MC / MCR in detail pls!!

The MC / MCR is listed by mitsubishi to use for high efficient ladder switching. So, I would expect it to skip devices that are not active due to a resetted MC. But then, I read the following:
"The devices between the MC and MCR instruction are even processed after the input condition of the MC instruction is reset. Therefore, the program scan time in this case is not decreased."

That puzzles me, why is this so "high efficient" if the instructions are still processed even when the MC is reset? Or do they mean that the instruction are processed ONLY for the first scan after the MC is resetted??

Does anyone know that??
Michel
  Reply With Quote
Old September 24th, 2006, 02:34 AM   #2
Goody
Member
United Kingdom

Goody is offline
 
Goody's Avatar
 
Join Date: Apr 2002
Location: Huddersfield W Yorks UK
Posts: 977
Quote:
MC / MCR is listed by mitsubishi to use for high efficient ladder switching
Not sure what you mean by ladder switching. The MC (master control) and MCR (master control reset) is used for virtually turning off a section of the left hand bus rail between the MC and MCR instruction.
This disables all outputs within this section. (there is more to the MC instruction but that is what it is foe)
  Reply With Quote
Old September 24th, 2006, 03:47 AM   #3
asmdude
Member
Australia

asmdude is offline
 
Join Date: Sep 2006
Location: Sydney
Posts: 9
Quote:
Originally Posted by Goody
Not sure what you mean by ladder switching. The MC (master control) and MCR (master control reset) is used for virtually turning off a section of the left hand bus rail between the MC and MCR instruction.
Hello Goody, "ladder switching" is a term used by mitsubishi and it does exactly what you just described. The part I dont understand is why it is called "highly efficient". A conditional jump for example is efficient because it saves execution time when the jump instruction is active. So, I would like to know, do I save execution time when using the MC / MCR, and if not, then why is it called highly efficient??
  Reply With Quote
Old September 25th, 2006, 06:58 AM   #4
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 3,638
That is incredibly stupid terminology.

They probably claim that an MC/MCR pair is [Choke] "Highly Efficient" because it doesn't actually scan the logic in between the MC and MCR instructions if the MC is false; rather, it just sets the outputs off.

Don't get hung up on words... Or, for that matter, the ethereal "Efficiency". Write a program that is safe, and performs the desired task. Only if you see that you have a scantime issue later, should you try to optimize it (and probably not even then).
  Reply With Quote
Old September 25th, 2006, 06:49 PM   #5
asmdude
Member
Australia

asmdude is offline
 
Join Date: Sep 2006
Location: Sydney
Posts: 9
Quote:
Originally Posted by rdrast
Only if you see that you have a scantime issue later, should you try to optimize it (and probably not even then).
Yes, that is exactly my point, I actually do have a scantime issue... So you suggest to "just leave it that way", you wouldn't worry much about a scantime issue?
  Reply With Quote
Old September 25th, 2006, 07:19 PM   #6
Steve Bailey
Lifetime Supporting Member + Moderator
United States

Steve Bailey is offline
 
Steve Bailey's Avatar
 
Join Date: Apr 2002
Location: The boondocks of Western Massachusetts USA
Posts: 4,658
I can't speak from experience with Mitsubishi, but on the PLCs with which I am familiar, using the MCR instruction minimizes the difference in scan between when the function is active and when it is not. In other words, if the scan time is X milliseconds when the logic controlling the MCR is true, it will still be X milliseconds when the logic controlling the MCR is false.

What is your "scan time issue"?

If your goal is minimizing scan time, then you should be using JUMP instructions or subroutine CALLs with logic controlling when to JUMP or CALL. If the scan time would be too long if all of the JUMPs were false and all of the CALLs were true in a single scan, then your challenge is to design the logic so that doesn't happen, yet still execute the subroutines (or the Jumped rungs) often enough to keep the process under control.

Also, remember that in the absence of an instruction turning it on or off, an output will retain the last state it was told to be in. That means if you don't call a subroutine or if you continually execute the JUMP instruction, outputs turned on or off by the rungs in the subroutine or in the JUMPed zone will not change their state.

You should also read the documentation for your PLC to determine what happens to timers within a JUMP zone or subroutine.

Last edited by Steve Bailey; September 25th, 2006 at 07:22 PM.
  Reply With Quote
Old September 25th, 2006, 08:26 PM   #7
panic mode
Member
Canada

panic mode is offline
 
panic mode's Avatar
 
Join Date: May 2003
Location: Toronto, Canada
Posts: 1,961
I agree, if you have problme with scan time, you can try skipping
parts of the program or call parts of program conditionally.
personally I would also rather use CALL Pn and FEND
but this has to be verified for particular CPU.
I'm not sure if they all support it (anything reasonably recent
should). what PLC and programming software you have there?

Last edited by panic mode; September 25th, 2006 at 08:31 PM.
  Reply With Quote
Old September 26th, 2006, 12:28 AM   #8
asmdude
Member
Australia

asmdude is offline
 
Join Date: Sep 2006
Location: Sydney
Posts: 9
Quote:
Originally Posted by panic mode
I'm not sure if they all support it (anything reasonably recent
should). what PLC and programming software you have there?
I am using medoc with an F1-30 (do they still work? yes they do....) :-). It supports jumps, but no calls... I actually thought that the MC/MCR worked similar as the jump with the only difference that it would disable the outputs in case the MC is false. I don't have the docs of this dinosaur so it's a bit of a guessing game...
  Reply With Quote
Old September 26th, 2006, 07:55 AM   #9
bob1371
Member
United States

bob1371 is offline
 
bob1371's Avatar
 
Join Date: Mar 2003
Location: Southern Indiana
Posts: 209
Quote:
Originally Posted by asmdude
I am using medoc with an F1-30 (do they still work? yes they do....) :-). It supports jumps, but no calls... I actually thought that the MC/MCR worked similar as the jump with the only difference that it would disable the outputs in case the MC is false. I don't have the docs of this dinosaur so it's a bit of a guessing game...
If your a member of www.mrplc.com you can download manuals from thier site.
http://forums.mrplc.com/index.php?dlcategory=20
or if not, just sign up. They have both the F1 hardware and programming manuals listed.

Bob
  Reply With Quote
Old September 27th, 2006, 04:03 AM   #10
asmdude
Member
Australia

asmdude is offline
 
Join Date: Sep 2006
Location: Sydney
Posts: 9
Quote:
Originally Posted by bob1371
If your a member of www.mrplc.com you can download manuals from thier site.
http://forums.mrplc.com/index.php?dlcategory=20
or if not, just sign up. They have both the F1 hardware and programming manuals listed.

Bob
That is exactly what I needed! Thanks bob!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
AB MicroLogix 1500 PLS function Shawn Cassidy LIVE PLC Questions And Answers 2 October 29th, 2009 02:44 PM
Allen-Bradley MCR instruction Chris335577 LIVE PLC Questions And Answers 13 May 4th, 2006 05:08 PM
Question? robmo62 LIVE PLC Questions And Answers 15 July 15th, 2005 01:28 AM
Acheiving output with PLS bigjoe LIVE PLC Questions And Answers 10 July 12th, 2005 09:49 AM
MCS / MCR Instrutions dandrade LIVE PLC Questions And Answers 1 February 9th, 2004 09:13 PM


All times are GMT -5. The time now is 07:54 PM.


.