plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old February 21st, 2018, 10:29 AM   #1
sultanahmed
Pakistan
sultanahmed is offline
Post fault code=001h Reason???
Dear All,
I am working on machine in which Allen bradley SLC 5/03 CPU (1747-L531E) is installed,i am having error again and again don't know why?? Each time i got error fault code=001h
when i try to go online no program available after that i download program then PLC goes normal,after a week got same error.
i checked battery which is ok
after each download PLC works fine.
What exact error reason is this??CPU?? Battery??power supply??any module??? :
please help
Error is attached
Old February 21st, 2018, 11:02 AM   #2
geniusintraining
United States
geniusintraining is offline
geniusintraining's Avatar
Just a guess but my money is on the power supply
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
Old February 21st, 2018, 12:00 PM   #3
CaspianSage
United States
CaspianSage is offline
CaspianSage's Avatar
You don't say how long this has been occurring...
If the battery is good it should not matter if the PS had a blip as far as keeping the program intact.
Check all your PS connections though, cycle power on purpose and see what happens.
Rarely seen in my experience but perhaps you have a flaky Processor or PS
.... or a module in the chassis pulling the PS down momentarily because of something connected or a programmed activity the module is doing. It may not be as random as you think, See what is taking place with the PLC, connected I/O etc. when this happens.
Can you connect anything to the plc to monitor power to see if it drops momentarily?
__________________
Caspian
1+1 = 3 and I never was good at math.
Old February 21st, 2018, 12:17 PM   #4
geniusintraining
United States
Quote:
Search the website.... 7 out of 10 (or more) issues with SLC's have been because of power supplies and program loss is way up on the list
__________________
Old February 21st, 2018, 04:40 PM   #5
CaspianSage
United States
Well that is interesting and I would not dispute it but I did say
"in my experience but perhaps you have a flaky Processor or PS"
Always good to start with a PS but I would not have guessed that alone considering the battery is good. Never seen a processor loose the program because the PS went dead.
But thanks for the tip!
__________________
Caspian
Old February 21st, 2018, 05:32 PM   #6
James Mcquade
United States
James Mcquade is offline
is there a power surge protector going to the plc?
I have had bad power do something similar.
james
Old February 21st, 2018, 07:29 PM   #7
Sydney
Supporting Member
United States
Sydney is offline
Quote:
ANY OUTPUT
We had a similar issue that was caused by an alarm/buzzer directly wired to an output that was internally shorted pulling down the power supply causing the processor to fault. It was difficult to troubleshoot because the alarm/buzzer was intermittent, once every week or so. After disconnecting the buzzer the faults went away.
You might want to inventory all hardware devices that ARE NOT isolated, any questionable devices directly connected to outputs should be isolated with a relay as a standard.
Old February 21st, 2018, 09:00 PM   #8
alan_505
Australia
alan_505 is offline
If you short the internal 24v power supply it will most likely wipe out the program.
Alan.
Old February 21st, 2018, 09:30 PM   #9
Sydney
Supporting Member
United States
Sydney is offline
Exactly!
Old February 22nd, 2018, 02:27 PM   #10
sharkyh2o
United States
sharkyh2o is offline
I have also had this on a 5/05. Power supply was bad. If the program was downloaded it ran fine till power was cycled.
Old February 23rd, 2018, 06:03 AM   #11
geniusintraining
United States
Exactly!
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
ET200S - ignore loss of IM-151 cjd1965 LIVE PLC Questions And Answers 10 May 28th, 2013 10:27 PM
All the light on s7-400 panel flashing leon.LEE LIVE PLC Questions And Answers 2 January 8th, 2009 10:06 AM
TwinCat and Indramat F268 Brake Fault boldive LIVE PLC Questions And Answers 0 December 4th, 2008 09:55 AM
Rockwell/Devicenet/Powerflex Comms fault - please help ukguy777 LIVE PLC Questions And Answers 14 June 14th, 2005 02:55 PM
1200 series ALLEN BRADLEY PLC WHAT ARE THE REASON IT GO IN THE FAULT MODE?IT IS NOT pcontrol LIVE PLC Questions And Answers 3 December 19th, 2002 12:12 PM