VFD disconnect aux contacts

Is there an electrical code requirement that calls out the a need for an auxiliary contact in a field mounted disconnect?
I have a customer that doesn't want to put auxiliary contact in the field disconnect. I though there was a call out for it but I can't find it.
__________________
There should be a minimum IQ before people can breed.

FS Eng (TÜV Rheinland, #11004/15, Machinery)
  Reply With Quote
Old January 29th, 2018, 11:07 AM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,925
Just tell him you will be glad to sell him a new drive after he blows up the one he has by skipping the aux. contact.

I am pretty sure you can find a VFD manual that states this as a requirement for any downstream disconnecting device.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old January 29th, 2018, 11:09 AM   #3
kekrahulik
Member
United States

kekrahulik is offline
 
Join Date: Apr 2009
Location: Lancaster,pa
Posts: 279
I don't know if there is something specific about that, but without it you will never know to stop the drive (or starter for non-vfd applications) or not start the drive. That opens the distinct possibility that some one will throw the disconnect on and have the motor suddenly start.

From a code point of view, you may want to look into unexpected motion or the fact that this scenario would equate to the disconnect acting as a starter.
  Reply With Quote
Old January 29th, 2018, 12:54 PM   #4
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,576
It's not a "code" issue, it's a drive protection issue. Opening the contacts of a disconnect switch while the drive is RUNNING can cause severe damage and failure of the output transistors of the VFD. So it's possible that just ONE mistake can cost them the entire cost of a replacement VFD + down time revenue loss. The cost of adding and wiring the aux contacts is insignificant in comparison. You can buy VFD cable that already has the two extra wires needed for that included in the bundle and already separately shielded for this exact purpose.

What the aux contact does is that you tie it back to the VFD control / command system to IMMEDIATELY turn off the output transistors. Because aux contacts on disconnect switches are (almost*) ALWAYS designed to open just BEFORE the main contacts, by the time the main contacts open, the transistors are already off-line and no damage occurs. Anyone who tells them / you that this is not an issue is clueless.

* MOST of the time that is going to be true, but it's actually incumbent on the specifier to ENSURE that the aux contacts open ahead of the main contacts.
  Reply With Quote
Old January 29th, 2018, 01:23 PM   #5
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 660
Make you case in writing why you suggest to have aux contact. Then move on.

He who pays the piper, calls the tune.

We have had plenty of call backs to the retro fit things we initially advised on some months / weeks later.
  Reply With Quote
Old January 29th, 2018, 02:31 PM   #6
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,576
Quote:
Originally Posted by janner_10 View Post
Make you case in writing why you suggest to have aux contact. Then move on.

He who pays the piper, calls the tune.

We have had plenty of call backs to the retro fit things we initially advised on some months / weeks later.
Amen to that. "Told-you-so" billing is always sweet, but I never actually rub it in to the customer unless they complain first.

I recently got called out to a large facility what I did 4 years ago; smart MCCs, Ethernet to everything etc. etc. Everything works great, but I gave them a $25k recommended spares list when we were done and they ignored it completely. Fast forward 4 years and a 500HP VFD blew up (because they changed to a 600HP motor and "assumed" it was OK). No spare parts on hand, so they were down for 5 days as everyone scrambled to find a way to get them on line again. $200,000 per day in lost production; that "savings" of $25k by not buying spares turned into $1 million in losses and emergency repair costs of another $100K... NOW they are buying the spare parts...
  Reply With Quote
Old January 29th, 2018, 05:01 PM   #7
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 416
I agree that it's bad practice not to use the aux contacts on the disconnects to stop the drive, but I've personally seen operators open and close disconnects on running drives enough times to know that it's not necessarily a sudden death situation. These were all <25HP drives, however...

Understand that I'm not advocating for doing that!

Actually, I've even seen major companies standardize on VFD control panel designs that perform an emergency stop that only stops the drive by first opening up a contactor on the load side of the drive. An aux contact on the load contactor then breaks the "Run Enable" signal to the drive. So every e-stop results in exactly the same damage as opening a disconnect on a running drive. Crazy!

Last edited by rupej; January 29th, 2018 at 05:08 PM.
  Reply With Quote
Old January 29th, 2018, 06:13 PM   #8
Gomez_
Lifetime Supporting Member
United States

Gomez_ is offline
 
Join Date: Sep 2014
Location: California
Posts: 177
Quote:
Originally Posted by rupej View Post
Actually, I've even seen major companies standardize on VFD control panel designs that perform an emergency stop that only stops the drive by first opening up a contactor on the load side of the drive. An aux contact on the load contactor then breaks the "Run Enable" signal to the drive. So every e-stop results in exactly the same damage as opening a disconnect on a running drive. Crazy!
Wow I hope that wasn't recent, with STO being pretty standard these days.
  Reply With Quote
Old January 29th, 2018, 07:19 PM   #9
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,576
Luck is not a valid strategy for reliable operations...
  Reply With Quote
Old January 29th, 2018, 09:42 PM   #10
seth350
Member
United States

seth350 is offline
 
seth350's Avatar
 
Join Date: Jul 2011
Location: Over yonder
Posts: 253
“What the aux contact does is that you tie it back to the VFD control / command system to IMMEDIATELY turn off the output transistors. Because aux contacts on disconnect switches are (almost*) ALWAYS designed to open just BEFORE the main contacts, by the time the main contacts open, the transistors are already off-line and no damage occurs. Anyone who tells them / you that this is not an issue is clueless.”

That’s good to know. I figured the aux and main opened/closed at same time. Thank you for sharing.
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry

Last edited by seth350; January 29th, 2018 at 09:46 PM.
  Reply With Quote
Old January 29th, 2018, 10:54 PM   #11
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,925
Quote:
Originally Posted by rupej View Post
...
Actually, I've even seen major companies standardize on VFD control panel designs that perform an emergency stop that only stops the drive by first opening up a contactor on the load side of the drive. An aux contact on the load contactor then breaks the "Run Enable" signal to the drive. So every e-stop results in exactly the same damage as opening a disconnect on a running drive. Crazy!
If you use an early break contact to disable the VFD, this strategy can work. It is much easier on the VFD than killing the input power via e-stop.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old January 29th, 2018, 11:11 PM   #12
sparkie
Lifetime Supporting Member
United States

sparkie is offline
 
Join Date: Nov 2014
Location: KS
Posts: 805
Not code, and others have mentioned why to use the aux disconnects, however at my hold job we can a 60A CH disconnected, mounted on a board, mounted on the wall with big black letters that said "This is not a light switch!" I regularly saw production people stand in front of and throw a 200A disconnect on a meat grinder while the grinder was heavily loaded for the days production like it was no big deal, not to mention the countless other smaller disconnects around there, so it is a pretty basic assumption that it will happen.
  Reply With Quote
Old January 30th, 2018, 02:54 AM   #13
Rob...
Supporting Member
United Kingdom

Rob... is offline
 
Join Date: Jul 2016
Location: Manchester
Posts: 142
Had a similar scenario with a 400hp motor connected to a fan for LEV.

Refused the additional minor cost for aux contacts on the local disconnect.

Operator starts the fan one morning, it doesn't move but the VFD is giving an output. The PID at this point is ramping the speed up slowly.

Operator realises the motors switched off at the local disconnect. An turns it on. A big flash and bang as the disconnect blows itself to pieces, an operator with brown underwear later and I get a call to price an emergency repair.

Thankfully nobody was hurt. An the VFD took it like a champ.

I was nicely covered too explaining the consequences of what potentially could happen in a previous email chain with the client. 400hp motors take some serious grunt starting them DOL!!
  Reply With Quote
Old January 31st, 2018, 08:50 PM   #14
DickDV
Member
United States

DickDV is offline
 
Join Date: May 2002
Location: Kalamazoo MI
Posts: 2,316
On the most recent designs of VFD's, ABB no longer requires or recommends pre-action switches on disconnects in VFD output circuits.

Not sure I'm comfortable with that especially over 100hp, but that is the official line.
  Reply With Quote
Old February 1st, 2018, 09:09 AM   #15
Cow
Member
United States

Cow is offline
 
Join Date: Jun 2009
Location: Eastern Oregon
Posts: 88
Quote:
Originally Posted by DickDV View Post
On the most recent designs of VFD's, ABB no longer requires or recommends pre-action switches on disconnects in VFD output circuits.

Not sure I'm comfortable with that especially over 100hp, but that is the official line.
One has to remember ABB is also in the business of selling drives.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Wiring s contactor without aux. contacts kapooski2012 LIVE PLC Questions And Answers 3 November 5th, 2012 04:40 PM
Field disconnect and VFD JeffKiper LIVE PLC Questions And Answers 11 August 16th, 2012 08:37 PM
Exposion Proof Disconnect with handle contacts JeffKiper LIVE PLC Questions And Answers 1 August 7th, 2012 05:34 PM
Seimens VFD issue ascot01 LIVE PLC Questions And Answers 5 February 14th, 2009 11:19 PM
OT: are 52a and 52b (Aux contacts) an ANSI standard? Sliver LIVE PLC Questions And Answers 7 November 3rd, 2005 02:57 PM