Hi Guys/Gals
I am having a problem connecting a pressure transducer to an analog module. This my setup; Pressure Transducer Thyracont VSC42MA4 4-20ma output Has 9 pin connector using 2 wires Wiring diagram is like so Pin 7 o---------------------------o +9-30VDC Pin 4 o------| Controller |-------o gnd Analog input 1762-1F4 PLC Micrologix 1200 1762-l40BWA My question is how do I wire the transducer to the analog input and how do i configure the analog input. Every time I configure the analog input for 1762-1F4 i get a fault condition. When i use I/O read configure it give othercard......code=67 and verify program, error shows up as 'other' card detected no current load was taken into account. I know that is a simple solution to the problem but it has eluded me. appreciate your help. |
|
|
|
#2 |
|
Member
|
In you offline program, does RSLogix 500 list the 1762-IF4 as an available selection? If you are using the "OTHER-requires module I.D. code", what code are you using? What version of RSLogix 500 do you have? The hook-up for a 2-wire transmitter for the IF4 should be Transmitter (pin 7) to INx(+) and your sensor's dc power supply negative (-) to INx(-). If you can provide the answers to the above questions, I cna help with the config.
|
|
|
|
#3 |
|
Member
![]() Join Date: Jun 2004
Location: Baltimore, MD
Posts: 13
|
Yes the RSlogix list 1762-1F4 as an available selection.
Other I.D. module code is 67. The sensor does not have a power supply I was plannind on using the 24VDC provided by the Micrologix 1200. |
|
|
|
#4 |
|
Member
|
The 1762-IF4 will not provide loop power for your instruments, you have to either provide the 24 vdc from a separate supply, or use 4-wire instruments that source their own current. I am assuming you mean the 24 vdc available on 1762-LxxBWA bases. If so, wire it as I suggested in the previous post. You should add and configure the IF4 module to your program offline, then download it into the controller. That should clear up the "other" module code and power supply warning. Note that this is just a warning telling you that if you use a module that is not selectable from the I/O config. list (Other I.D. code), it can't calculate the backplane power usage.
Last edited by mgvol; April 13th, 2006 at 10:24 AM. |
|
|
|
#5 |
|
Member
![]() Join Date: Jun 2004
Location: Baltimore, MD
Posts: 13
|
Iam not sure I understand whatpu are saying.
Pin 4 from the sensor is the 4-20ma signal, Pin 7 +24VDC power input. |
|
|
|
#6 |
|
Member
|
Go here: http://literature.rockwellautomation...m001_-en-p.pdf and look at the 2-wire sensor wiring diagram on page 3-28. I should have state pin 4 instead of 7. My bad.
|
|
|
|
#7 |
|
Member
![]() Join Date: Jun 2004
Location: Baltimore, MD
Posts: 13
|
Okay i have a seprate power supply and wired it as suggested.
Now i need help on configuring the 1762-1F4 analog module. When i download and go to run postion, i get a fault. Major error S:6 = 187h The error meassage states the following: Check module1. The expansion i/o configuration in the user program did not match actual configuration or speicfied module that was found or data size for the module was greater than what the module is capable of doing. Last edited by mikewood; April 13th, 2006 at 01:40 PM. |
|
|
|
#8 |
|
Member
|
Got your program; now I just need help remembering what the I/O config looked like in RSLogix V 4.10. Your version is probably close to 10 years old, so it may not behave the way that my V 7.10 does. When you go to I/O config, does your screen look like this:
|
|
|
|
#9 |
|
Member
|
If the answer is yes, when you click on the advanced config button (with your cursor over the 1762-IF4 module), does your screen look like this, with all three folder tabs showing (Expansion General Config, Analog Input Config, and Generic Extra Data Config)? If not, tell me what you see.
|
|
|
|
#10 |
|
Member
![]() Join Date: Jun 2004
Location: Baltimore, MD
Posts: 13
|
The answer to your 1st question is yes. To answer the 2nd question, the screen is exactly the same.
|
|
|
|
#11 |
|
Member
|
O.K., that's great; we'll be reading from the "same piece of music" then. Have you opened the Analog Input configuration tab and set up your 4 channels yet? If so, let me know what the settings are.
|
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Micrologix 1200 analog | Jnelson | LIVE PLC Questions And Answers | 4 | July 30th, 2004 02:27 PM |
| ML 1200 Analog Module | ArikBY | LIVE PLC Questions And Answers | 5 | April 2nd, 2004 05:41 AM |
| micrologix 1200 analog input board | shayne | LIVE PLC Questions And Answers | 11 | May 27th, 2003 09:30 AM |
| Micrologix 1200 analog I/O | PLCgirl | LIVE PLC Questions And Answers | 7 | February 14th, 2003 08:01 PM |
| Micrologix 1200 analog I/O module error | taknevs | LIVE PLC Questions And Answers | 1 | January 25th, 2003 07:16 PM |