Old May 28th, 2005, 05:20 PM   #1
ea44rl
Member
United States

ea44rl is offline
 
Join Date: May 2005
Posts: 1
code question

does the nec permit coax and current conductors in the same conduit?
  Reply With Quote
Old May 28th, 2005, 06:01 PM   #2
rsdoran
Lifetime Supporting Member
United States

rsdoran is offline
 
rsdoran's Avatar
 
Join Date: Apr 2002
Location: Birmingham, AL
Posts: 7,372
Its not a question of can you as much as should you. If the current conductors are AC, especially motor leads, they have a high probability of inducing voltage onto any cables parallel to them. Therefore any cable may give a false signal or have noise that interferes with its signal.

If the current carrying conductors are DC, with no inductance/motors, the probability is low.
__________________
http://www.patchn.com Industrial Electrical & Maintenance @ www.patchn.com "Tell me and I forget, show me and I remember, involve me and I understand."
  Reply With Quote
Old May 28th, 2005, 06:19 PM   #3
Terry Woods
Member
United States

Terry Woods is offline
 
Join Date: Apr 2002
Posts: 3,170
"Rock... Paper... Scissors..."

My local inspector said... "NO!"

That caused me some grief.

Considering that my coax is typically shielded, what's the big deal?

With respect to the NEC... the NEC sorta-kinda says no. Local jurisdiction has the final say... sorta...

When I say that the NEC "sorta-kinda says no", there are a couple of clauses which surrender the decision. One is a clause that says that rulings by local jurisdictions can over-ride the NEC. This happens quite often in my state (OR). Then there is a clause which then says that a local Professional Engineer can over-ride the NEC.

There is no clear statement (that I have found) regarding the authority of the local jurisdiction vs. the local Professional Engineer... or vice-versa.

It's almost like a case of... "Rock... Paper... Scissors..."

Aside from the FACT that the NEC is gobbledy-gook ((Humpty-Dumpty speak in Alice in Wonderland (do a search on this site for Humpty-Dumpty or Humpty.), or maybe Double-Speak from "1984")), it also appears that they (the NEC) want to maintain an impeccablly high degree of separation (deniability).

Gee, why does that attitude seem so popular lately... so current... so much in the news (as poor as it is) lately?

Gee... imagine a government running under the auspices of the NEC...

Lot's of rules, and yet, minimum accountability on the part of the rule-givers.

If it looks like a duck and quacks like a duck... damn, it must be....
  Reply With Quote
Old May 28th, 2005, 07:29 PM   #4
Rick Densing
Member
United States

Rick Densing is offline
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 1,538
We recently had a discussion along these lines.

If you are looking for for a code violation,- if the voltage in the current carrying conductors is higher than the insulation rating of the coax, you are in violation.
  Reply With Quote
Old May 28th, 2005, 10:46 PM   #5
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 5,929
All of the conductors in the same conduit must have an insulation voltage rating equal to the voltage rating of the highest voltage conductor. So if you have 480VAC motor leads in the conduit then all wires in that conduit must have a 600VAC insulation rating. That means that the 300V rated insulation on your coaxial cable isn't going to cut it. As far as I know, the NEC doesn't concern itself with the quality of signals you send, thats your problem.
  Reply With Quote
Old May 28th, 2005, 10:57 PM   #6
rsdoran
Lifetime Supporting Member
United States

rsdoran is offline
 
rsdoran's Avatar
 
Join Date: Apr 2002
Location: Birmingham, AL
Posts: 7,372
Its not a question of can you as much as should you.

Its sad when the Engineers dont/wont take the time to read what is said.

The best thing to do if having to deal with NEC code is obtain the book. The next thing to do is talk with any inspecting authority on their requirements.

The OTHER thing is that there is DEFINITELY NOT a code AGAINST using multiple conduits/raceways etc for different cables/wires
THEREFORE
Can you or should you?
__________________
http://www.patchn.com Industrial Electrical & Maintenance @ www.patchn.com "Tell me and I forget, show me and I remember, involve me and I understand."
  Reply With Quote
Old May 29th, 2005, 12:00 AM   #7
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 5,929
Article 300.3

(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.

(2)Over 600 Volts, Nominal. Conductors of circuits rated over 600 volts, nominal, shall not occupy the same equipment wiring enclosure, cable, or raceway with conductors of circuits rated 600 volts, nominal, or less unless otherwise permitted in (C)(2)(a) through (C)(2)(e).

Last edited by TConnolly; May 29th, 2005 at 12:04 AM.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Simulator, Simulation, Shadow Code Terry Woods LIVE PLC Questions And Answers 1 January 2nd, 2005 01:40 PM
Protecting my code in Koyo products jimpad LIVE PLC Questions And Answers 12 September 4th, 2004 11:07 AM
starting out Brendan Dixon LIVE PLC Questions And Answers 8 June 20th, 2004 08:48 PM
Automatin Direct Changes Download ArikBY LIVE PLC Questions And Answers 53 May 12th, 2004 12:05 AM
Mapping RSLogix Code Aaron LIVE PLC Questions And Answers 3 March 19th, 2003 12:04 PM


All times are GMT -5. The time now is 05:19 PM.


.