plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old March 7th, 2018, 10:46 AM   #1
abishur
United States
abishur is offline
RSLogix 500 Address Descriptions
Using RSLogix 500, I add a description to a specific address (Let's say N7:0) then I use that address in a scaling block. I would expect to see the description of the address, but all I see is N7:0. It's been a long time since I used RSLogix 500 and I can't remember if this is just how it works or if I'm forgetting something obvious to display the address description. Is there a way to display address descriptions when used inside other instructions (Add, subtract, SCP, etc)?
Old March 7th, 2018, 11:00 AM   #2
Operaghost
United States
Operaghost is offline
Operaghost's Avatar
The description for an output instruction would come from the Destination address. If you used the address as the Source, you would not see that description.
OG
Old March 7th, 2018, 11:07 AM   #3
abishur
United States
abishur is offline
Ah, which would mean that for an instruction like the SCP instruction, only the destination address description is visible and there is no way to show the description of each address being used. Oh, well. I was hoping I had forgotten something, but apparently I had not.
Old March 7th, 2018, 11:41 AM   #4
Mickey
United States
Mickey is offline
Mickey's Avatar
Quote:
Use the rung comment for that.see link
https://www.youtube.com/watch?v=dUTL7BD9mRI
You could add the description to the "instruction"(not the address) see link
https://www.youtube.com/watch?v=2oncu5NlclQ
__________________
Mickey
If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
Old March 7th, 2018, 12:58 PM   #5
Operaghost
United States
Operaghost's Avatar
Yeah I think the rung comment is the way to go.
Just bear in mind that the Instruction Comment ties itself to the instruction AND the output address. So it is not unique to just that one instruction. If you had another SCP that used the same destination address, you would get the same comment again.
The Rung Comment attaches to the last output on the rung. So if that output where used elsewhere as an output, you would get the same rung comment. For example picture a OTL latch instruction as the last output on one rung and an OTU unlatch as the last instruction on another rung.
  • The rung comment would be displayed on both rungs. Changing one would change both.
  • The address description would be displayed on both instructions. Changing one would change both.
  • The instruction comment would be unique for each instruction. Changing one would NOT change the other.
Now there is an option for changing rung comments so that they attach to rung numbers instead of the last output, but that can get ugly. Particularly when different computers connect to the same controller.
You'll notice for the rung comment I mentioned the "last output". Imagine that rung with an OTL as the only output. Now put a branch around it with a different output instruction below and your rung comment would disappear. Move the new instruction above and carry the existing one below and the rung comment reappears.
When you work on the 5000 you can forget how painful descriptions were in the 500. Everything had a trade-off.
OG
Old March 7th, 2018, 06:16 PM   #6
JaxGTO
United States
JaxGTO is offline
You can also give the address a symbol and then turn on replace addresses with symbols.
Old March 7th, 2018, 06:43 PM   #7
daba
United Kingdom
daba is offline
daba's Avatar
A couple of things to note about "descriptions" in SLC Logix500, which also applied to PLC5 and PLC2 systems.
When you create a description for a data-table address, it can be "attached" to either the address itself (Address Comments), on its own, or to a combination of the address AND the specific instruction (Instruction Comments).
I hate it.
It means you can have multiple comments for the same physical address.
Example : assume you have an internal bit B3/0 derived from the state that the "gate is open". You could attach "The gate is Open" as the descriptor for XIC B3/0, and "The Gate is Closed" to XIO B3/0. On top of that, you could have "This bit describes the gate condition" attached to OTE B3/0.
IMHO this just causes confusion, and I have never, NEVER, used "Instruction Comments", taking the view that a comment should describe what the address IS, not what it DOES.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
RSLogix Emulate 500 v 6.00 not opening RSS Saulo35 LIVE PLC Questions And Answers 6 November 30th, 2016 01:08 PM
RSLogix 500 and 5000 licensing and versions ryangriggs LIVE PLC Questions And Answers 8 June 29th, 2016 11:09 AM
Symbol Descriptions RSLogix 500 ajb1131 LIVE PLC Questions And Answers 1 February 28th, 2006 12:10 AM
RSLogix 500 bug bit me today.... jstolaruk LIVE PLC Questions And Answers 1 February 3rd, 2006 01:08 AM
RSLogix 500 warning Beryl LIVE PLC Questions And Answers 6 April 13th, 2004 02:53 PM