IO discrete bits getting stuck ON in WW Intouch/AB PLC5 system

Hi,

Sorry, but I thought I had posted this before but could not find it. I appologize for the possible duplication. If you know the whereabouts of my original post, please post a link. Thanks.

Until recently I've been running InTouch v9.0 P2 and DASABCIP v3.0 P1 on XP Pro SP2. Itouch was upgraded to v9.0 P3 last week. My nodes are grouped into pairs, each running the same app. Each Intouch pair talks to a pair of AB PLC5s via one of two a ControlLogix ethernet/dh+ bridges consisting of an ENBT and two DHRIO modules. I have 4 apps, so 4 pairs of Intouch nodes with 4 pairs of PLCs. The 57k DH+ networks are separate although each connects to one of the two DHRIO modules in each of the two bridges. They are still logically separate. The following pictures may clarify that...



6 of 10 HMIs are connected to the same switch. The last 4 are connected to another switch in another part of the facility and the 2 switches are connected with a gig fibre connection. Tag counts in each app range from 1600 to 2400. Our new IT department has declared that all Ethernet is to be V-LANed. The 4 nodes are on a V-LANed switch shared with one general pc and printer. The entire switch to which the 6 are connected is set up for process control ip addresses. Sorry, I'm not very fluent in IT talk.

Ocassionaly we find that an IO discrete tag's item (bit in plc) is stuck, that is, is ON all the time where it should be off. The Intouch buttons that activate these tags are set as direct acting. It's as if the initial ON (1) makes it to the PLCs data table but the subsequent OFF (0) gets lost somewhere. I have no idea if this is a WW or AB issue.

The problem began when we upgraded from IT v7.11 with KT card IO servers on NT4 to v9.0 P2 on XP Pro SP2 with DASABCIP 3.0 P1. This never happened back in the KT card days even though each node polled the two PLCs independanly (redundant and doubled the traffic but it worked fine). We thought the problem was isolated to one particular set of nodes. We knew we had network traffic volume issues with that pair (expanded to 4 IT nodes) that was experiencing the stuck bits.

We changed that Intouch app to read from only one node's DAServer in that group of 4, thereby reducing the DH+ traffic to 1/4 of what it was when each node talked to the PLCs independantly. Not only did that speed up update time significantly but the stuck bit issue became much less frequent but not entirely gone. It still happens every few weeks.

I've gone through this with tech support and have applied their hotfix to ITv9.0 P2 to all my apps and nodes where I added "ForceWriteForDiscreteIOTags=1" to the app's ini file and view's intspt.dll was updated with a new version dated 2/18/2005 3:54 pm. Even then it still happens occassionaly. WW tech has since suggested applying Intouch patch 3, which I did last week, but it happened agian the other day.

We've found a stuck bit on another of the apps so it's not isolated to the 4 node/2 plc system I described earlier.

Is anyone else running into this? I have no idea how do I figure out what's causing this? Your assistance would be greatly appreciated. Thanks in advance.
  Reply With Quote
Old May 5th, 2006, 10:06 AM   #2
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 5,859
I never rely upon the HMI to turn off a bit that should be momentary. I've seen momentary PB bits get stuck on with RSView, CiTect, and Factory Link HMIs. If the bit is supposed to be momentary then the HMI handler subroutine in the PLC is programmed to make sure that the bit gets turned off.
  Reply With Quote
Old May 5th, 2006, 02:03 PM   #3
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 8,391
Quote:
Originally Posted by Alaric
I never rely upon the HMI to turn off a bit that should be momentary. I've seen momentary PB bits get stuck on with RSView, CiTect, and Factory Link HMIs. If the bit is supposed to be momentary then the HMI handler subroutine in the PLC is programmed to make sure that the bit gets turned off.
Ditto: With Intellution FIX32 also, below is an example:
Note N22:9/0 is written to by SCADA system, PLC logic resets bit after its use. It does not matter if the SCADA system turns it off
or not ( even though it is programmed to do so )
Attached Files
File Type: pdf resetbit.pdf (13.7 KB, 30 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old May 8th, 2006, 11:28 AM   #4
dkh333
Member
United States

dkh333 is offline
 
Join Date: Apr 2003
Location: Virginia
Posts: 9
I have seen this happen many times in various platforms including Wonderware and RSView. Like the others said a good method is to not use the HMI to turn off bits. If I have a button on Wonderare, I turn the bit on when the button is pressed. When the PLC receives the signal, I use an unlatch in the PLC to turn it off.
  Reply With Quote
Old February 20th, 2009, 10:58 AM   #5
wildswing
Member
Canada

wildswing is offline
 
wildswing's Avatar
 
Join Date: May 2005
Location: Sault Ste Marie, Ontario
Posts: 259
Hey fellas,

Sorry for blowing the dust off an old thread but, being the OP, I figured I'd provide an update and close the loop.

We finally found a solution. After creating a test Intouch app that simulated double clicking a button (IO discrete tag) I was able to intentionally create "stuck bits". I shipped that off to WW tech support for them to play with. They too were able to recreate the stuck bits.

After countless months of troubleshooting, which included a site visit by my tech contact, WW tech suggested that I change the "MAX CIP connections per channel" settings of the DHRIO module in their DASABCIP server from default of 4 to 1. That did it. No more stuck bits. I thought update times would suffer but it didn't. Case closed.

FYI, I'm told this was the longest open service request in WW tech support history at 3 years and 1 month.
__________________
Mark
Hard work never killed anyone, but why take the chance?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Reliability of WW Intouch v9.5 IO failover function? wildswing LIVE PLC Questions And Answers 2 March 6th, 2006 07:20 AM
Delay Timer AGENTTINFOIL LIVE PLC Questions And Answers 9 February 11th, 2006 07:25 PM
Quick question: Discrete IO does not need Block Transfer ckchew666 LIVE PLC Questions And Answers 17 September 19th, 2005 04:30 PM
Sugeest System based on PLC5 sandymax LIVE PLC Questions And Answers 0 June 22nd, 2005 05:18 AM


All times are GMT -5. The time now is 10:19 AM.


.