Flex IO to PLC5 addressing
Hey guys. I have a flex IO module 1794-IT8 that is talking via controlnet to a PLC5. The question I have is that the input in question appears to be scaled already by the time it reaches the PLC 5. That is, we are taking the raw integer that is coming from the FLexIO and displaying that exact # for the operators and calling it the Process Variable. I read the manual for the IT8 and am only confused even more. Can someone simply explain how the input is scaled and where I can get a visual of it. This is just for personal understanding for future reference. Thanks.
Russ |
|
|
|
#2 |
|
Lifetime Supporting Member
|
The input is scaled based on the channel configuration (mV/TC, and what TC type), and is indeed scaled properly into engineering units scaled up by 10. The Data Type can be configured programmatically, but defaults to degrees C. Other options are Degrees F, Raw bipolar, and Raw unsigned integer.
The PDF manual can be found at: http://literature.rockwellautomation...m007_-en-p.pdf |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| PLC5 Analogue IO addressing | TimeFluxCap | LIVE PLC Questions And Answers | 4 | December 26th, 2004 06:26 AM |
| AB PLC5/80B RIO Flex IO Fault | corkers | LIVE PLC Questions And Answers | 9 | September 4th, 2004 01:12 AM |
| PLC5 Indirect addressing | chavak | LIVE PLC Questions And Answers | 4 | April 15th, 2004 12:10 AM |
| PLC5 HotBackup with Flex IO Configuration | Joydip | LIVE PLC Questions And Answers | 0 | May 7th, 2002 06:22 AM |