plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old January 24th, 2018, 05:53 AM   #1
PrasannaP
India
PrasannaP is offline
PLC-5/40c read throgh serial port in ML1400
Hiii.
i am trying to read the PLC-5/40c data to the ML1400 PLC throgh channel 0(25 pin to 9 pin pin configuration). When i downloaded the program in PLC-5/40C, error code of 89 occurs (Processor's messagebbuffer is full). Can anyone help me to resolve this error.
Old January 24th, 2018, 07:26 AM   #2
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
Post a screenshot of your msg logic and msg setup screen.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
Old January 24th, 2018, 10:19 AM   #3
Ken Roach
United States
Ken Roach is offline
Ken Roach's Avatar
Welcome to the PLCTalk forum community !
In general, I'd recommend a "SLC Typed Write" command, though the MicroLogix 1400 will accept a PLC-5 message command.
If your controller has a program that has used up all of the available communications buffers, it's possible that this MSG instruction doesn't have one available.
I also recommend a screenshot of the MSG instruction configuration. Be sure that you are triggering it based on an event or a repeating timer, rather than simply re-triggering it every time it completes or errors.
Old January 25th, 2018, 12:15 AM   #4
PrasannaP
India
please find the attached message setup in PLC-5/40
Old January 25th, 2018, 12:18 AM   #5
PrasannaP
India
i configued msg setup in PLC-5/40C as PLC-5 Typed write and in ML1400 configured msg setup as PLC-5 read for Channel0.
Old January 25th, 2018, 01:33 AM   #6
Ken Roach
United States
Ken Roach's Avatar
Thank you for the follow-up screenshots. I don't have a full computer to comment at length right now but want to post my thoughts.
First:. MSG instructions do not need to be used in pairs, which is what I think you are describing. A Write message in one controller does not require a corresponding Read message in the other controller. The operating system in the target controller handles the data automatically.
The screenshots you posted perform the kind of MSG trigger logic that I recommend against. In that program the MSG will re-trigger every time it completes or errors, which uses up more buffers and bandwidth than the 2-second timer preceding it suggests was intended.
Old January 25th, 2018, 02:08 AM   #7
PrasannaP
India
ok. i will setup msg instruction in ML1400 as PLC-5 Read for reading data from PLC-5 serial communication.
i have attached the screenshot of the channel0 configuration in PLC-5/40 and Channel2 configuartion in ML1400 for read PLC5 data in ML1400 serially. Whather the configuration i did is correct?
Old January 25th, 2018, 02:58 AM   #8
Mickey
United States
Mickey is offline
Mickey's Avatar
I would change the Communication Mode on the PLC 5 to "System (Point to Point)".
And the Driver on the Micrologix side to "DF1 Full Duplex".
It might help to speed up the baud rate also, but thats up to you.
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old January 25th, 2018, 04:31 AM   #9
PrasannaP
India
As per said i change the full duplex in ML1400 and system point to point, but now also iam not getting data
File Type: docx full duplex and system point to point.docx (348.1 KB, 6 views)
Old January 25th, 2018, 07:46 AM   #10
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
How is the cable wired? the way you have it configured, you should need a simple 3-wire cable. Rx from one PLC goes to Tx on the other and vice versa. Gnd to Gnd on both.
__________________
Old January 25th, 2018, 07:55 AM   #11
PrasannaP
India
Quote:
Yes sir.
I did the wiring as you said. Tx to Rx , Rx to Tx and Gnd to Gnd. And I configured msg setup in ML1400 as PLC-5 read in channel2
Old January 25th, 2018, 11:14 AM   #12
Ken Roach
United States
Ken Roach's Avatar
It is correct to have set up the controllers for DF1 Full Duplex point-to-point communications instead of DF1 Half Duplex Master/Slave.
It is also correct to set the data rate (19200) and the Error Checking (CRC) the same on both controllers.
Remember that the 25-pin and 9-pin RS-232 ports do not use the same pins for the same functions.
DB25 to DB9
Tx 2 to Rx 2
Rx 3 to Tx 3
Com 7 to Com 5
Disable or remove the MSG logic in the PLC-5/40C so that it does not overwhelm the PLC-5/40C message buffers or the MicroLogix buffers.
Now that you have everything configured correctly, show the configuration of the MSG instruction in the MicroLogix 1400 and the value of any Error codes you are getting from that MSG instruction.
Old January 27th, 2018, 02:06 AM   #13
PrasannaP
India
DB25 to DB9
Tx 2 to Rx 2
Rx 3 to Tx 3
Com 7 to Com 5
Thank you.I have set the configuration as below attached file. And i deleted the msg setup in PLC-5 write in PLC-5/40C, oonly i setup an msg instruction in ML1400 only as PLC-5 Read.
Please tell me if there is any changes i have to make.
Old January 27th, 2018, 02:39 PM   #14
Ken Roach
United States
Ken Roach's Avatar
Thank you for those screenshots !
It looks like your configuration and addressing are all correct, but the ladder logic that manages the MSG instructions is causing your problems.
Your MicroLogix 1400 screenshot shows that the .EW bit is set for that MSG instruction control block. The "Enabled and Waiting" status bit indicates that this particular MSG instruction is waiting for an available communications buffer in the controller operating system.
I know the SLC-5/03,4,5 controllers had just 4 simultaneous message buffers. I'm not sure how many the MicroLogix 1400 has.
I can't see the ladder logic you are using, but the fact that you are using an OTU (unlatch output) instruction addressed to the Enable bit suggests that you are re-triggering the MSG continuously.
While this method is often shown in sample logic (including in some Rockwell reference manuals) it is not appropriate for systems that need to communicate with large numbers of remote devices. Your program list shows several routine names that suggest that your MicroLogix is communicating with an ABB device and the PLC-5/40 and maybe with other devices.
Examine the MicroLogix 1400 program and see how many MSG instructions you have, and change them to logic that does not automatically re-trigger them by unlatching the Enable bit. In my opinion, the only MSG instruction status bit that should ever be manipulated in logic is the .TO bit, which causes the message to go through an orderly shutdown as though it has timed out at the operating system level.
Old January 28th, 2018, 01:51 AM   #15
Ken Roach
United States
Ken Roach's Avatar
The attached screenshot is an example of how I prefer to use a repeating Timer to trigger MSG instructions.
The .EN bit is used to prevent re-triggering of the MSG instruction while it is still in process, which would put another MSG into the operating system message buffer.
I do not recommend using the self-retriggering method, or ever manipulating the .EN bit with an Output (OTU or OTL or OTE) instruction.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
CP 5711 9-pin serial port to PLC MPI 9-pin port communication cable. hinddhindsa LIVE PLC Questions And Answers 7 October 22nd, 2016 08:55 AM
Panel View Standard pload/Download Help JoseM LIVE PLC Questions And Answers 18 December 11th, 2015 08:08 AM
HMI and Laptop to PLC via Serial Port elitheei LIVE PLC Questions And Answers 5 March 28th, 2008 11:31 PM
MPI comunication Manuel Raposo LIVE PLC Questions And Answers 22 July 16th, 2007 07:24 AM
Need PLC to control via serial port ... LIVE PLC Questions And Answers 9 February 28th, 2003 08:01 AM