Unhappy SLC 500 serial communication

Hi all,

I am experiencing a 'wierd' issue with serial port on a SLC 5/05. The processor is new out of the box. I had previously loaded a program and configuration through the serial port. However, when I attempt to establish communications with RSLinx via DF1 I can no longer connect to the processor.

When I click on 'auto-configure', I get a message "failed to find baud and parity!" The baud rate on the processor is 19200 and is the same for my laptop COM1 port as well.

Interestingly, I dumped the program from the processor and was able to download the same program through the serial port. However, the same issue arose again. The serial port seems to be "dead".

I can connect to the processor via ethernet port just fine. But I will need the serial port to message to an InView display.

Any help would be greatly appreciated.
  Reply With Quote
Old December 9th, 2005, 11:46 AM   #2
jstolaruk
Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: SE Michigan
Posts: 2,082
Check channel 0's configuration when you are connected. It may have slipped out of system mode/df1 protocol into one of the four other protocols (DH485, DF1 radio modem, etc.) or user mode.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Old December 9th, 2005, 12:15 PM   #3
bernie_carlton
Lifetime Supporting Member + Moderator
United States

bernie_carlton is offline
 
bernie_carlton's Avatar
 
Join Date: Apr 2002
Location: Yakima, Washington
Posts: 4,593
Alternately just check the channel 0 setup in your offline program. If it isn't DF1 then you should have recieved a warning on download about the communications being lost. If it is set up to some other mode (DH-485 etc then you may have to change RSLinx to connect. If it is ASCII mode then you probably cannot connect in that manner.
__________________
Controlling outputs is the PLC's way of getting its inputs to change.

www.thePLCguy.com
  Reply With Quote
Old December 9th, 2005, 06:35 PM   #4
Greg Dake
Member
United States

Greg Dake is offline
 
Greg Dake's Avatar
 
Join Date: Jun 2005
Location: Milwaukee, Wi
Posts: 499
The problem was that "user" instead of "system" was selected in the drop down box for the channel config. He was trying to communicate ASCII to a message display, and then get online with the laptop serial port.

Greg
  Reply With Quote
Old December 10th, 2005, 01:47 PM   #5
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 4,223
along these same lines, there is a way to have the serial port “switch over” from User to System mode ... usually this requires the use of something like HyperTerminal to send the Mode “switch over” command ...



but ...



there’s a very neat trick suggested by Mr. Ken Roach in this thread which lets you trigger a spare input (or something like that) to make the channel "switch over" ... just read on for the next couple of posts to see how it works ...

I can imagine that this would come in very handy in situations where the SLC's serial port is normally configured for the User mode - but occasionally required for making a "programming" connection ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Allen Bradley Basic Card XEV2005 LIVE PLC Questions And Answers 19 March 22nd, 2012 02:28 PM
SLC 500 and Panelview Communication radarwolfe LIVE PLC Questions And Answers 5 June 2nd, 2005 02:07 PM
SLC 500 Pogram Disappear!! hhuong LIVE PLC Questions And Answers 7 February 2nd, 2005 07:03 PM
SLC 500 communication problem kelvinxu LIVE PLC Questions And Answers 7 June 9th, 2003 07:31 AM
Communication With Slc 500 Processor PERSPOLIS LIVE PLC Questions And Answers 3 November 6th, 2002 10:55 AM


All times are GMT -5. The time now is 11:47 AM.


.