anti tie-down circuit
darren
Dec 2002
I'm taking a course and I'm trying to figure out how to draw an anti-tie-down circuit. Does anyone know how?
I think you are talking about a circuit which requires an operator to have both hands on start switches in order to begin a machine cycle. This minimizes the possibility of an operator having a hand in the work area when a machine cycle is started. If one or both switches are "tied-down", the control will not allow a new machine cycle to begin.
The circuit is not complicated, what it does is important. This should be enough info for you to give it a shot. Post what you try and you will get help.
Yes. I can tell you what it should do, but you figure out how to code it, OK?
The idea is to have two push buttons, usually palm buttons on a machine that operates in a specific cycle. These buttons should be physically located so that the operator must use both hands to operate both buttons. The operator must operate both buttons simultaneously to start the cycle, and hold them both until the cycle progresses to some "safe point"--i.e. where the operator cannot physicaly get his hand(s) into the pinch point. He then may release the buttons and the cycle will complete. For a punch press, this "safe point" would be when the die closes at the bottom of the stroke. For some machines this "safe point" may well be the end of the cycle.
Now for the anti tie down / anti repeat. If the operator holds the buttons throughout the cycle, the machine must stop at completion of the cycle. Before the cycle may be started again, BOTH buttons must be fully released and re applied. This prevents the operator from running the machine in a "continuous" cycle. It also prevents him from "tying" down one of the two buttons and operating the machne one-handed.
Easy to do in PLC ladder logic, although not legal, I think, for lots of machinery, like presses, which require a lot of redundant circuitry.
plc anti tie down
Thanks Big Cheese and Mike Williams for your responses. Yes, that is what was meant by anti tie down. I've already completed it in relay logic, it's just that we have to convert it to plc's and we don't have a lot of resources at our disposal to figure it out. I'll try to work it out, though, and I thank you again for taking the time.
Darren
john paley said:
The operator must operate both buttons simultaneously to start the cycle...
Just to clarify this for Darren. As far as anti tie-downs go, simultaneously means "within a 1/2 second of each other".
I doubt you'll find an operator that can operate both buttons at EXACTLY the same time. I've seen quite a few operators that can't even do it in the 1/2 second window... :p
By the way, that's also a hint for Darren that you'll need to use timers!... :D
beerchug
-Eric
these are made in hardware
FYI, IMHO, for anti-tiedown, I'd never program it
where Safety, liability, etc. were involved.
There's a sub-$200.00 module made by NOLATRON (and
maybe others, I don't know) that does it all,
including the latching or unlatching feature.
I will say that a NOLATRON uses the N.O. contact and the
N.C. contact of the pushbutton.
See where that leads you.
Safety
As John mentioned, that and other issues with safety are not permitted to be done VIA PLC or control. Emergency stops, Anti Tiedowns and safety Lock-outs just to name a few. Although they can be diplicated in the PLC for status.
That isnt totally correct, there are a few PLC's designed to work with safety. AB has the GuardPLC's (which they bought from another company that is still being sold thru others as are some of their light curtains etc).
Safety issues look at redundant factors and a plc can provide those BUT when using a plc for safety issues it is not to do process work...ie it can only do the things involved with safety.
I have had to attend an abundance of seminars/training recently because of corporation issues on safety. At the same time I have to deal with engineers that do not seem to care (I suspect budget issues) about code/osha issues on what is suppose to be done to conform to the rules/guidelines.
There are many tools out there to use, it takes alot of time/energy to determine what to use.
I don't know how it is with AB GuardPLC, but I've worked with Pilz, there you have to use a Programme-block which i is Certified.
Using a Saftety PLC is no guarantee for that the code is right !!!!
beerchug
Steffen
Safety
I must not be up to date on my safety. I thought O.S.H.A. insisted that emergency stops & lockouts were to be hardwired. If they have strayed from that I think it is a mistake.
Roger
Roger. PLC control of a safety circuit is possible. BUT it is not done with any normal PLC. The Pilz and the AB safety PLCs are programmed with function blocks that are certified by a relevant authority, the controllers themselves use at least 2 processors that must match on the decision and the inputs are as far as I can remember are duplicated. Regards Alan Case
Good day all. I have a machine to automate. It is a 2-ton heat press. It moulds small plastic parts. The mould cycle is initiated after the...
3,083
I searched and could not find an answer. The machine is a pneumatic press,two cylinders 32mm bore. Can this machine be built per OSHA safety...
3,731
Hello, I am in school learning about PLC and RLL and my professor gave us an assignment to try to figure out how to write code for a anti tie down...
85
30,016
Can someone show me an example of an anti tie down program? I am using micrologix 1200.
5,728
I am setting up an educational work cell in my University's automation lab. It is a senior thesis project and will be used for educational...
28
8,641