I have a customer that needs to start logging their waster water system at the demand of the county.
They need to report quarterly the daily gallons discharged into the sewer system (2 totalizers involved here, 1-1/4" & 2" pump discharges) and another 2" pipe of gallons they process daily through their columns before discharged. The county also wants a quarterly average of gallons per day, and a peak daily readings for the period.
Does anyone know of networked totalizers and software to automatically log these figures? All I have found so far is manual meters, and network batch meters that need read and reset manually
The customer also would like the feature of automatic emails, either reminding to get the log and forward it to the county, or emailing the log direct to the county, if that is possible.
__________________
Never underestimate the quality of idiots that will be running your machines
http://aabeck.com
Old March 2nd, 2018, 02:50 PM   #2
CaspianSage
Member
United States
CaspianSage is offline
CaspianSage's Avatar
Doesn't the waste water treatment facilities in Detroit have equipment that can do at least some of what you want? Maybe someone at one of the plants can help get you what you need.
Obviously you can build your own solution with flow switches and other components but you already know that.
__________________
Caspian
1+1 = 3 and I never was good at math.
Old March 2nd, 2018, 03:08 PM   #3
John Morris
Member
United States
John Morris is offline
John Morris's Avatar
About a decade ago I work for a battery manufacturer.
Obviously the place used alot of water, and discharged almost as much in cooling. The city wanted to know the pH of the discharge and how much.
The city came out and installed a pH monitoring device which doubled as a flow meter, with real time reporting over cell.
Needless to say, the companies water bill was alot higher for a couple of months.
__________________
"When nothing is going right, go left."
"Even a fish wouldn't get into trouble if it kept its mouth shut."
(I should probably look into this)
Old March 2nd, 2018, 03:09 PM   #4
harryting
Lifetime Supporting Member
United States
harryting is offline
harryting's Avatar
Something like this? Or you want a networked system?
http://www.gfps.com/country_US/en_US...ents/8150.html
Old March 2nd, 2018, 03:13 PM   #5
Aabeck
Member
United States
Aabeck is offline
Aabeck's Avatar
CaspianSage,
I have been in contact with the county auditor (this comes from Wayne County, not City of Detroit Water Dep't) but so far he only knows what he wants - I have even asked for names of other companies that already get him these logs but haven't received any.
What I have seen so far are totalizers (water meters) that record gallons, one has networking capabilities that shows a report on a web page, but no software that will do the polling and actual logging - or a system for small flows (the 2" pump discharge runs about 90GPM)
__________________
http://aabeck.com
Old March 2nd, 2018, 03:19 PM   #6
Aabeck
Member
United States
Aabeck is offline
Aabeck's Avatar
harryting,
They are looking for a system that is networked and will log the daily totals, with an average and peak value also. Plus, I already talked to the local GF/Signet distributor (Harrington Plastics) and they say they have nothing like what is needed - Signet or other brand.
They want this done fully automatically so it doesn't rely on someone reading the values daily and manually entering them in log.
__________________
http://aabeck.com
Old March 2nd, 2018, 03:37 PM   #7
JordanCClark
United States
JordanCClark is offline
JordanCClark's Avatar
ifm has flow meters that can sit on IO-Link.
http://www.ifm.com/ifmus/web/pmain040_030_010.htm
__________________
_____________________________
Jordan
Any man that can hitch the length and breadth of the Galaxy, rough it, slum it, struggle against terrible odds, win through and still know where his towel is, is clearly a man to be reckoned with.
-- Hitchhiker's Guide to the Galaxy
Old March 2nd, 2018, 03:39 PM   #8
Tom Jenkins
United States
Tom Jenkins is offline
Tom Jenkins's Avatar
Somethin like these should do it - do a bit of searching on the supplier sites:
http://www.dwyer-inst.com/Product/Fl...eters/ModelTM2
http://www.dwyer-inst.com/Product/Fl...e/SeriesTFM-LI
https://www.omega.com/pptst/FTB-630.html
https://www.omega.com/pptst/FP90.html
https://www.omega.com/pptst/FTB790.html
Old March 2nd, 2018, 05:19 PM   #9
OkiePC
United States
OkiePC is offline
OkiePC's Avatar
I have three of these in a water plant:
http://www.onicon.com/F3000.html
With a Modbus interface to a Micrologix that reads the flow rates and totalizers right out of the meters. There is a Red Lion HMI that allows the operator to view those data points. Once we add a remote access VPN it wouldn't take but a little more keyboard magic to create automatic emails.
We have investigated the Scadametrics EtherMeter for an existing sensus meter and it looks very promising but the project for it never panned out so I have not used their stuff yet:
http://www.scadametrics.com/products/products.htm
It should talk to meters that use the Sensus protocol and a handful of others and act as a protocol converter to a more PLC friendly language.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
Old March 2nd, 2018, 05:43 PM   #10
Aabeck
Member
United States
Aabeck is offline
Aabeck's Avatar
THE IFM looks promising - that didn't show when I searched Google.
The Omega line won't work - I already went through their site and did an online chat with their tech supp - he finally admitted they didn't have anything that would do what the county wants.
Something like the Dwyer, which like many others has an analog output, would need a PLC to calculate the values, then have the computer get the values - both myself and the customers IT guru would like a system of 3 meters networked to the PC, then the PC emailing &/or storing the log over the Ethernet.
__________________
http://aabeck.com
Old March 2nd, 2018, 07:50 PM   #11
seth350
Member
United States
seth350 is offline
seth350's Avatar
Look up Hach. They have all kinds of options and waste water is their forte’.
We use one for discharge flow and it has an RS232 interface for pulling the data right from the controller. I think they also have software that will do the same if you want a canned solution.
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry
Old March 2nd, 2018, 09:04 PM   #12
danw
Member
United States
danw is offline
danw's Avatar
Quote:
I think a stand-alone Honeywell paperless recorder could do this. It might be a collection of .rtf report files generated/issued daily for the daily max and average flow rates (prints out as a single page report) and then a separate report for the monthly total value.
If a non-PLC approach is on the table, continue with rest, if not, then feel free to move on.
1. That's three totalizers: 1-1/4", 2" line, 2nd 2" line, correct?
2. Is that three separate totals, one for each line, or one grand total, the sum of the individual line totals? Or the sum of the 1-1/4" total and 2" total and a separate 2" (2nd line) total?
quarterly means once every 3 months (approximately every 92 days), correct?
A daily total with a daily average flow rate is doable and makes sense because flow rates vary throughout the day.
Are they really asking for daily totals being averaged? If so, over what period? (that could a show stopper)
I would assume that a "maximum daily flow rate value? is what you call a "peak daily reading".
All in all, email of a generated report is the best approach, in fact one should email to two recipients/destinations, where one is a back-up.
Old March 3rd, 2018, 06:06 AM   #13
Aabeck
Member
United States
Aabeck is offline
Aabeck's Avatar
Danw,
1. Yes, 3 totalizers
2. It will be 2 totals - the 2 discharge pumps will be combined (2" pump & 1-1/4" pump)
3. Quarterly is what was requested - the first week of Jan, Apr, Jul & Oct.
4. The average would be of the gallons per day over the quarter, the daily log would be gallons pumped - they are not asking for a flow rate (yet)
5. Yes, they want the daily count of gallons & the average gallons per day for the quarter being reported. The peak value will be the day that quarter with the highest gallon count.
6. The customer has already said they would like 3 emails sent - 1 to the QC engineer that usually reports to the county and 2 others as backup, with the probability of emailing it directly to the county in the future if somehow 3 people still don't get it through to them.
__________________
http://aabeck.com
Old March 3rd, 2018, 06:09 AM   #14
cardosocea
Member
United Kingdom
cardosocea is offline
Consider yourself lucky... I have to log a similar thing at work and provide continuous sampling recordings. However, no one can tell me what continuous sampling means. Once a second? minute? hour? No one knows and no one can point me to the legal document that specifies continuous sampling.
In our plant, since the system is quite remote we put in a radio telemetry that gets the pulses from the flowmeter and we have a SCADA system that compiles this data into a report format that they accept as valid. No PLC involved as the radio setup has its own IO.
Also, bear in mind that they will likely require regular calibration (the Government, that is), so make a provision for that to be "easy" on your set up.
Old March 3rd, 2018, 07:24 AM   #15
danw
Member
United States
danw is offline
danw's Avatar
The Honeywell is not a fit. It has specific record generation functions but not quite to the extent needed for everaging daily totals.
Some other comments on the task:
Accuracy:
The most accurate total will be the one calculated by the flow meter and communicated digitally to the receiver (Modbus or Ethernet/IP)
The second most accurate is when the receiver counts 'total' pulses (say one pulse every hundred gallons) from the flow meter.
Third most accurate is having the receiver total a frequency output (0-5KHz = 0-max flow rate)
Least accurate is having the receiver totalize an analog flow rate signal.
Calibration:
One advantage of digital communication (Modbus or Ethernet/IP is that the there's nothing to calibrate on the receiver, leaving only periodic calibration of the flow meters.
Major magmeter vendors should have some means of "verifying" an installed magmeter eliminating the need to pull the flow tube and have it sent to a cal lab with a flow stand. Siemens does this by renting their Verificator box, which tests the tube coils and magnetic field and the converter's electronics and creates a one page pdf document that every water/waste wster plant I've been in has accepted as suitable evidence of in-situ 'calibration'.
Reply
Jump to Live PLC Question and Answer Forum
Bookmarks
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Similar Topics
Thread Thread Starter Forum Replies Last Post
WinCC flexible 2008 logging timing error. falgunvasava LIVE PLC Questions And Answers 3 January 21st, 2011 02:19 AM
Horizontal Tank Level Measurement & Logging Joe_WaZoo LIVE PLC Questions And Answers 19 September 26th, 2009 09:24 AM
Logging on MMC (wincc flex) Combo LIVE PLC Questions And Answers 29 June 30th, 2008 09:20 AM
PID problem... taz3m LIVE PLC Questions And Answers 104 May 21st, 2008 12:56 AM
Data logging & reporting ckchew666 LIVE PLC Questions And Answers 18 November 11th, 2005 11:08 PM