temp input to vfd
lesmar96
May 2017
PA
520
What is the best way to interface a thermocouple with a vfd. I would like to run a vfd on pid loop based off of temperature. I have used some temperature transmitters, but have had some trouble with accuracy on the ones I had. If this is the best method, what transmitter would you recommend?
What temperature range?
if it is lower than 400ºC better to use a PT100 sensor with the corresponding converter
For room temperature much better to use a PT100 it measures the real temperature, instead thermocouples measure difference between cold junction & hot junction, if the cold junction compensation is not good or not well installed or the cable to sensor is not the correct extension cable that can produce error.
PT100 is much precise and probably cheaper
When you had issues in the past, were you using an isolating signal converter that had offset and gain adjustments, or did you just attempt to convert the signal yourself?
Hello, I'm working with a 1747-NI4 analog input module (for the first time) on a SLC503 processor. I noticed in the IO configuration within...
4,762
I am in the packaging industry and we are looking to build a new machine. We are in the process of designing our product and are wondering...
3,549
I am developing for an S7-1200 in Total Integrated Automation v11 and I see these different local variable types in a function block. It looks...
32
27,429
Gentlemen, I am using an Omega 5550 temp ir with 4-20 input to plc. Trying to display the temp value has been discouraging. The displayed value is...
4,866
I am trying to calibrate an Siemens 13 bit analogue card to read a temperature can anybody help me on how to set the current input to be linear...
1,914