Questions about DF-1 protocol

Hey all,

We have a customer who will be using our controllers as part of a remote inventory picking system. The controllers communicate through aerocomm wireless modems. Our controllers will be interfaced to the clients of the wireless communications. There are two controllers for this remote system...one for the X coordinates, one for the Y coordinates.

The server is attached to an Allen Bradley with a DF-1 protocol. I believe it is a Micrologix

My questions are:

1. Can the DF-1 protocol interface with either ASCII or ModBus?

2. Does AB offer Modbus interface for the Micrologix?

3. If the answer is no to the above, what other options are there?

ModBus and ASCII are the protocols we support.

To all who respond, thanks for sharing your knowledge.

God Bless,
__________________
Stephen Luft - Eternity Sales (website) (email)
Representing: Kessler Ellis, and Wirefree CNC
Distributing: Kessler Ellis, Kepware, Triangle Research, Westermo and Wirefree CNC
(jewishheritagerevival)
  Reply With Quote
Old August 26th, 2005, 02:28 PM   #2
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 3,065
Depending on your Micrologics model and revision you should be able to do either.

I think you need to get to at least a Micrologix 1200 Series B before ASCII and MODBUS RTU are supported. But you can configure the channel as either.

You will be using the only prot on the plc form this function, however. So you will effectively give up you ability to monitor or program it. I believe there is a way to switch between user and system mode on the prot but I have never done that.

Keith
  Reply With Quote
Old August 26th, 2005, 02:49 PM   #3
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,260
The DF-1 protocol uses ASCII characters, and I believe it is published by Allen Bradley. It is not exactly public domain, butI don't believe there are royalties associated with it like there are for DH+.

Many A-B products support Modbus RTU, including some of the newer MicroLogix models. Some of the older ones don't, and I suggest you go to the A-B website for particulars on the models your customer is using. http://www.ab.com/

We have interfaced a number of different automation products with Modbus RTU to DF-1 protocol PLCs using the PRoSoft products. I suggest you look at them as an option. http://www.prosoft-technology.com/
  Reply With Quote
Old August 29th, 2005, 03:54 AM   #4
(8{)} ( .)
Member
Israel

(8{)} ( .) is online now
 
(8{)} ( .)'s Avatar
 
Join Date: Apr 2004
Location: Israel
Posts: 396
Hi Stephen,

Seeing as others have answered your questions I'd like to suggest that you look into supporting DF1. There are ActiveX and OPC servers available to make this easy. If your ML supports Modbus then you'll be OK but if you want to interface to an A-B controller that doesn't support Modbus then you'll probably spend less engineering time integrating and ActiveX or OPC solution than writing the ASCII ladder code in the ML. Finally, once you support DF1 then you won't have to worry about future A-B/DF1 installations.

Good Luck,

(8{)} ( .)

(Yosi)
  Reply With Quote
Old August 29th, 2005, 10:16 AM   #5
Peter Nachtwey
Member
United States

Peter Nachtwey is offline
 
Peter Nachtwey's Avatar
 
Join Date: Apr 2002
Location: Vancouver, WA, UMSA, United Marxist States of America
Posts: 5,858
Quote:
Originally Posted by (8{)} ( .)
Hi Stephen,

Seeing as others have answered your questions I'd like to suggest that you look into supporting DF1. There are ActiveX and OPC servers available to make this easy.
(Yosi)
A small PLC such as Entertron will not be able to use a OPC or ActiveX. An engineer a Entertron will have to add the protocol to the firmware. This will use valuable prom or flash space as the DF1 protocol is not just one protocol. It is a datalink layer and mulitple application layers depending on how many AB PLCs Entertron wishs to emulate.

Steve, we use DF1 as our standard protocol modbus as a option. The reason we prefer DF1 is that:

1. it has better support for different data types such as floats. The float type and double integer types are defined in DF1 and is a continually question if you monitor the modbus forums.
2. DF1 is not timing dependent, Modbus is. Modbus requires time at character times. This is not easy to do on a PC running windows. It may also be a problem on a PLC with long scan times.
3. DF1 supports segmented(file) and larger data areas.
  Reply With Quote
Old August 29th, 2005, 01:54 PM   #6
Jiri Toman
Member
United States

Jiri Toman is offline
 
Jiri Toman's Avatar
 
Join Date: Jun 2002
Posts: 498
If I remember correctly one of your previous posts stated that your controllers are coded in assembly. Undoubtadly so is ML 1000.
Last time I looked ML 1000 was using Intel 8051 type processor and it only had one processor for both ladder processing and communications.
You should be able to implement DF1 in assembly.
ML has a timeout adjustable in 20 ms increments, you can get away with just pegging it at 1s , that's what RSLinx does anyways.

You only need to move data to and from data tables ( AB uses DF1 for programming as well).

I have done DF1 in different languages including assembly and I like assembly simply because you can achieve maximum throughput.

Short term solution for you is to get a DF1 to ModBus converter.
They are costly and will slow the communications down.
Most wireless Modems use DF1 half duplex.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Pro-face Factory Gateway Protocol rhung LIVE PLC Questions And Answers 3 April 16th, 2005 09:24 PM
S7 PLC protocol rkorem LIVE PLC Questions And Answers 12 March 18th, 2005 02:53 AM
Protocol creation in Omron CJ Omronfaq LIVE PLC Questions And Answers 1 November 19th, 2003 04:56 PM
DF! protocol master driver query shroffsp LIVE PLC Questions And Answers 5 August 4th, 2003 02:16 AM
Using the directNet Protocol with DCM Modules across leased lines controlsbyjoe.com LIVE PLC Questions And Answers 2 March 19th, 2003 09:13 PM


All times are GMT -5. The time now is 12:53 AM.


.