running an AC coil on DC

Would like your input........

I am not sure I know all how a shunt trip breaker works, but the ones I am used to you use a control voltage signal to trip the breaker.

I have a customer ( and I don't have all the details) that has a tripping coil rated for 125VAC. Now he needs it to run on 125VDC for whatever reason. Is it possible to run a coil like that on either AC or DC? What will happen?
  Reply With Quote
Old February 7th, 2018, 07:51 AM   #2
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 271
Coil impedance increases with frequency, higher the frequency lower the current and with DC the impedance is minimal.

If you run with 125 VDC probably it will burn in a matter of seconds , don't try it.

The coil should be changed for other rated for 125 VDC

Last edited by lfe; February 7th, 2018 at 07:59 AM.
  Reply With Quote
Old February 7th, 2018, 08:51 AM   #3
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is online now
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: Copenhagen.
Posts: 13,393
There are coils that are rated for both AC and DC, but unless actually labelled for DC or AC/DC - replace the coil.
__________________
Jesper
3 strikes and you're out
  Reply With Quote
Old February 7th, 2018, 03:09 PM   #4
T Gibbs
Member
United States

T Gibbs is offline
 
Join Date: Jun 2012
Location: Morristown, TN
Posts: 382
You could always set a relay with a DC coil and run AC through the contacts to the shunt trip coil.
  Reply With Quote
Old February 8th, 2018, 10:34 AM   #5
lesmar96
Lifetime Supporting Member
United States

lesmar96 is offline
 
Join Date: May 2017
Location: PA
Posts: 228
My customer came up with the idea to run a bridge rectifier in reverse to run this coil. I don't think there is any way this will work. A recitifer cuts the sine wave, right? to take the hz out of it? Running it in reverse, there is no way that it will be able to build a sine wave? He is sure that he has done this before, and it worked, but I don't see how.

Any thoughts?
  Reply With Quote
Old February 8th, 2018, 10:39 AM   #6
dogleg43
Member
United States

dogleg43 is offline
 
Join Date: Dec 2005
Location: Indiana
Posts: 300
Quote:
Originally Posted by lfe View Post
Coil impedance increases with frequency, higher the frequency lower the current and with DC the impedance is minimal.

If you run with 125 VDC probably it will burn in a matter of seconds , don't try it.

The coil should be changed for other rated for 125 VDC
Agree with the above response.
I saw a customer hook up several 24VAC rated relay coils to 24VDC and they all got hot very quickly.
  Reply With Quote
Old February 8th, 2018, 11:26 AM   #7
Dirt
Member
Sweden

Dirt is offline
 
Join Date: Apr 2008
Location: Stockholm
Posts: 211
Quote:
Originally Posted by lesmar96 View Post
My customer came up with the idea to run a bridge rectifier in reverse to run this coil. I don't think there is any way this will work. A recitifer cuts the sine wave, right? to take the hz out of it? Running it in reverse, there is no way that it will be able to build a sine wave? He is sure that he has done this before, and it worked, but I don't see how.

Any thoughts?
Is he joking?

Yeah it's diodes cutting the sine wave, in reverse the dc would see either a "brick wall" or a short circuit.

An inverter would do the trick, but that sounds more expensive/complicated than just getting the correct relay?

Last edited by Dirt; February 8th, 2018 at 11:29 AM.
  Reply With Quote
Old February 8th, 2018, 11:56 AM   #8
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,130
Talking

Quote:
Originally Posted by Dirt View Post
Is he joking?

Yeah it's diodes cutting the sine wave, in reverse the dc would see either a "brick wall" or a short circuit.

An inverter would do the trick, but that sounds more expensive/complicated than just getting the correct relay?

This thread should clear the above up. A long read but funny. I miss those old threads.

http://www.plctalk.net/qanda/showthr...light=thing+dc
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old February 8th, 2018, 01:00 PM   #9
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 910
Quote:
Originally Posted by Mickey View Post
This thread should clear the above up. A long read but funny. I miss those old threads.

http://www.plctalk.net/qanda/showthr...light=thing+dc
What I took away from that thread was:

You see, this forum is kinda like talking to my wife. You ask her one question, and you get a whole boat load of something else.


*
  Reply With Quote
Old February 8th, 2018, 07:52 PM   #10
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 416
Quote:
Originally Posted by Mickey View Post
This thread should clear the above up. A long read but funny. I miss those old threads.

http://www.plctalk.net/qanda/showthr...light=thing+dc
Lol, thanks for wasting 20 minutes of my life. It was haliarious. Unfortunately, I think I actually agree with the a$$hat
  Reply With Quote
Old February 9th, 2018, 04:57 PM   #11
NetNathan
Lifetime Supporting Member
United States

NetNathan is offline
 
Join Date: Nov 2011
Location: Corona, CA
Posts: 1,468
The are 2 types of trip units.... "Shunt Trip" and "Undervoltage Trip".
A "Shunt Trip" device trips on voltage applied.
An "Undervoltage Trip" device trips on loss of voltage.

These can be ordered at different voltage levels.
__________________
****Control Freak****
Net is where I be and Nathan is me.
  Reply With Quote
Old February 17th, 2018, 09:25 PM   #12
DickDV
Member
United States

DickDV is offline
 
Join Date: May 2002
Location: Kalamazoo MI
Posts: 2,316
I don't mean to suggest this as any kind of practical solution but I believe you will find that an AC rated coil in a relay will operate successfully at a much lower DC voltage. You can play around with one in the lab and I believe that if you start very low with the DC and come up slowly, you will reach a voltage where the coil will attract the armature and not overheat.

This is not to recommend doing this. It might do if your life was at risk and you were stranded on a remote island with nothing but variable DC power but few other places.

If you disassemble an AC relay coil, you will find that it is simply a coil of wire (just like the DC version) but with a bronze shading ring around the nose of the magnetic core.

Without the shading ring, you would have a 60hz buzzer much like a motor starter with an AC coil and a broken shading ring. You have to replace the coil to get the starter to stop chattering but really, all you need to replace is the broken shading ring (comes with the new coil).

Of course, the AC coil is wound with different inductance and wire turns if the voltage was to be the same AC for DC in addition to the shading ring.
  Reply With Quote
Old February 18th, 2018, 02:36 AM   #13
BobB
Lifetime Supporting Member
Australia

BobB is offline
 
BobB's Avatar
 
Join Date: Jun 2002
Location: Sydney
Posts: 4,271
Not reliable - been there - done that! Works sometimes and not other times.
__________________
The Old Pfhaart

  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Getting a DC input from an AC circuit sumPLC LIVE PLC Questions And Answers 4 October 18th, 2017 12:52 PM
Wiring of an AC motor to a DC PLC with relay outputs arunprackash LIVE PLC Questions And Answers 16 August 19th, 2013 08:36 AM
Using coils with different voltages AC vs DC mikas_m LIVE PLC Questions And Answers 11 January 22nd, 2013 08:00 AM
DC into AC PLC inputs SteinCollector LIVE PLC Questions And Answers 7 May 6th, 2011 06:26 PM
50HP DC motor to AC !!! Pierre LIVE PLC Questions And Answers 26 October 18th, 2004 03:47 PM


All times are GMT -5. The time now is 10:13 AM.


.