus simulator within my PC and it doesn't display any of the values I have forced through the simulator.
Does make it look like a PLC problem, though I would be happier if you used a terminal program rather than a Modbus simulator to be certain that no data is coming out of the PLC. It just removes a layer of complication. Or if the Modbus simulator has something that just tells you what data is coming in on that port. You did reset the port on the PLC to 502 or set the simulator to use 23?

Looking at your Modbus DB Setup file I can see that you have a StatusCap variable that I am assuming is a captured Status, this is showing 16#8380 and that error is "Received Modbus frame has incorrect format or too few bytes were received."
Attached Images
File Type: jpg Modbus versions.JPG (18.0 KB, 17 views)
  Reply With Quote
Old January 18th, 2018, 10:21 AM   #6
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,202
Also you need to think about a firewall blocking port 23, it is the normal telnet port and is very likely to be blocked on your PC.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Wago eCockpit CoDeSys - Modbus TCP Client Issue Hal9000 LIVE PLC Questions And Answers 4 November 13th, 2017 05:13 PM
client is asking about Red Lion Data Station Plus with Scadapacks defcon.klaxon LIVE PLC Questions And Answers 9 August 9th, 2017 07:15 PM
Opinion: Prosoft Modbus card or Red Lion Data Station Plus? Bullzi LIVE PLC Questions And Answers 5 August 3rd, 2016 07:44 PM
How do I pull Modbus Data over Ethernet: CompactLogix Thinkster LIVE PLC Questions And Answers 9 June 24th, 2014 09:35 PM
Modbus on RS-485: a frame without data Ken Roach LIVE PLC Questions And Answers 18 December 18th, 2009 03:30 PM


All times are GMT -5. The time now is 10:09 PM.


.