plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old February 6th, 2018, 01:31 PM   #1
NiloRamirez
Brazil
NiloRamirez is offline
Read_var Modbus TCP/IP - Schneider M340
I'm using a PLC M340 (Master) to communicate with a M221 (Slave) PLC. To do this communication, I'm using "Read_var" and "Write_var" blocks.
The communication is working, but when I lose it, I can not communicate again. I have to reset my M340 (Master) to reestablish the communication.
I've seen in my "GEST" vector that when I lose communication, the "ModbusRead_Dig01_CP04[1].0" is aways 1. Picture "Stop".
I need an automactic reconnection.
Can anybody help me?
Thanks, Nilo Ramirez.
Old February 6th, 2018, 04:20 PM   #2
gclshortt
Canada
gclshortt is offline
gclshortt's Avatar
http://www.plctalk.net/qanda/showthread.php?t=52962
The above thread may help you out.
Regards,
__________________
Garry
https://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
Old February 6th, 2018, 05:02 PM   #3
NiloRamirez
Brazil
I've tried to reset the activation bit, it resets but my communication don't return.
My configuration is in the picture.
Just some brief observations:
- The first compare is used because I have 15 Read_var, so, I have a counter that counts from 0 to 14. In this case, when my counter is in 10 and the other contact is enabled, my communication starts.
- The second compare is to reset my "activity bit" because it freezes on "1" station when the communication stops.
Old February 7th, 2018, 06:19 AM   #4
NiloRamirez
Brazil
Up
Old February 7th, 2018, 12:54 PM   #5
Saffa
New Zealand
Saffa is offline
Do you have a timeout set? 3rd word of the management parameters. The default is zero which means wait infinitely on comms fail. See the help file.
When i detect a comms fail I write zeroes to the management parameters except for timeout and retrigger the read_var block
Old February 7th, 2018, 03:31 PM   #6
NiloRamirez
Brazil
Hi
My Read_var was without a timeout.
So, I put 1000ms in the third position of my GEST, remove the gateway (the 2 after my IP), and reset the "Activity bit" as demonstrated.
It finally works.
Thank you all for help me.
Nilo Ramirez.
Old February 7th, 2018, 06:31 PM   #7
Lare
Finland
Lare is offline
Activity bit can still jam to "1" state, making force reset for activity bit helps. (reset bit if at "1" state too long.
Zeroing whole gest parameter group and setting timeout to back also works.
(Jamming depends maybe of firmaware version)
On TCP comms you can have several comms active same time, it is sayed somewhere at manual. (you have as many gest parameter groups than you have TCP coms active at same time)
On serial side you can have only one query active same time/for one port. (And using only 1 gest parameter is only needed for serial)
Send new query only when activity bit is at "0" state.
I don't see if you use negated ModbusRead_2_CP04(1).0 bit before read_var block.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Ethrnet IP, Ethernet TCP/ip, Modbus TCP/ip Steve_D LIVE PLC Questions And Answers 4 June 23rd, 2016 08:36 PM
Modbus TCP/IP Between S7-417-4H CPU & Schneider PLC sachin.patil LIVE PLC Questions And Answers 2 June 18th, 2015 04:56 AM
Reversing VSD ATV71 using Schneider M340 via modbus TCP/IP adrien LIVE PLC Questions And Answers 5 May 1st, 2014 10:28 PM
Programming M340 with Modbus TCP/IP Forrest LIVE PLC Questions And Answers 6 August 25th, 2011 02:57 PM