For a revamp we will have a configuration with S7 1500 and FM350 in ET200M on profinet. Will the FM350 work? Because I see in Siemens Tia configurator that it will not work, although I already heard apposing comments.
Has somebody experience with this?
 
Hello!
A FM 350-1 can be used as a IO device with S7-1500 as IO controller. But FM 350-2 couldn't. TIA Portal V14 SP1 gives an error during compiling hardware configuration.

Best regards, Oleksandr.
 
I have FM350-1 (one channel) and TIA V14 SP1 gives warning (yellow triangle), not an error. So I am not sure.
 