Air Enthalpy calcs

Morning, folks. I hope I get some views on this and maybe a reply. I'm reaching out to the best of the best here.
I'm writing logic for some Air Handling Units (AHU's) for a customer that has contracted us to do so. I'm using RS5k v. 20.04
Anyway, to be brief, I need to perform an enthalpy calculation on outside air temp and humidity percent, which are the only 2 values I get into the logic.
If you'll note the 2 links, the equation gives you the result in kJ/kg, which I don't know how to relate to the temp. I am using the one from wiki without steam tables. I have absolutely no problem using the equation in the logic and doing the math, I just don't understand how to use the result. The reason for this routine is that an AHU can use outside air to help with cooling without using the chilled water at certain outside temps. But if the humidity is too high, even though the outside temp is low, say 50, then it would do no good to bring in that air. There will probably be some kind of a comparison I will have to make. I have emailed the engineers that do this and that sent me the links, but no reply so far. Any enlightenment is more than I have now. Thanks in advance, folks. Happy Monday.

https://sciencing.com/calculate-enth...r-6118694.html

https://www.wikihow.com/Calculate-th...y-of-Moist-Air
__________________
Detroit City Limit: An Automation Alley Community
  Reply With Quote
Old January 22nd, 2018, 12:05 PM   #2
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,039
It's been too many years since I hade to deal with thermodynamics.

this maybe a stupid question on my part, if you have a humidity limit (not to exceed this value), why not program that into your logic as the determining factor?

just a question and as I said, to many years ago for this calculation but I still have my books.

james
  Reply With Quote
Old January 22nd, 2018, 12:55 PM   #3
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,836
I guess I'm not sure what the question is. I assume that the AHU is going to be used with tempering air, and the enthalpy calculation is part of that. Here is one explanation of tempering air: https://www.garagejournal.com/forum/...hp/t-3860.html Some searching by you will yield more results. You might also look at the ASHRAE site.

A couple of notes. First, do some checking on the formula's accuracy over the range of operation you are expecting. These look like empirical formulas, and they may or may not be accurate for your conditions. A check calculation with known accurate results provided by your client would be in order.

Second, note that the moisture content portion of the equation is the humidity ratio, kg/kg. This is not equal to relative humidity (%RH) but is a function of %RH and temperature.
  Reply With Quote
Old January 24th, 2018, 12:11 PM   #4
saultgeorge
Supporting Member
United States

saultgeorge is offline
 
Join Date: Jul 2015
Location: Detroit
Posts: 53
Thanks Tom and James. Yes, I have received even more equations from their engineers. They use an on-line type calculator (similar to a mortgage calculator) to do their math. A comment to Tom's reply, that sounds like a good idea, using RH to say yea or nay to using the outside air economizer, but the specs call for enthalpy calculation of the outside air and humidity. I'll keep at it. Really, thanks so much for taking the time to help.
__________________
Detroit City Limit: An Automation Alley Community
  Reply With Quote
Old January 24th, 2018, 01:51 PM   #5
g.mccormick
Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 439
https://www.vaisala.com/sites/defaul...210973EN-F.pdf


This pdf shows how to calculate various air properties with temperature and RH, etc. I have used calculations from this pdf to calculate the dewpoint give drybulb T and RH inside a P2k plc. I believe that chapter 6 is enthalpy. I assume the mechanical guys are saying to use the dampers to select the lowest enthalpy air to use to (freshaire or recirc air).
  Reply With Quote
Old January 25th, 2018, 05:34 PM   #6
shooter
Member
Netherlands

shooter is offline
 
shooter's Avatar
 
Join Date: Sep 2002
Location: duketown
Posts: 2,617
Have a look at the functions on the website of oscat.de they are used to make the calcs in a simple way.
and yes it is enthalpy , however the moist will change the enthalpy as it takes more energy to cool moist air, and if the water condenses it even takes more energy.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
  Reply With Quote
Old January 26th, 2018, 03:48 PM   #7
saultgeorge
Supporting Member
United States

saultgeorge is offline
 
Join Date: Jul 2015
Location: Detroit
Posts: 53
Thank you g.mccormick and shooter. I was given that PDF from Vaisala and those are the equations I'm using to compute the enthalpy in my logic. I then compare outside air enthalpy to return air enthalpy. If outside is more, then no economizer dampers open and no free cooling. Thanks to all for the replies and research and your time.
__________________
Detroit City Limit: An Automation Alley Community
  Reply With Quote
Old January 27th, 2018, 10:55 AM   #8
g.mccormick
Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 439
Quote:
Originally Posted by saultgeorge View Post
Thank you g.mccormick and shooter. I was given that PDF from Vaisala and those are the equations I'm using to compute the enthalpy in my logic. I then compare outside air enthalpy to return air enthalpy. If outside is more, then no economizer dampers open and no free cooling. Thanks to all for the replies and research and your time.

You're welcome.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Furnace gas air ratio control cross limiting pauly LIVE PLC Questions And Answers 12 July 5th, 2017 05:16 AM
Im totally new! Please help! Tool changer PLC mike^3 LIVE PLC Questions And Answers 34 November 3rd, 2015 04:28 PM
Air velocity sensor for air with particles accidentalengineer LIVE PLC Questions And Answers 15 June 22nd, 2012 01:01 PM
Air pressure control loop Pandiani LIVE PLC Questions And Answers 8 September 2nd, 2007 11:41 AM
Boiler Fuel Feed Simulation for Bunker C sjknight LIVE PLC Questions And Answers 1 November 20th, 2005 04:42 PM


All times are GMT -5. The time now is 06:08 AM.


.