Unhappy Micrologix 1200 Analog Module Help

Hi Guys/Gals

I am having a problem connecting a pressure transducer to an analog module.
This my setup;
Pressure Transducer Thyracont VSC42MA4
4-20ma output Has 9 pin connector using 2 wires
Wiring diagram is like so
Pin 7 o---------------------------o +9-30VDC

Pin 4 o------| Controller |-------o gnd

Analog input 1762-1F4
PLC Micrologix 1200 1762-l40BWA

My question is how do I wire the transducer to the analog input and how do i configure the analog input.

Every time I configure the analog input for 1762-1F4 i get a fault condition.
When i use I/O read configure it give othercard......code=67 and verify program, error shows up as 'other' card detected no current load was taken into account.

I know that is a simple solution to the problem but it has eluded me.
appreciate your help.
  Reply With Quote
Old April 13th, 2006, 09:56 AM   #2
mgvol
Member
United States

mgvol is offline
 
mgvol's Avatar
 
Join Date: Dec 2004
Location: Knoxville, TN
Posts: 746
In you offline program, does RSLogix 500 list the 1762-IF4 as an available selection? If you are using the "OTHER-requires module I.D. code", what code are you using? What version of RSLogix 500 do you have? The hook-up for a 2-wire transmitter for the IF4 should be Transmitter (pin 7) to INx(+) and your sensor's dc power supply negative (-) to INx(-). If you can provide the answers to the above questions, I cna help with the config.
  Reply With Quote
Old April 13th, 2006, 10:07 AM   #3
mikewood
Member
United States

mikewood is offline
 
Join Date: Jun 2004
Location: Baltimore, MD
Posts: 13
Yes the RSlogix list 1762-1F4 as an available selection.
Other I.D. module code is 67.

The sensor does not have a power supply I was plannind on using the 24VDC provided by the Micrologix 1200.
  Reply With Quote
Old April 13th, 2006, 10:19 AM   #4
mgvol
Member
United States

mgvol is offline
 
mgvol's Avatar
 
Join Date: Dec 2004
Location: Knoxville, TN
Posts: 746
The 1762-IF4 will not provide loop power for your instruments, you have to either provide the 24 vdc from a separate supply, or use 4-wire instruments that source their own current. I am assuming you mean the 24 vdc available on 1762-LxxBWA bases. If so, wire it as I suggested in the previous post. You should add and configure the IF4 module to your program offline, then download it into the controller. That should clear up the "other" module code and power supply warning. Note that this is just a warning telling you that if you use a module that is not selectable from the I/O config. list (Other I.D. code), it can't calculate the backplane power usage.

Last edited by mgvol; April 13th, 2006 at 10:24 AM.
  Reply With Quote
Old April 13th, 2006, 10:45 AM   #5
mikewood
Member
United States

mikewood is offline
 
Join Date: Jun 2004
Location: Baltimore, MD
Posts: 13
Iam not sure I understand whatpu are saying.
Pin 4 from the sensor is the 4-20ma signal, Pin 7 +24VDC power input.
  Reply With Quote
Old April 13th, 2006, 10:55 AM   #6
mgvol
Member
United States

mgvol is offline
 
mgvol's Avatar
 
Join Date: Dec 2004
Location: Knoxville, TN
Posts: 746
Go here: http://literature.rockwellautomation...m001_-en-p.pdf and look at the 2-wire sensor wiring diagram on page 3-28. I should have state pin 4 instead of 7. My bad.
  Reply With Quote
Old April 13th, 2006, 01:32 PM   #7
mikewood
Member
United States

mikewood is offline
 
Join Date: Jun 2004
Location: Baltimore, MD
Posts: 13
Okay i have a seprate power supply and wired it as suggested.
Now i need help on configuring the 1762-1F4 analog module.
When i download and go to run postion, i get a fault. Major error S:6 = 187h
The error meassage states the following:

Check module1. The expansion i/o configuration in the user program did not match actual configuration or speicfied module that was found or data size for the module was greater than what the module is capable of doing.

Last edited by mikewood; April 13th, 2006 at 01:40 PM.
  Reply With Quote
Old April 14th, 2006, 06:54 AM   #8
mgvol
Member
United States

mgvol is offline
 
mgvol's Avatar
 
Join Date: Dec 2004
Location: Knoxville, TN
Posts: 746
Got your program; now I just need help remembering what the I/O config looked like in RSLogix V 4.10. Your version is probably close to 10 years old, so it may not behave the way that my V 7.10 does. When you go to I/O config, does your screen look like this:
  Reply With Quote
Old April 14th, 2006, 06:59 AM   #9
mgvol
Member
United States

mgvol is offline
 
mgvol's Avatar
 
Join Date: Dec 2004
Location: Knoxville, TN
Posts: 746
If the answer is yes, when you click on the advanced config button (with your cursor over the 1762-IF4 module), does your screen look like this, with all three folder tabs showing (Expansion General Config, Analog Input Config, and Generic Extra Data Config)? If not, tell me what you see.
  Reply With Quote
Old April 17th, 2006, 09:12 AM   #10
mikewood
Member
United States

mikewood is offline
 
Join Date: Jun 2004
Location: Baltimore, MD
Posts: 13
The answer to your 1st question is yes. To answer the 2nd question, the screen is exactly the same.
  Reply With Quote
Old April 17th, 2006, 09:23 AM   #11
mgvol
Member
United States

mgvol is offline
 
mgvol's Avatar
 
Join Date: Dec 2004
Location: Knoxville, TN
Posts: 746
O.K., that's great; we'll be reading from the "same piece of music" then. Have you opened the Analog Input configuration tab and set up your 4 channels yet? If so, let me know what the settings are.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Micrologix 1200 analog Jnelson LIVE PLC Questions And Answers 4 July 30th, 2004 02:27 PM
ML 1200 Analog Module ArikBY LIVE PLC Questions And Answers 5 April 2nd, 2004 05:41 AM
micrologix 1200 analog input board shayne LIVE PLC Questions And Answers 11 May 27th, 2003 09:30 AM
Micrologix 1200 analog I/O PLCgirl LIVE PLC Questions And Answers 7 February 14th, 2003 08:01 PM
Micrologix 1200 analog I/O module error taknevs LIVE PLC Questions And Answers 1 January 25th, 2003 07:16 PM


All times are GMT -5. The time now is 03:03 AM.


.