Member
![]() Join Date: Feb 2006
Location: Nebraska
Posts: 244
|
What are your opinions on grounding the 24VDC- to ground in a control cabinet? I've always done it, this latest place I'm working they thought I was nuts when I did it.
Any advantages or disadvantages? |
|
|
|
#2 |
|
Member
![]() Join Date: Jun 2004
Location: Lubbock, Texas
Posts: 642
|
I'm sure I'll get nailed for this as its not the generally accepted "correct" method, but its what my experience has led me to do...
In my opinion you're better off leaving it floating because then you know your 24vdc power is clean. I know that virtually every time I've tried connecting 24vdc- to ground I've created some sort of problem for myself...
__________________
Success is a journey, not a destination. -Ben Sweetland |
|
|
|
#3 |
|
Member
![]() Join Date: Apr 2006
Location: Newbury Park
Posts: 43
|
I have never grounded 24 vdc and never experienced any problems. The power supplies I use don't have a ground terminal on the dc output side so I figured it wasn't necessary.
|
|
|
|
#4 |
|
Member
![]() Join Date: May 2006
Location: Gonzales, LA
Posts: 691
|
My current project, because of the way we had to wire, I grounded the negative to the cabinet.
Another reason to do so is for troubleshooting; it's easier to find out where your voltage is going when you can reference it to ground. I'm working on offshore projects; typically everything is referenced to the frame as a ground anyway. |
|
|
|
#5 |
|
Member
![]() Join Date: Apr 2002
Location: WI
Posts: 1,152
|
I ground all of mine. But, I have a very hard time calling this reference -24VDC like most people do, I prefer 0V. also, I have started to use conductor insulation of white with a blue stripe.
|
|
|
|
#6 |
|
Lifetime Supporting Member
|
I never leave any supply floating unless it is absolutely required by the attached devices.
In all of my panels, all control reference legs (115VAC Neutral, 24VDC 0V, 12VDC 0V, 5VDC 0V, are all tied to earth. I've never had a problem. |
|
|
|
#7 |
|
Member
|
I never ground my 24 but I also don't work with anything other than inputs that use 24.
__________________
Mark A. Crowley Automation is not a corrective action for a lack of discipline. |
|
|
|
#8 | |
|
Lifetime Supporting Member
|
Quote:
__________________
Regards Dave "When you are courting a nice girl an hour seems like a second. When you sit on a red-hot cinder a second seems like an hour. That's relativity." Albert Einstein (1879-1955) |
|
|
|
|
#9 |
|
Member
![]() Join Date: Nov 2003
Posts: 122
|
Crntlfrk, you're not alone:
Poll: 24 Volt Inputs and Grounds Steve. Sorry, that should be cntrlfrk...
__________________
For the Present is the point at which Time touches Eternity. C.S. Lewis. |
|
|
|
#10 |
|
Lifetime Supporting Member
|
I also ground by 24V power supplies and I also call it 0DC not -24Vdc because it is not -24Vdc. I also use a white wire with a blue trace.
Note: even though the AC Neutral and 24V are both bonded to ground keep the neutral and the 0vdc buss seperated each with an independent ground. |
|
|
|
#11 |
|
Member
![]() Join Date: Aug 2002
Location: Eastman, Wisconsin
Posts: 745
|
Marksji,
Just out of curiosity, what problems have you caused for yourself? |
|
|
|
#12 |
|
Member
![]() Join Date: Jun 2004
Location: Lubbock, Texas
Posts: 642
|
Most of the time its from noise caused by ignition transformers, but sometimes its noise that already existed on the ground.
__________________
Success is a journey, not a destination. -Ben Sweetland |
|
|
|
#13 |
|
Member
![]() Join Date: Aug 2002
Location: Eastman, Wisconsin
Posts: 745
|
Wouldn't that indicate a ground problem at your site? Not trying to be a smartass here, electrical systems design is not my area of expertise. But if grounding a voltage cause noise on a system, my inclination and little experience would tempt me to look at my ground system more. Is ground noise a common problem that is accepted or not usually remedied? Thanks.
Russ |
|
|
|
#14 | |
|
Member
![]() Join Date: Jun 2004
Location: Lubbock, Texas
Posts: 642
|
Quote:
__________________
Success is a journey, not a destination. -Ben Sweetland |
|
|
|
|
#15 |
|
Member
![]() Join Date: Jan 2005
Location: Chatham, Ontario, Canada
Posts: 212
|
I always ground the common (negative if you will) of my power supplies. Never had a problem. As others mentioned, I also use blue with white stripe for the DC common.
__________________
Rob |
|
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
|
|
Similar Topics
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| 120VAC or 24VDC power on new PLC? | georgeofthejungle02 | LIVE PLC Questions And Answers | 33 | February 14th, 2018 02:03 PM |
| 24Vdc Tri-state LED | ranjana | LIVE PLC Questions And Answers | 8 | March 4th, 2009 09:48 AM |
| Voltage spikes on ground wire. | BigAl | LIVE PLC Questions And Answers | 26 | November 11th, 2004 03:08 PM |
| Phase Voltage Imbalance | Vetteboy | LIVE PLC Questions And Answers | 8 | June 21st, 2003 07:25 PM |
| grounding 24vdc | Michael Barabas | LIVE PLC Questions And Answers | 14 | June 21st, 2003 02:16 PM |