Allen Bradley 1762-IF2OF2 12 bit resolution, but 0-32760? Does anyone know why?
TimWilborne
Oct 2005
Roanoke, VA
2,210
Hi guys, I'm working on an article about the bit resolution and precision of a 1762-IF2OF2. I know it is 12 bit which is 0-4096 and that the data is shifted by 3 bits to take up bits 3-14, making the range 0-32,760 instead. But I'm not sure I fully understand why this was done.
Does anyone know why this was done? Here's the explanation of the shift, I just think it leaves a big question lingering as to why. Obviously it makes the value look more precise, but that just doesn't seem like the correct answer.
https://www.theautomationstore.com/rslogix-500-analog-bit-resolution-and-precision/
I can' say for sure but I would think is the resolution of the chip they use in card
12bit analog to digital are more common and cheaper, while they do make higher resolution chips they start to get pricey
Yes, but 12 bit is 0-4096. There is a 3 bit offset making the 12 bits use bits 3-14, changing the range to 0-32760. Why?
Probably ease of data transfer over the backplane bus and within the operating system, where data words are likely 2 byte/16 bit words. Sign bit uses the MSB.
I don't think there's a low-level technical reason, but rather a collection of decisions for compatibility and history.
MicroLogix is based on the SLC-500 operating system, of course, and the old 4-channel analog modules for the SLC used 12-bit A/D converters and provided a value between 0 and 4095.
But the newer MicroLogix 4-channel analog modules (1762-IF4) had higher resolution; 15 bits plus sign.
So when they built a low-resolution combination module for the same platform, the question arose; do we make this compatible with old examples and legacy code from the SLC-500, or do we make it as close as possible to its 4-channel, 15-bit siblings ?
The evident decision was to just shift the data left, so that the full-scale value was similar despite the resolution being lower.
Thanks Ken. I figured I was missing the obvious. I didn't think about matching up to the 1762-IF4's units.
Now why didn't they continue that with built in analog?:mad:
Yes! We do this internally on our products. Analog inputs are 'normalized' by shifting them left to make signed or unsigned numbers. We shift unsigned inputs left 15-number of bits and signed inputs 16-number of bits. This way all our code is written for 0-32767 or -32768 to +32767. Sometimes we filter the inputs. The lower bits arer used then. When computing analog outputs for a servo valve or motor, the outputs are always normalized to be -32768 to 32767. If the output has only 12 bits then only the upper 12 bits are used. However, we keep track of the lower bits to provide a PWM effect on the lower bits.
Things have changed with the new 32 bit CPUs. We now have 18 bit analog inputs but the values are still shifted left
I think this is common in motion control. It doesn't surprise me at all that others would do the same. This way the main part of the code always treats the values the same regardless of the number of bits the inputs have.
Thanks for the explanation Peter. It makes more sense to me now.
Interesting.... Siemens use the lower 3 bits as diagnostic bits, years ago this foxed me a little (RTFM doh..) So in that case we used to move the lower 3 bits to flags for diagnostic purposes then shift the data to remove them giving the correct value.
I have 1769-IF4 module and 1766 micrologix 1400 series B controller, when connecting Analogue input in module it's showing maximum values of...
1,669
I'm working on developing a standard program across about 6 or 7 dozen machines that contain nearly identical controls, with the exception of one...
2,627
have a issue that i can not figure out what to do to correct. we have hundreds of machines that have molds with J type thermocouples that then go...
2,505
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
41
