PLC Mounted Vertically

Hello!

I am working on a project to replace an AB SLC 5/04 10 slot rack which is currently mounted vertically, with a Compact Logix 1769-L33ER and associated 1769 I/O.

Are there any issues or caveats with mounting the Compact Logix vertically?

TIA,

Greg
  Reply With Quote
Old March 8th, 2018, 02:18 PM   #2
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,313
From the Manual:
Quote:
A CompactLogix 5370 L3 control system must be mounted so that the
modules are horizontal to each other. If you separate modules into multiple
banks, the banks can be vertical or horizontal to each other.
I think the big issue is cooling. But if the 5/04 worked vertically not sure why the L33 wouldnt work too.
Attached Images
File Type: jpg CLX mounting.jpg (47.9 KB, 132 views)
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old March 8th, 2018, 03:06 PM   #3
bernie_carlton
Lifetime Supporting Member + Moderator
United States

bernie_carlton is offline
 
bernie_carlton's Avatar
 
Join Date: Apr 2002
Location: Yakima, Washington
Posts: 6,253
The natural airflow should be vertical from the bottom to the top of thee components. Other orientations are not recommended. But if you have forced air (fan) through the modules it might work.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.

www.thePLCguy.com
  Reply With Quote
Old March 8th, 2018, 03:21 PM   #4
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 306
For me the answer can only be one: if the specifications say that it must be mounted horizontally, it can not be mounted vertically ... and the guarantee would be lost
__________________
Suppanel HMI
  Reply With Quote
Old March 8th, 2018, 03:36 PM   #5
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 429
Obviously it's not ideal for cooling, so if the enclosure will stay very warm, I wouldn't do it without a fan as Bernie suggested.

Check the specs on the PLC though, it is probably rated for 140*F or so, so if you keep the enclosure cool you will probably be fine.

I've seen plenty of PLCs mounted vertically to know it's not a sudden death situation.
  Reply With Quote
Old March 8th, 2018, 04:17 PM   #6
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,585
It was not recommended for the SLCs either. From the manual:

ATTENTION
Vertical mounting is not recommended due to thermal
considerations.


  Reply With Quote
Old March 8th, 2018, 04:48 PM   #7
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,961
Quote:
Originally Posted by Greg Dake View Post
Hello!

I am working on a project to replace an AB SLC 5/04 10 slot rack which is currently mounted vertically, with a Compact Logix 1769-L33ER and associated 1769 I/O.

Are there any issues or caveats with mounting the Compact Logix vertically?

TIA,

Greg
Most of the products I've used (mostly Siemens) come with temp ratings for different mounting positions. Horizontal is best, but there is often a de-rating if you want to mount it at a different angle.
  Reply With Quote
Old March 8th, 2018, 07:24 PM   #8
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,401
Quote:
Originally Posted by mk42 View Post
Most of the products I've used (mostly Siemens) come with temp ratings for different mounting positions. Horizontal is best, but there is often a de-rating if you want to mount it at a different angle.
That is not a helpful reply, considering the OP has specified the hardware in question.

It is always best to adhere to the manufacturers recommendations for mounting, which can be found in the reference documentation.

I have not seen any documention from A-B that "allows" vertical mounting of either SLC, CompactLogix, or ControlLogix, chassis,

Of course, you can always "roll your own", provide forced cooling with ducted fans etc., but if the manufacturer says "horizontal", they will always stick by their own recommendations, and support, should anything go wrong, will be severely limited.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Old March 8th, 2018, 07:31 PM   #9
lanman
Member
Canada

lanman is offline
 
Join Date: Nov 2003
Posts: 29
34499 | Date Created: 03/09/2006 | Last Updated: 01/10/2018
Access Level: Everyone

Question
Is vertical mounting of SLC, Micro800, PLC and LOGIX processors, chassis, and power supplies a supported configuration?

Answer
Unless otherwise specified, Allen Bradley/Rockwell Automation does not recommend vertical mounting of any SLC/PLC/LOGIX chassis or power supplies.

Temperature, Shock and Vibration are all tested and rely on horizontal mounting in order to meet our published specifications. Temperature especially relies on convection air flow for cooling of the modules and mounting vertically would prevent this.

One noted exception is the CompactLogix 5370 L1x controllers. Vertical mounting of these controllers is supported, however, the 2" air gap all around the controller must always be maintained.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PLC to replace spark detection/suppression system in LP ducting, good idea or bad? SolarNinja LIVE PLC Questions And Answers 17 January 7th, 2017 11:03 PM
Difference between Modular and Rack Mounted PLC tahir4awan LIVE PLC Questions And Answers 3 October 7th, 2012 09:53 PM
Magelis hmi xbtg4320 and a twido plc twdlcda24drf asim_rana LIVE PLC Questions And Answers 23 February 3rd, 2012 01:37 PM
PC to PLC Protocol TheRixta LIVE PLC Questions And Answers 13 December 17th, 2008 01:56 PM
rack mounted plc joku LIVE PLC Questions And Answers 7 June 25th, 2005 04:30 PM


All times are GMT -5. The time now is 03:02 PM.


.