Question sqo instruction
how does an sqo instruction work with no bit to trigger the next step
Old March 1st, 2018, 02:19 PM   #2
RonJohn
United States
RonJohn is offline
RonJohn's Avatar
Welcome to the forum!
The answer to that question may depend on the processor you're using. Tell us make/model/etc. of your PLC for starters.
If you have a screen shot of the code in question, posting that may help us as well.
Old March 1st, 2018, 02:42 PM   #3
chutnik
United States
chutnik is offline
using a allen bradley 1769-l33
Old March 1st, 2018, 02:53 PM   #4
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
Some other logic is driving the control.pos value. What you have there is a glorified MOV with indirect addressing (since the mask is all 1s).
Do a cross reference on TANK_QUEUE_SEQUENCER and/or TANK_QUEUE_SEQUENCER.POS
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
Old March 1st, 2018, 03:19 PM   #5
daba
United Kingdom
daba is offline
daba's Avatar
Or, it could be the .EN is being OTU'd elsewhere.
This will cause the next scan of the SQO to advance to the next step.
EDIT Mickey suggested this, but deleted his post....
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem
Old March 1st, 2018, 07:14 PM   #6
Mickey
United States
Mickey is offline
Mickey's Avatar
Yes. I am not a RSLogix5000 user.So deleted the post.
Reading the instruction help lead me to believe the instruction executes when it is enabled. Not from a false to true transition( like other platforms RSLogix500 and RSLogix5). If that is true then maybe the instruction is in a conditional subroutine.
RSLogix5000 users, please correct me.
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old March 1st, 2018, 11:12 PM   #7
bernie_carlton
United States
bernie_carlton is online now
bernie_carlton's Avatar
I believe that sometimes this instruction can be paired with an SQI instruction which is looking for the appropriate conditions to advance to the next step (or position using the instruction parameter)
__________________
Controlling outputs is the PLC's way of getting its inputs to change.
www.thePLCguy.com
Old March 2nd, 2018, 06:54 AM   #8
daba
United Kingdom
daba is offline
daba's Avatar
Quote:
Irrespective of whether an SQO is paired with an SQI, each of them will require a false-to-true transition to make it advance to the next "index".
This is actually the case for nearly all instructions that have "Control" bits associated with them.
The control bits are used (amongst other things), to remember the last state of the rung, in most cases that is an "Enable" (.EN) bit, to determine if the rung has gone false-to-true.
Counters have 2 "Enable" bits, .CU (Count Up Enable), and .CD (Count Down Enable).
Remember that, in the PLC world, each and every instruction only knows one thing, the current state of the rung, true or false, when it is executed. They have absolutely no knowledge of what precedes them, or follows them, they just receive the "Rung Logic Continuity" as an input parameter (the "Enable_In"), and acts on the state of that accordingly. The "Enable_In" state is passed on to the next instruction as the "Enable_Out", mirroring the input state, so that following instructions can see the Rung Logic Continuity, true or false.
For this reason we can always fool an instruction into thinking the rung has changed state false-to-true, by resetting its "Enable_Out" bit anywhere else in the logic. The next scan of the instruction, assuming Enable_In is true, determines that since "Enable_Out" is false, the rung will appear to have changed state, false to true, even though it actually hasn't.
If a programmer wants a "controlled" instruction to execute every time it is scanned, it is quite common to see an OTU of the instruction's "Enable_Out" either in front of, or behind, the instruction.
Timers are an exception to this false-to-true "rule", timers being "Enabled" do not stop the instruction working each and every scan, for obvious reasons.
__________________
a-b train ltd.
www.abtrain.co.uk
tel: 07506 73 9999
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Using SQO Position PLC Pie Guy LIVE PLC Questions And Answers 7 September 20th, 2016 01:48 PM
MSG Instruction Problem - SLC 5/03 to 1761-NET-ENI to Email johnd_125 LIVE PLC Questions And Answers 0 February 12th, 2016 05:06 PM
osr instruction help Mossman LIVE PLC Questions And Answers 5 September 20th, 2007 02:08 AM
SQL & SQO Instruction peavey_wolfgang_2000 LIVE PLC Questions And Answers 1 September 17th, 2005 11:59 AM
Sqo Instruction JAYALA LIVE PLC Questions And Answers 7 June 26th, 2002 09:02 AM