control methods for AC motor drives

I am looking for documents that describe the control methods for AC motor drives such as V/F control, Vector Control....
Any idea will be appreciated.
  Reply With Quote
Old December 20th, 2005, 09:31 AM   #2
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,890
Go to the Cutler Hammer Site, http://www.eatonelectrical.com/NASAp...eSearchResults , and do a search for TD.08H.17.T.E
  Reply With Quote
Old December 20th, 2005, 09:34 AM   #3
Leadfoot
Member
United States

Leadfoot is offline
 
Leadfoot's Avatar
 
Join Date: May 2005
Location: Red Stick, Cajun Land
Posts: 577
Try this site. This is a member's site. It has a good "laymans" explaination.


http://www.patchn.com
__________________
My brain hertz when I program!
  Reply With Quote
Old December 20th, 2005, 04:37 PM   #4
hashem
Member
United States

hashem is offline
 
Join Date: Aug 2005
Location: anytown
Posts: 33
I wonder why most VFD support output frequency more than 100Hz, although most AC motors have the rated of 50 or 60 Hz?
  Reply With Quote
Old December 20th, 2005, 05:11 PM   #5
PLC Gremlin
Member
United States

PLC Gremlin is offline
 
Join Date: Aug 2004
Location: TN
Posts: 80
Probably because VFD's can be used to control devices other than AC motors. I have used bowl Feeders controlled by VFD,s.
  Reply With Quote
Old December 20th, 2005, 05:30 PM   #6
Doug_Adam
Member
Australia

Doug_Adam is offline
 
Doug_Adam's Avatar
 
Join Date: Sep 2002
Location: Perth
Posts: 949
Quote:
Originally Posted by hashem
I wonder why most VFD support output frequency more than 100Hz, although most AC motors have the rated of 50 or 60 Hz?
Many 4 pole motors have the same barings and mechanical components used in 2 pole motors, allowing them to run at the same speed as a 2 pole motor. 2*60hz = 120hz, which is a common maximum for many brands of VFD.

Aircraft AC power runs at 400hz, although I don't think anyone would use a standard VFD in an aircraft, or use aircraft components on the ground, but you never know.
  Reply With Quote
Old December 21st, 2005, 01:25 AM   #7
automatic
Member
United States

automatic is offline
 
Join Date: Aug 2004
Posts: 136
I've found these two manuals from AB to be very useful:

http://literature.rockwellautomation...p003_-en-p.pdf

http://literature.rockwellautomation...p002_-en-p.pdf
  Reply With Quote
Old December 21st, 2005, 03:18 PM   #8
DickDV
Member
United States

DickDV is offline
 
Join Date: May 2002
Location: Kalamazoo MI
Posts: 2,313
While they are not exactly common, there are applications for induction motors that involve speeds up into the 20,000+ rpm range. A two pole motor at that speed requires frequencies over 300Hz.

These motors would be build special for the application, of course. They are often water cooled, not for cooling efficiency but to suppress the horrendous noise levels issuing from a rotor turning at those speeds.
  Reply With Quote
Old December 21st, 2005, 03:53 PM   #9
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,890
Here is an example of the very high speed units Dick talks about:

http://www.absgroup.com/absgroup/def...?iLanguageID=1


Search for High Speed Turbocompressor

These blowers hit 25,000 rpm. Scary, huh?

Last edited by Tom Jenkins; December 21st, 2005 at 03:57 PM.
  Reply With Quote
Old December 21st, 2005, 05:48 PM   #10
hashem
Member
United States

hashem is offline
 
Join Date: Aug 2005
Location: anytown
Posts: 33
Tom,
With reference to TD.08H.17.T.E document, it is quoted that "Operation at rated torque at twice speed means that the motor will be operating at twice its rated horsepower".
Is that achieved for all AC motor, or there are some restrictions? When we can use this method?
Any example?
  Reply With Quote
Old December 21st, 2005, 08:16 PM   #11
DickDV
Member
United States

DickDV is offline
 
Join Date: May 2002
Location: Kalamazoo MI
Posts: 2,313
When you operate a motor over its base speed, the torque goes down in inverse proportion to the overspeed. As a result, the horsepower holds constant into a limited amount of overspeed. Above that point, the torque starts falling faster than the speed increase so the horsepower starts to fall off. Eventually, if the motor doesn't fly apart, it will not have enough torque to even run itself so it stops rotating.
  Reply With Quote
Old December 22nd, 2005, 01:01 AM   #12
Vic
Member
Canada

Vic is offline
 
Join Date: Jun 2002
Posts: 236
hashem
Quote:
With reference to TD.08H.17.T.E document, it is quoted that "Operation at rated torque at twice speed means that the motor will be operating at twice its rated horsepower".
This situation, as described in the document, is for special applications where a 240 volt motor is run from a 480 volt drive and the motor is run at 480 volts, 120 Hz. This keeps the V/Hz ratio constant to 120 Hz and the motor will develop twice its rated horsepower.

I have heard of this being done but have never seen it myself. The main reason for doing this, as I understand it, is to get more HP from a small motor where space restrictions prevent using a larger motor. The document lists the considerations and restrictions to be followed when running a motor above its rated speed.
  Reply With Quote
Old December 22nd, 2005, 03:26 AM   #13
ivo.maenen
Member
Belgium

ivo.maenen is offline
 
ivo.maenen's Avatar
 
Join Date: Nov 2003
Posts: 617
Quote:
Originally Posted by hashem
Tom,
With reference to TD.08H.17.T.E document, it is quoted that "Operation at rated torque at twice speed means that the motor will be operating at twice its rated horsepower".
Is that achieved for all AC motor, or there are some restrictions? When we can use this method?
Any example?
I think one restriction is the maximum insulation-voltage.
  Reply With Quote
Old December 22nd, 2005, 08:52 AM   #14
hesham
Member
Egypt

hesham is offline
 
hesham's Avatar
 
Join Date: Jan 2003
Location: cairo
Posts: 328
hashem
please send your email i can provide some good documents
Br
__________________
Hesham Farid
Egypt
------------------------------------------------------------------------
Let your plans be dark and impenetrable as night, and when you move, fall like a thunderbolt(Sun Tzu) .
  Reply With Quote
Old December 22nd, 2005, 09:18 AM   #15
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,890
Quote:
Originally Posted by hashem
Tom,
With reference to TD.08H.17.T.E document, it is quoted that "Operation at rated torque at twice speed means that the motor will be operating at twice its rated horsepower".
Is that achieved for all AC motor, or there are some restrictions? When we can use this method?
Any example?
This has nothing to do with it's being an AC motor. This is just the laws of physics. hp = Tlbft x rpm / 5252. It doesn't matter if it is an AC motor or a hamster wheel - twice the speed at the same torque load means twice the horsepower load.

It is important to keep separate the load requirements, the load capabilities of the engine or motor, and the capacity of the energy delivery system.

The load power is dictated by the rate energy is needed to do the intended job. I could theoretically raise the Washington Monument with a hamster wheel - it would take a lot of gear reduction, reallly good bearings, and a very long time.

On the other hand, if I actually tried this I would probably exceed the thermal limitations of the hamster. After a few minutes the little bugger would die of heat stroke. Many of the limitations on AC motors are similar - sustained operation above rated power causes the thermal capabilities to be exceeded and the motor will fail from insulation burnout or whatever. You rarely see a motor fail from structural failure (twisted shaft, for example) due to overload.

If I could get a water cooled hamster (you figure out where to put the hose!) I might not have thermal problems. However, the ability of the energy delivery system would probably result in failure. The hamster's system simply couldn't provide enough energy transport in the blood stream to sustain muscular activity for the required duration. He'd stall out.

Similarly, the VFD cannot provide twice the rated power to the motor. The phenomenon Dick is talking about has to do with the limits of the VFD's ability to deliver current to the motor, and the ability of the motor to convert that current to rotating energy. The drive can't produce output voltge higher than what it sees at the input terminals. It can't produce current in excess of the thermal capacity of the internal components. That limits the power it can provide and the current it can provide. These in turn limit how much power the motor can produce and how much torque the motor can create.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Proportional-only control – why won’t it work right? Ron Beaufort LIVE PLC Questions And Answers 13 April 25th, 2005 04:18 AM
Dcs, Scada hasnoclue LIVE PLC Questions And Answers 15 April 11th, 2005 06:12 AM
PID - Simple Velocity Control Peter Nachtwey LIVE PLC Questions And Answers 15 July 9th, 2004 04:39 PM
how often should I trigger the PID? Ron Beaufort LIVE PLC Questions And Answers 11 February 22nd, 2003 10:57 AM
grounding power sources drewcrew6 LIVE PLC Questions And Answers 18 December 12th, 2002 05:16 PM


All times are GMT -5. The time now is 12:25 PM.


.