Difference between inverters

Dear experts,

Sorry for disturbing you all in the first place. Hope you all don't mind to answer me a question...

Well, may I know is it bigger capacity drive Omron inverter cannot be functioning or control by plc when turning on a motor with smaller load? I got read a statement in that manual mentioning that, need to use a smaller size of capacity to drive the motor with 'about the same' load. I change to a smaller capacity of inverter and it works. Is it correct by the way or I missed out something? If is it correct, then any expert don't mind to provide some valuable explanation for me? Is it some other brand of inverter also giving the same problem like this?

Thank you to those who willing to spend time to read this thread... (",")


regards,
Freshy
  Reply With Quote
Old March 11th, 2005, 07:32 AM   #2
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 3,638
Firstly, (/sigh) a PLC has nothing to do with an Inverter (VFD, AC DRIVE, SERVO DRIVE, VECTOR DRIVE, et al) other than telling it to "GO", "STOP", "REVERSE", "RUN AT x SPEED/TORQUE".

Now, second question, in general, an Inverter (VFD, AC DRIVE, SERVO DRIVE, VECTOR DRIVE, et al) should be close in size to the total rated load of the motor(s) it is connected to.

Yes, you can oversize a drive, but there are limits. You can probably run a 10KW motor on a 25 or 30KW drive, but trying to run a 10KW motor on a 100KW drive will (almost always) cause problems. The simplest reason? Drives need to control and monitor the current delivered to a motor. The feedback devices for current in drives are optimized to a certain range of loads, generally 30% to 150% of the rated drives capacity.

Running too small a motor can cause problems with stability in the current/torque loops, as well and potentially damage the connected motor.

Think of it like a load-cell. Controlling 50 to 100KG tension on a loadcell rated for 150KG isn't much of a problem. Controlling 10g to 20g on the same loadcell is.
  Reply With Quote
Old March 11th, 2005, 04:12 PM   #3
DickDV
Member
United States

DickDV is offline
 
Join Date: May 2002
Location: Kalamazoo MI
Posts: 1,915
On an open loop or V/Hz or scalar drive, mismatching isn't much of a problem within a 5 or 6 to 1 ratio.

The problem comes when trying to use Flux Vector or Sensorless Vector Drives. They probably should stay within about a 3 to 1 ratio to function properly. And, as stated above, the reason is poor detection and measurement of unexpectedly small motor lead currents.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Inverters with non-inverter rated motors JRW LIVE PLC Questions And Answers 28 September 29th, 2005 01:23 AM
Difference between Industrial Ether net and Ethernet chauhanrasikendra LIVE PLC Questions And Answers 6 February 12th, 2005 03:00 PM
Difference between siemens CP5410-A1 and CP5412-A1 donex LIVE PLC Questions And Answers 0 February 5th, 2005 09:03 AM
Soft starters vs Inverters Prince LIVE PLC Questions And Answers 2 November 23rd, 2004 06:59 AM
Difference between DDE,ActiveX and OPC? abhilashponoli LIVE PLC Questions And Answers 1 June 3rd, 2004 07:47 AM


All times are GMT -5. The time now is 08:44 AM.


.