I am experiencing a 'wierd' issue with serial port on a SLC 5/05. The processor is new out of the box. I had previously loaded a program and configuration through the serial port. However, when I attempt to establish communications with RSLinx via DF1 I can no longer connect to the processor. When I click on 'auto-configure', I get a message "failed to find baud and parity!" The baud rate on the processor is 19200 and is the same for my laptop COM1 port as well. Interestingly, I dumped the program from the processor and was able to download the same program through the serial port. However, the same issue arose again. The serial port seems to be "dead". I can connect to the processor via ethernet port just fine. But I will need the serial port to message to an InView display. Any help would be greatly appreciated. |
|
|
|
#2 |
|
Member
![]() Join Date: Dec 2004
Location: SE Michigan
Posts: 2,082
|
Check channel 0's configuration when you are connected. It may have slipped out of system mode/df1 protocol into one of the four other protocols (DH485, DF1 radio modem, etc.) or user mode.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen |
|
|
|
#3 |
|
Lifetime Supporting Member + Moderator
|
Alternately just check the channel 0 setup in your offline program. If it isn't DF1 then you should have recieved a warning on download about the communications being lost. If it is set up to some other mode (DH-485 etc then you may have to change RSLinx to connect. If it is ASCII mode then you probably cannot connect in that manner.
__________________
Controlling outputs is the PLC's way of getting its inputs to change. www.thePLCguy.com |
|
|
|
#4 |
|
Member
|
The problem was that "user" instead of "system" was selected in the drop down box for the channel config. He was trying to communicate ASCII to a message display, and then get online with the laptop serial port.
Greg |
|
|
|
#5 |
|
Lifetime Supporting Member
|
along these same lines, there is a way to have the serial port “switch over” from User to System mode ... usually this requires the use of something like HyperTerminal to send the Mode “switch over” command ...
but ... there’s a very neat trick suggested by Mr. Ken Roach in this thread which lets you trigger a spare input (or something like that) to make the channel "switch over" ... just read on for the next couple of posts to see how it works ... I can imagine that this would come in very handy in situations where the SLC's serial port is normally configured for the User mode - but occasionally required for making a "programming" connection ...
__________________
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Allen Bradley Basic Card | XEV2005 | LIVE PLC Questions And Answers | 19 | March 22nd, 2012 02:28 PM |
| SLC 500 and Panelview Communication | radarwolfe | LIVE PLC Questions And Answers | 5 | June 2nd, 2005 02:07 PM |
| SLC 500 Pogram Disappear!! | hhuong | LIVE PLC Questions And Answers | 7 | February 2nd, 2005 07:03 PM |
| SLC 500 communication problem | kelvinxu | LIVE PLC Questions And Answers | 7 | June 9th, 2003 07:31 AM |
| Communication With Slc 500 Processor | PERSPOLIS | LIVE PLC Questions And Answers | 3 | November 6th, 2002 10:55 AM |