Old June 15th, 2006, 07:23 AM   #1
cntrlfrk
Member
United States

cntrlfrk is offline
 
Join Date: Feb 2006
Location: Nebraska
Posts: 244
Question Tying 24VDC- to Ground

What are your opinions on grounding the 24VDC- to ground in a control cabinet? I've always done it, this latest place I'm working they thought I was nuts when I did it.

Any advantages or disadvantages?
  Reply With Quote
Old June 15th, 2006, 07:46 AM   #2
marksji
Member
United States

marksji is offline
 
Join Date: Jun 2004
Location: Lubbock, Texas
Posts: 642
I'm sure I'll get nailed for this as its not the generally accepted "correct" method, but its what my experience has led me to do...

In my opinion you're better off leaving it floating because then you know your 24vdc power is clean.

I know that virtually every time I've tried connecting 24vdc- to ground I've created some sort of problem for myself...
__________________
Success is a journey, not a destination.
-Ben Sweetland
  Reply With Quote
Old June 15th, 2006, 07:56 AM   #3
gphillips
Member
United States

gphillips is offline
 
Join Date: Apr 2006
Location: Newbury Park
Posts: 43
I have never grounded 24 vdc and never experienced any problems. The power supplies I use don't have a ground terminal on the dc output side so I figured it wasn't necessary.
  Reply With Quote
Old June 15th, 2006, 08:01 AM   #4
tomalbright
Member
United States

tomalbright is offline
 
Join Date: May 2006
Location: Gonzales, LA
Posts: 691
My current project, because of the way we had to wire, I grounded the negative to the cabinet.

Another reason to do so is for troubleshooting; it's easier to find out where your voltage is going when you can reference it to ground. I'm working on offshore projects; typically everything is referenced to the frame as a ground anyway.
  Reply With Quote
Old June 15th, 2006, 08:15 AM   #5
Jim Dungar
Member
United States

Jim Dungar is offline
 
Join Date: Apr 2002
Location: WI
Posts: 1,152
I ground all of mine. But, I have a very hard time calling this reference -24VDC like most people do, I prefer 0V. also, I have started to use conductor insulation of white with a blue stripe.
  Reply With Quote
Old June 15th, 2006, 09:00 AM   #6
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,129
I never leave any supply floating unless it is absolutely required by the attached devices.
In all of my panels, all control reference legs (115VAC Neutral, 24VDC 0V, 12VDC 0V, 5VDC 0V, are all tied to earth. I've never had a problem.
  Reply With Quote
Old June 15th, 2006, 09:07 AM   #7
Rube
Member
United States

Rube is offline
 
Rube's Avatar
 
Join Date: Sep 2003
Location: Fort Worth, Texas
Posts: 939
I never ground my 24 but I also don't work with anything other than inputs that use 24.
__________________
Mark A. Crowley

Automation is not a corrective action for a lack of discipline.
  Reply With Quote
Old June 15th, 2006, 09:23 AM   #8
504bloke
Lifetime Supporting Member
England

504bloke is offline
 
504bloke's Avatar
 
Join Date: Jan 2005
Location: West Ssx
Posts: 2,651
Quote:
Originally Posted by rdrast
I never leave any supply floating unless it is absolutely required by the attached devices.
In all of my panels, all control reference legs (115VAC Neutral, 24VDC 0V, 12VDC 0V, 5VDC 0V, are all tied to earth. I've never had a problem.
Same as me
__________________
Regards

Dave



"When you are courting a nice girl an hour seems like a second. When you sit on a red-hot cinder a second seems like an hour. That's relativity."
Albert Einstein (1879-1955)
  Reply With Quote
Old June 15th, 2006, 09:25 AM   #9
Steve Kemp
Member
Wales

Steve Kemp is offline
 
Join Date: Nov 2003
Posts: 122
Crntlfrk, you're not alone:

Poll: 24 Volt Inputs and Grounds
Steve.

Sorry, that should be cntrlfrk...
__________________
For the Present is the point at which Time touches Eternity. C.S. Lewis.
  Reply With Quote
Old June 15th, 2006, 10:19 AM   #10
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 6,147
I also ground by 24V power supplies and I also call it 0DC not -24Vdc because it is not -24Vdc. I also use a white wire with a blue trace.


Note: even though the AC Neutral and 24V are both bonded to ground keep the neutral and the 0vdc buss seperated each with an independent ground.
  Reply With Quote
Old June 15th, 2006, 10:35 AM   #11
russrmartin
Member
United States

russrmartin is offline
 
Join Date: Aug 2002
Location: Eastman, Wisconsin
Posts: 745
Marksji,

Just out of curiosity, what problems have you caused for yourself?
  Reply With Quote
Old June 15th, 2006, 10:57 AM   #12
marksji
Member
United States

marksji is offline
 
Join Date: Jun 2004
Location: Lubbock, Texas
Posts: 642
Most of the time its from noise caused by ignition transformers, but sometimes its noise that already existed on the ground.
__________________
Success is a journey, not a destination.
-Ben Sweetland
  Reply With Quote
Old June 15th, 2006, 03:05 PM   #13
russrmartin
Member
United States

russrmartin is offline
 
Join Date: Aug 2002
Location: Eastman, Wisconsin
Posts: 745
Wouldn't that indicate a ground problem at your site? Not trying to be a smartass here, electrical systems design is not my area of expertise. But if grounding a voltage cause noise on a system, my inclination and little experience would tempt me to look at my ground system more. Is ground noise a common problem that is accepted or not usually remedied? Thanks.

Russ
  Reply With Quote
Old June 15th, 2006, 03:12 PM   #14
marksji
Member
United States

marksji is offline
 
Join Date: Jun 2004
Location: Lubbock, Texas
Posts: 642
Quote:
Originally Posted by russrmartin
Wouldn't that indicate a ground problem at your site? Not trying to be a smartass here, electrical systems design is not my area of expertise. But if grounding a voltage cause noise on a system, my inclination and little experience would tempt me to look at my ground system more. Is ground noise a common problem that is accepted or not usually remedied? Thanks.
Russ
Yes, I would assume so, but I have no control over the electrical system at any individual customer site so I have to build my machines to make do with what they've got. There was a time not too long ago when actually getting a ground wire pulled to the machine was rather remarkable.
__________________
Success is a journey, not a destination.
-Ben Sweetland
  Reply With Quote
Old June 15th, 2006, 05:44 PM   #15
rstech
Member
Canada

rstech is offline
 
Join Date: Jan 2005
Location: Chatham, Ontario, Canada
Posts: 212
I always ground the common (negative if you will) of my power supplies. Never had a problem. As others mentioned, I also use blue with white stripe for the DC common.
__________________
Rob
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
120VAC or 24VDC power on new PLC? georgeofthejungle02 LIVE PLC Questions And Answers 33 February 14th, 2018 02:03 PM
24Vdc Tri-state LED ranjana LIVE PLC Questions And Answers 8 March 4th, 2009 09:48 AM
Voltage spikes on ground wire. BigAl LIVE PLC Questions And Answers 26 November 11th, 2004 03:08 PM
Phase Voltage Imbalance Vetteboy LIVE PLC Questions And Answers 8 June 21st, 2003 07:25 PM
grounding 24vdc Michael Barabas LIVE PLC Questions And Answers 14 June 21st, 2003 02:16 PM