plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old February 9th, 2018, 02:18 PM   #1
Willlly
United States
Willlly is offline
Willlly's Avatar
4-20mA Output scaling
Hey guys, I have been having a bit of trouble with analog output scaling.
Iím programming out of a compactlogix, Iím trying to output 4-20mA to a valve only using a set point, would an SCP or PID be better for this test station?
It has been while since I actually programmed, trying to get back into it. Any info will help, thanks
Old February 9th, 2018, 02:30 PM   #2
rupej
United States
rupej is offline
You are just wanting to send a constant signal to the valve to hold it in a set position, or do you want to control the valve based on an input, such as flow rate?
If you just want to set the valve, you can use an SCP function (would be an add-on-instruction for RSLogix 5000) to scale the output from 0-100 to 4000-20000, or whatever units your output card is set up for. PID would be for controlling the output based on an input.
If you just want to get some signal to the valve, you don't need an SCP at all. Just write a value in the the Local:1.O.Data (Or whatever yours may be) register.
Old February 9th, 2018, 02:51 PM   #3
Willlly
United States
Willlly is offline
Willlly's Avatar
Yes, I wasn't sure if I needed a SCP. All I am trying to do is create a tag to simply put a set point to control the 4-20 from my PanelView. Lets say I put in a setpoint of 50 only to open half way. would that work? If my scaling is correct?
Old February 9th, 2018, 03:08 PM   #4
janner_10
Supporting Member
United Kingdom
janner_10 is offline
Yes as above. Just scale 0% to 100% to 4mA to 20mA.
Old February 9th, 2018, 03:22 PM   #5
Willlly
United States
Willlly is offline
Willlly's Avatar
Ok thanks, I will try that and see what else I can come up with.
Old February 9th, 2018, 04:53 PM   #6
Willlly
United States
Willlly is offline
Willlly's Avatar
ok I have my SCP scaled but my valve is only staying open half way, could this be a module config or something? I have not dealt with analog output cards a lot.
Old February 9th, 2018, 06:35 PM   #7
rupej
United States
rupej is offline
Yes it could. What's the part number for your output card, and how is it configured? Post a screenshot of the setup screen and your SCP
Old February 10th, 2018, 08:31 AM   #8
Willlly
United States
Willlly is offline
Willlly's Avatar
Input min=0
Input max=100
Scaled min=4000
Scaled max=20000
I have my module configured to raw/proportional data with low limit at -29822 and high and +29085. I have also tried engineering units with a high low of 4000 and 20000. but still get the same outcome. 1769-OF8C is my analog output card
Old February 10th, 2018, 11:12 AM   #9
Willlly
United States
Willlly is offline
Willlly's Avatar
Here is my SCP and Configuration.
Old February 10th, 2018, 12:28 PM   #10
Aardwizz
United Kingdom
Aardwizz is offline
Aardwizz's Avatar
According to the Help file, the scaling for 4-20 mA "Raw/Proportional" is -29,822 to 29,085.
Because your SCP block never sets a value lower than 4000, you're always sending out at least 12.something mA, keeping your valve at at least 50%, and never more than roughly 80% open.
Either change the scaled min / max on your SCP block to -29,822 & 29,085, or change your Configuration to "Engineering Units" and see what happens.
Old February 10th, 2018, 05:08 PM   #11
Willlly
United States
Willlly is offline
Willlly's Avatar
I know I am missing something simple that I have not checked or done. I tried both ways with the same outcome. Ill keep digging into it, but what else could it be?
Old February 10th, 2018, 05:13 PM   #12
dogleg43
United States
dogleg43 is offline
Quote:
Could it be the valve or wiring?
Try using a4-20mA signal generator and see if the valve responds correctly.
Old February 11th, 2018, 12:00 AM   #13
Aardwizz
United Kingdom
Aardwizz is offline
Aardwizz's Avatar
In the controller tags, open up the Input file for the module / channel. There is diagnostic information there that may tell you what's going on.
Old February 12th, 2018, 10:19 AM   #14
Willlly
United States
Willlly is offline
Willlly's Avatar
ok thanks guys I think I have figured it out, the valve may be the issue. Thanks for the help!
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Step 7 output value scaling Sake_no_oni LIVE PLC Questions And Answers 1 February 12th, 2014 09:11 AM
Omron E5CN temp controller control output type unsaint32 LIVE PLC Questions And Answers 4 January 5th, 2014 12:01 AM
Siemens Step5 150u Analogue Output Scaling b16mcc LIVE PLC Questions And Answers 20 October 24th, 2011 10:06 AM
ControlLogix PID Scaling - Help! kdcui LIVE PLC Questions And Answers 4 May 10th, 2011 07:09 PM
Encoder output types Orn Jonsson LIVE PLC Questions And Answers 10 May 9th, 2007 05:25 PM