Question Allen Bradley RIO

Thanks for your interest!

Does anyone know how to determine the scan frequency of the flexbus remote I/O mechanism. Does it occur asynchronously to the PLC scan time? At the moment I'm only interested in discrete I/O. Its my understanding that analog I/O must be read using BTs. Perhaps I just dont fully understand the mechanism in which case please explain it!

As an example, I have an SLC5/05 with a 1794-SN installed in Rack 0. A 1794-ASB is intalled and connected with blue hose to the SN. There is a 1794-IB16 on a 1794-TB3 with one wired input to a switch.

Any help is appreciated!
  Reply With Quote
Old December 16th, 2005, 09:51 AM   #2
wtakacs
Member
Canada

wtakacs is offline
 
Join Date: Dec 2005
Location: Ontario
Posts: 2
Smile Correction

In the example it should be a 1747-SN not a 1794-SN. OOPS 8-)
  Reply With Quote
Old December 16th, 2005, 10:32 AM   #3
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 7,656
The adapter scans its I/O on an independent cycle. The main rack's scanner polls the adapters. The processor gets it's copy of the I/O data table from the scanner module during it's I/O scan cycle. In short, the RIO is updated asynchronously to the program scan. The I/O image that the processor is working with does not change during logic solving (with SLCs and PLC5s anyway). With a PLC5, I have read some old A/B manuals that stated that the change of state of a discrete input, for example, may be reported to the processor up to 125ms after it actually occurs. Likewise for an output bit. It may take up to 125ms after the PLC turns on the output before that information reaches the remote output point. Repeatability of this delay is random. It might be 5ms one time and 100ms the next. The number of remote racks will affect this as well. A/B has worksheets that can help you accurately determine maximum RIO delays in their system design manuals.

This is something to always keep in mind at design time. Always try to put your time critical I/O in the local rack.

Hope this helps.
Paul C.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Learning Allen Bradley mbferrari LIVE PLC Questions And Answers 9 March 11th, 2009 11:25 AM
Allen Bradley 1746-BTM ChuckM LIVE PLC Questions And Answers 20 January 28th, 2008 07:16 AM
Wincc 6.0 and Allen Bradley PKTX 1784. nistam LIVE PLC Questions And Answers 1 March 31st, 2004 10:19 AM
Need Help with allen bradley mneumonic explanation Ctrayler LIVE PLC Questions And Answers 3 February 26th, 2004 01:23 PM
Allen Bradley 5/40L with local I/O extension nfvtmeinc LIVE PLC Questions And Answers 2 June 10th, 2003 09:55 PM


All times are GMT -5. The time now is 11:58 PM.


.