cx-protocol

dear sir's,
i have OMRON CJ1M CPU with SCU41-V1 CARD for RS-422/485 communication with omron inverter of model V7 via PMCR(260) Instruction. now i want to replace the V7 inverter with V1000. i have made all the port settings and parameter settings for V1000. but i am not much familiar with cx-protocall. i wnat to edit the send and receive sequence for V1000. i have the sequece as mentioned below for V7 inverter. please can some one help me on this regard.
send message for v7 inverter was written as mentioned below.
send msg:
SD(0)_1 <a>+[100118000102]+(R(2),2)+<c>
SD(1)_1 <a>+[0300230001]+<C>

RECEIVE MSG:
RV(17)_1 <A>[0302]+(W((1),2)+<C>

i could not understand the data [100118000102] which was not clearly mentioned in any of the manual.

thanks and best regards,
anushamoorthy.s
  Reply With Quote
Old March 6th, 2018, 05:57 AM   #2
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Cobourg
Posts: 2,551
http://www.omronkft.hu/nostree/pdfs/...-v7az/v7az.pdf

The above manual is for the V7 inverter. It looks like this may be modbus communication.
You can tell by the set up of the SCU41 card.
http://mikrokontrol.rs/proizvodi/pdf...OperManual.pdf

The inverter manual is the reference you need to determine the information being sent to the device.
Regards,
__________________
Garry
http://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
  Reply With Quote
Old March 6th, 2018, 07:22 AM   #3
scornush
Member
India

scornush is offline
 
Join Date: Mar 2018
Location: saudi
Posts: 2
cx-protocall

dear sir,
thank you so much for your prompt assistance. here we are using modbus communication. in the PLC program we are using {PMCR(260) instruction with control word 1 as #110(position 0 is used for scu41-v1 card), with control word 2 as (&212, &239, &240) sequence no (1, 14, 15) in the attached photo (1.modbus sequence),& first send word with data of frequency reference1,2,3,4 & acceleration deceleration 1,2,3,4}. the above said program was done for V7 inverter in that i have replaced part of V7 inverter with V1000 which falls under sequence 1(&212). i would like modify this sequence to communicate with v1000 inverter which involves send and receive of 2 bytes of frequency reference. i have attached the photos of cx-protocall which was programmed for V7 inverter. i want to add new sequence, send&receive msg for V1000 inverter. so please help me how to write for the v1000 inverter. the data to be transfered for v1000 is same as of v7. but i confused with register addressing. so please help me to modify as required. thanks in advance
Attached Images
File Type: jpg 1.MODBUS SEQUENCE LIST.jpg (65.5 KB, 4 views)
File Type: jpg 2.SEQUENCE 1.jpg (54.4 KB, 4 views)
File Type: jpg 3.SEND MSG LIST.jpg (58.4 KB, 3 views)
File Type: jpg 4.RECEIVE MSG LIST.jpg (66.9 KB, 2 views)
File Type: jpg 5.MATRIX LIST.jpg (57.6 KB, 1 views)
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC Protocol ssamir LIVE PLC Questions And Answers 1 October 27th, 2010 09:19 AM
Gem80 ESP protocol to modbus ESP- any suggestions (redlion maybe)? 2stepsforward LIVE PLC Questions And Answers 7 June 30th, 2010 09:51 AM
Redlion Protocol Converter Problem murarisetty_apparao LIVE PLC Questions And Answers 7 April 30th, 2008 07:55 AM
advantech with Twincat over Parker with Omron CX Supervisor rock LIVE PLC Questions And Answers 3 March 7th, 2004 06:54 PM
Protocol creation in Omron CJ Omronfaq LIVE PLC Questions And Answers 1 November 19th, 2003 04:56 PM


All times are GMT -5. The time now is 10:53 AM.


.