Mitsubishi Q Series Modbus TCP module QJ71MT91 set up help req'd...

Hi,

I'm having some difficulty getting our Mitsubishi Modbus TCP module (QJ71MT91) up and happily communicating to our other modbus slave devices. I can get it to work in slave mode using the default parameters, but we want to use it as a Modbus master and also with a custom configuration.

I require specific advice in regard to the set up of this module through the intelligent function module inside GX Developer. I'm pretty sure i'm coming unstuck in the set up of the Modbus to Mitsubishi conversion buffer addressing.

I have a tight time frame on this job and if possible I'd like your assistance on this matter. I'll give a brief below of our intended set up for the project and if you need me to elaborate on any of it please let me know.

For the programming of the Q series PLC we have available both GX Developer V8.03 and GX IEC Developer V7.00. We have installed the GX Configurator and downloaded the latest intelligent function module for the QJ71MT91 modbus card. The card has passed all the harware tests as per the set up manual (the manual is article number =158847), and as mentioned earlier it has been working in slave mode from tests I have done. The user manuals on the Mitsubishi gear are horrible too which doesn't help, they jump all over the place!!

The QJ71MT91 will need to be a modbus master and ideally also able to operate as a slave (the manual mentions it can be a master and a slave simultaneously but doesn't give a set up path or example for this arrangement?) and it needs to control a slave that has a very large table of modbus registers (they are also scattered across the full range of modbus addresses and not grouped tightly). We want to map the following from the modbus side to Q PLC

SLAVE 1 DETAILS

ITEM = MTL8000 I/O INTERFACE (INTRINSICALLY SAFE INPUT / OUTPUT INTERFACE)
IP ADDRESS = 10.1.1.201
COMMS METHOD = MODBUS TCP/IP
MODBUS ADDRESS = 1
PORT=502

.....................................MODBUS ADDRESS............DESTINATION...........PLC I/O TYPE...............Q PLC ADDRESS.......CONTROL LEVEL
--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
MODBUS COILS................000001-065536..............mapped to...............DISCRETE OUTPUT........Yxxxxx......................Read/Write
MODBUS CONTACTS........100001-165536...............mapped to...............DISCRETE INPUTS.........Xxxxxx......................Read
MODBUS INPUTS..............300001-365536...............mapped to...............ANALOG INPUTS...........Dxxxxx......................Read
MODBUS HOLDING...........400001-465536...............mapped to...............ANALOG INPUTS...........Dxxxxx......................Read/Write
MODBUS INPUTS..............300001-365536...............mapped to...............ANALOG INPUTS...........Dxxxxx......................Read/Write

SLAVE 2 DETAILS

ITEM = WONDERWARE INTOUCH v9.5 SCADA SOFTWARE
IP ADDRESS = 10.1.1.150
COMMS METHOD = MODBUS TCP/IP
MODBUS ADDRESS = 1
PORT=502

.....................................MODBUS ADDRESS............DESTINATION...........PLC I/O TYPE...............Q PLC ADDRESS.......CONTROL LEVEL
--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
MODBUS COILS................000001-065536..............mapped to...............DISCRETE OUTPUT........Yxxxxx......................Read/Write
MODBUS CONTACTS........100001-165536...............mapped to...............DISCRETE INPUTS.........Xxxxxx......................Read
MODBUS INPUTS..............300001-365536...............mapped to...............ANALOG INPUTS...........Dxxxxx......................Read
MODBUS HOLDING...........400001-465536...............mapped to...............ANALOG INPUTS...........Dxxxxx......................Read/Write
MODBUS INPUTS..............300001-365536...............mapped to...............ANALOG INPUTS...........Dxxxxx......................Read/Write

If you have any example projects, intelligent function set up text files, or further info in regard to the set up and use it would be greatly appreciated.

Thanks for your time, Regards Chris
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Eurotherm iTool and module 2500 series mmore LIVE PLC Questions And Answers 0 February 3rd, 2006 08:33 AM
plc5 with AB 1771-DB basic module, its urgent plz help me nileshsurya LIVE PLC Questions And Answers 6 July 20th, 2005 02:45 AM
mitsubishi A series how old? Will maintenance LIVE PLC Questions And Answers 4 June 25th, 2005 02:06 PM
I need help with Q Series Mitsubishi PLC programming functions KarateExplosion LIVE PLC Questions And Answers 4 November 9th, 2004 06:06 PM
SLC 5/03 data loss andydaoust LIVE PLC Questions And Answers 1 October 10th, 2002 07:38 PM


All times are GMT -5. The time now is 11:12 AM.


.