What are the limits for module use on a AB 1794 FLEX IO system?
I know that the maximum number of modules is eight and the maximum number of I/O points is 256. Based on this info, I can use eight 32point modules. Is that correct?
Also, is there a limitation to the number of input or output modules used?. For example, can I use six 1794-IB32 modules with two 1794-OB32 modules
Adrian
Old March 17th, 2006, 02:29 PM   #2
Ken Roach
United States
Ken Roach is online now
Ken Roach's Avatar
Disclaimer; I have not worked directly with the 32-point I/O modules but I am very familiar with the fundamentals of the 1794 platform.
The physical FLEX bus can support eight modules of any type. Analog, Specialty, 8-point, 16-point, or 32-point, it doesn't matter.
1794 FLEX is a 16-bit I/O architecture, so if you have 32-point modules you will have to logically communicate with them differently than with 16-point ones.
The most important consideration is which network adapter you are going to choose. Only the newest adapters for RIO, DeviceNet, ControlNet, and EtherNet/IP support the 32-point I/O modules, and they do so in slightly different ways.
The EtherNet/IP adapter, for example, allows you to make a logical I/O connection directly to the 32-point module, which is less efficient than a "rack optimized" connection but still works. I think the RIO adapter requires block transfers.
Get the release notes for the network adapter you will be using and they will have information on how 32-bit support is implemented in that adapter.
Here's a 32-bit module compatiblity table, taken from the 1794-IB32 installation manual:
Remote I/O
1794-ASB series E or later
1794-ASB2 series D or later
ControlNet
1794-ACN15 series C, firmware revision 4.1 or later
1794-ACNR15 series C, firmware revision 4.1 or later
Ethernet
1794-AENT series A, firmware revision 2.4 or later
PROFIBUS
1794-APB series A, version 1.1 of the GSD file
ControlLogixTM Family RSLogix5000 programming software, version 11 or later
__________________
- "Simpler is better, except when complicated looks really cool."
Old March 17th, 2006, 03:23 PM   #3
Contr_Conn
United States
Contr_Conn is offline
Contr_Conn's Avatar
Just want to confirm that Ken is correct.
Limit still 8 modules.
Correct adapter must be used that supports 32 bit mode.
Old March 17th, 2006, 08:34 PM   #4
AJZ
Canada
AJZ is online now
Thanks, Ken.
I am working on a new system using DeviceNet as the Network. A CLX L61 is the PLC.
Ken, I noticed that you did not list a DeviceNet module in your list. Does that mean I cannot use the 32point modules?
Adrian
Old March 18th, 2006, 08:17 AM   #5
Contr_Conn
United States
Contr_Conn's Avatar
Check these technotes for 32 point modules and 1794-ADN:
P20842 - 1794OB32P, 1794IB32, 32 point Flex I/O module and supported adapters.
Q110737688 - DeviceNet: 1794-ADN f/w 2.002 issue with Autoscan and 1794-IB32 or 1794-OB32P
A63745719 - Configuring 32 point discrete Flex I/O on a 1794-ADN DeviceNet adapter
Old March 18th, 2006, 09:48 PM   #6
Ken Roach
United States
Ken Roach's Avatar
Thanks for those, Control_Conn.
Those knowbase articles are more thorough than the installation instructions that I downloaded. See what happens when we let literature majors do engineer's work !
FLEX is a pretty old architecture and I'm grumpy about the way it works on DeviceNet (complex to map and maintain), but it's a good way to get a lot of I/O in a small space, especially when you connect it up on ControlNet or EtherNet/IP.
__________________
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
AB 1794 Flex IO DaveW LIVE PLC Questions And Answers 4 January 6th, 2006 06:34 PM
Connect TI-545 to AB 1794-APB Flex I/O Profibus adapter MHennel LIVE PLC Questions And Answers 1 August 9th, 2005 07:18 AM
AB PLC5/80B RIO Flex IO Fault corkers LIVE PLC Questions And Answers 9 September 4th, 2004 01:12 AM
PLC5 HotBackup with Flex IO Configuration Joydip LIVE PLC Questions And Answers 0 May 7th, 2002 06:22 AM