5069 I/O fault
phuz
Jun 2008
Mohnton, PA
1,044
I added a 5069-OW16 module to a system yesterday that currently has a 5069-L306ER processor and a 5069-IY4 module. The OW16 was tested and running when I left yesterday, but I got a call this morning saying that the pump we wired to it was not running and the card's MODULE STATUS indicator was flashing red. What could possibly make that card fault while the rest of the system is running OK?
Module configuration will dictate if a controller controller fautl occurs if the connection fails while in Run Mode. See the Connection Properties of the module and the setting "Major Fault On Controller If Connection Fails While In Run Mode".
As far as why the module faulted, I don't have that magic sense that can reach out to the circuit and tell you why; wish I did.
I'm just wondering what things can make a module fault like that. I've never seen it happen. Brand new out of the box module, too.
Is the power on 5069-OW16 24VDC or 120VAC?
5069-OW16 Channel Status LEDs are flashing red after applying 120 VAC SA Power
1070979 | Date Created: 12/14/2017 | Last Updated: 02/09/2018
Access Level: Everyone
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/1070979
The module is on 24VDC power. As I stated, the MODULE STATUS is flashing red, not the channel status.
Supposedly with these new 5069 relay output modules, they don't have any internal suppression for inductive loads (which I would guess account for the majority of loads out there), so connecting an inductive load, as we did, to power a motor starter, can introduce "noise" into the module and cause it to fault. Talk about poor design. Funny how the 5069-OW16 manual makes no mention of this and it took a call to AB tech support to reference a Tech Note about such loads. Not impressed.
same problem happening here
I am troubleshooting a rack of 5069 I/O that has been experiencing repeated comms failures as well. I have 1 5069-OW16 in the rack, connected to a half-dozen or so old 24VDC MAC valves. The first time I saw this error it was this card at the main point of failure (all cards to the left were still talking). But since then it seems to be the entire rack going off-comms when it happens. All I/O is 24VDC, no 120VAC. The rack config is below:
5069-L310ERS2
5069-IB16
5069-IB16
5069-OB16
5069-FPD
5069-OW16
5069-HSC2xOW4
5069-IB16
5069-IB16
5069-IB16
Anyone have any luck fixing/working around this problem?
5069-L310ERS2
5069-IB16
5069-IB16
5069-OB16
5069-FPD
5069-OW16
5069-HSC2xOW4
5069-IB16
5069-IB16
5069-IB16
Unfortunately, it looks as if you need to use a load resistor. Because we did not have one, and needed to keep running, I had the electricians wire in a temporary 24vdc ice-cube relay to drive the starter. We are upgrading the starter very shortly and I strongly suggested a 24vdc coil. So far it's been OK on 24vdc. Still not happy with the results.
I notice you have an FPD in your tree. Why is that? Extra power?
I found in the last 5069 commission that the inut modules are very sensitive to noise on the input signal wires; more so than 1769 or 1734 inputs. Extra care had to be taken to route wiring father away from vfd output wiring than in the past.
The FPD was (I'm told) a result of the design in IAB. The engineer designing this followed the IAB guidelines and I thought doing that would pose no problems. :rolleyes: The IO in the cabinet is all 24v, no 120v anywhere in the box. All the VFDs are in a separate cabinet but the inputs and VFD cables may be too close somewhere on the machine. That said... I'm VERY disappointed that it's that finicky on noise. If this were all 1756 IO I'd be virtually certain this wouldn't be happening.
You're correct. This doesn't happen with 1756 I/O. I have several of these 5069 PLCs installed at various customers and I'm wondering if it was a bad choice.
We're in the same boat... went with the new platform for the longest life cycle available and now we have random IO failures. Not good...
I have the same issue on 2 installs. 5069-IQ16 24vdc input at reference does not initiate the input. Re-routing of the wiring solved the issue. 5069-IF8 input properly shielded had to be re-routed not to induce a fault on the card.
I have discontinued using the 5069 i/o until AB solves the issue.
Rick
Rick
Have you made AB or your supplier aware of this? If we want a fix, it's important that they know of all these issues.
Of course I informed my AB rep of the issues, and I apologized for wasting his time after he deduced that I must have incorrectly applied his product (for the past 40 years).
Rick
Is there a known issue with V32 and displaying the correct Energy Storage Fault Information? We have a ton of these out there deployed over the...
567
We have an installation with with 6 Compactlogix 5069-L3X0ER PLCs. Within the past week, two of the 6 have crashed with the unrecoverable fault...
2,648
Hi gang, We just recently started using these newer controllers, and I have a energy storage fault on one of them. It's not causing any issues...
7,309
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
125
Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the...
417