plc storereviewsdownloads
Reply
Thread Tools Display Modes
Old November 19th, 2019, 11:06 AM   #1
Leukic
United States
Leukic is offline
1734-AENTR Input light issue
Gaurdlogix 5380 tied into 1734-AENTR. Safety scanner ossd1 and ossd2 are in I0 and I1 respectively. Common is hooked to 4&5. When we reset the scanner we get 24vdc from the scanner at the terminals of I0 and I1. But niether input shows to light up nor swap states in the program. Kinda stuck on this one. i may try to swap in a new input module and see if it works.
Old November 19th, 2019, 11:49 AM   #2
Geospark
Ireland
Geospark is offline
Geospark's Avatar
You probably need to set the "Point Mode" for the input points in the software?
Without this set the inputs will be inactive.
Go the the module properties for the 1734-IB8S and then to the "Input configuration" tab.
Under "Point Mode", select the Safety function for the individual input points.
Usually for a light curtain or similar you will select "Safety".
You also setup for Single or Dual function here with "Point Operation".
Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
Old November 19th, 2019, 12:16 PM   #3
Leukic
United States
Leukic is offline
Regards,
George
I found it. Just as I read you reply a little bit ago. When our engineer set up this stuff under config he forgot to set the status of the inputs they were set as NOT USED. Not sure why I didnt check that. Could because he said it's good to go haha. Thanks Geospark
Old November 19th, 2019, 12:22 PM   #4
Ken Roach
United States
Ken Roach is online now
Ken Roach's Avatar
The Input channel LED will also remain OFF if the module isn't configured yet, or if it's configured incorrectly for the inputs.
Did you inadvertently associate either of the Test Output signal sources with the inputs ? The inputs would be expecting to see the pulse train from the Test Output, not a steady 24V signal (which would indicate a short to 24V).
Otherwise your wiring sounds correct for a light curtain or safety scanner connection, like the example on Page 62 of the POINT Guard I/O User Manual.
edit: answered correctly while I was looking at the user manual and contemplating coffee.
Old November 19th, 2019, 01:24 PM   #5
Leukic
United States
Leukic is offline
Thanks Ken!
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Analog Input 1734 Ie2v flashing red bornwild LIVE PLC Questions And Answers 2 October 26th, 2019 12:41 AM
RSLogix 500 - I/O mapping question toads LIVE PLC Questions And Answers 8 September 25th, 2019 12:40 PM
FactoryTalk View SE Numeric Input Focus zacslade LIVE PLC Questions And Answers 1 March 2nd, 2016 06:26 AM
1762-IF2OF2 Analog Input Problem davidgay LIVE PLC Questions And Answers 22 August 14th, 2013 05:25 AM
Bit shifting? tlvaun LIVE PLC Questions And Answers 17 December 5th, 2002 11:51 PM