S7 Function Block Question
I am using a function block to do repetative math calculations. I noticed that the results were coming back incorrect. After playing with the Function, I tracked it down to a constant that I was setting. Is there a special way to set constants in FB's?
I am taking a Real number and sending it to the Function where I divide it by 100000.0 and do other math on it. I noticed in monitor mode the constant actually had a large random looking number in it.
To troubleshoot it, I Replaced the constant with an address to one of my DB's (shared).
I noticed also in a different FB that it did not work and it seems the internal temp registers do not transfer to the next network. Is there a trick to that too?
Lance
__________________
No matter where you go in life.....there you are.
Old May 2nd, 2005, 09:43 PM   #2
S7Guy
United States
S7Guy is offline
The internal registers will transfer to the next network, so you must be doing something that affects the value. Can you post a snippet of the code? Even of you switch to STL and cut/paste the code as text, that would be fine.
There is no special way to set a constant in a function. You can even set it literally without using a variable. Or, you can use any of the other data types (even local data, as long as you initialize it).
Old May 3rd, 2005, 02:29 AM   #3
jvdcande
Belgium
jvdcande is offline
jvdcande's Avatar
This indicates you're not really using a constant, but a constant stored in a variable. Constants are what their name indicates: constant. I have never seen a real constant change value in S7 in whatever situation. Are you maybe storing the constant in a variable first? As S7Guy already indicated: a snippet of the code you're using would clarify a lot.
Temp variables are temporary, meaning if you leave the block these variables are lost. If you want to retain internal variables in a FB you have to make them static variables (STAT).
Kind regards,
__________________
Jean Pierre Vandecandelaere
Trainer nautical sector
VDAB Competentiecentrum
L. Blondeellaan 9
B-8380 Zeebrugge
Belgium
Old May 3rd, 2005, 08:33 AM   #4
snydl0ga
United States
snydl0ga is offline
snydl0ga's Avatar
Here is the STL code for the FB that is not working properly.
"Real to Int High/Low"
This FB receives a Real number and breaks it down to High and Low order Integers.
Example: 123456 Real would become 12 High 3456 Low.
When I use the 10000.0 as a constant it does not work but if I point these two locations to
a DBlock with the 10000.0 value in it, it works.
O(
L #Real_IN
L 1.000000e+004
/R
T #Real_1
AN OV
SAVE
CLR
A BR
O(
L #Real_1
TRUNC
T #Dint_1
AN OV
SAVE
CLR
A BR
O(
L #Dint_1
DTR
T #Real_2
SET
SAVE
CLR
A BR
O(
L #Real_2
L 1.000000e+004
*R
T #Real_upper
AN OV
SAVE
CLR
A BR
O(
L #Real_IN
L #Real_upper
-R
T #Real_3
AN OV
SAVE
CLR
A BR
O(
L #Dint_1
T #INT_High
SET
SAVE
CLR
A BR
O(
L #Real_3
T #INT_Low
SET
SAVE
CLR
A BR
= #Dummy
__________________
Old May 3rd, 2005, 08:38 AM   #5
snydl0ga
United States
snydl0ga is offline
snydl0ga's Avatar
S7 FB Question forgot to attach LAD
here is the LAD shot. Nope File too large. If you need, I will email it.
__________________
Old May 3rd, 2005, 09:26 AM   #6
SimonGoldsworthy
United Kingdom
SimonGoldsworthy is offline
SimonGoldsworthy's Avatar
There is a coding error in your processing, the last "move" loads a floating point number and moves it to an integer, this will produce what appears to be a random number in the result. You need to use ROUND to convert the floating point to a double integer, and then move the double integer to the integer.
When testing a function block like this, I always call it once but use flag words for the inputs and outputs. I put test data in the flag words using a VAT table and then monitor the output to verify the block is operating correctly before calling it more than once.
Be sure that the data you feed the block will not cause you problems later, for example what if you fed 3.4e+038 as the input ?
Old May 3rd, 2005, 02:26 PM   #7
snydl0ga
United States
snydl0ga is offline
snydl0ga's Avatar
Simon, Thanks for the explanation. I wrote this originally in ladder and was under the impression that the MOVE statement allowed any type to any type. Should that not work. That is why I had it there. I will test further though. I am still getting familiar with S7 and have a lot to learn.
Lance
__________________
Old May 3rd, 2005, 03:05 PM   #8
S7Guy
United States
S7Guy is offline
Lance, one thing you may consider when doing math like this is STL representation. It is much faster and easier to troubleshoot because you can follow the math in the accumulators as it is being processed. For instance, in ladder you needed about 65 statements, but in STL it only needs 13 to do the same thing (I think this will work, but I didn’t try it. Still, the concept stands.):
Code:
	 L	 #Real_IN
	 L	 1.000000e+004
	 /R
	 TRUNC
	 T	 #Int_High
	 DTR
	 L	 1.000000e+004
	 *R
	 L	 #Real_IN
	 TAK
	 -R
	 TRUNC
	 T	 #Int_Low
STL is also much more tolerant when using mixed data types, so a lot of the conversions can be eliminated. You just need to think in terms of the accumulators.
Also, like Simon says, you need to put in some range checking, unless you are clamping the input values to make sure you can never get an out of range number.
Old May 3rd, 2005, 07:17 PM   #9
snydl0ga
United States
snydl0ga is offline
snydl0ga's Avatar
Gotcha....I have been doing some STL and plan on getting better at it. I have begun to see the advantages.
Thanks for da help!
Lance
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
MPI comunication Manuel Raposo LIVE PLC Questions And Answers 22 July 16th, 2007 06:24 AM
Function Block with RS Logix 5000 amgc5 LIVE PLC Questions And Answers 3 February 29th, 2004 03:45 AM
what is the function Of TP Block m_abd_el_khalik LIVE PLC Questions And Answers 3 November 10th, 2003 06:37 PM
Function block help harryg LIVE PLC Questions And Answers 1 September 4th, 2003 05:41 PM
Need help with making 'integrator' function block? IanJohnston LIVE PLC Questions And Answers 4 June 13th, 2003 11:19 AM